Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 422
    • 423
    • 424
    • …
    • 501
  • Next »

Is there a setting that will retransmit a BACnet point in case a BACnet device goes offline?

Issue Is there a setting that will retransmit a BACnet point in case a BACnet device goes offline? Environment Niagara G3 ENS, ENC-410, ENC-520 Cause Points go offline and come back online with controller default values. Resolution The Max Write Time applies to writable proxy points. Specifies the maximum “wait time” before rewriting the value, in case nothing else has triggered a write. Any write action resets this timer. If property value is 0 (default), this rule is disabled (no timed rewrites). The Max Write Time of the Tuning Policy can be set to periodically write to proxy points at a set time interval. 1. Open the station and expand its BACnetNetwork 2. Expand Tuning Polices 3. Double-click on the policy you want to update 4. Enter a maximum time to be used in the Max Write Time property. (example 10 minutes) 5. Save change Note: In some cases setting this to some value, for example 10 minutes, may be useful. Often, a network may have devices that upon a power cycle (or even a power “bump”), have writable points that reset to some preset “default” value or state.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC IA Series
1670 Views

After the power cycle the nvi values in any LON device will be "Invalid value/null".

Issue When any LON device is power cycled the nvi values will change to invalid / null / last changed / default value.   Environment LON Devices Cause Using the device for the first time or after re-flashing the firmware. Power cycling the device. Resolution If nvi has any binding it receives the value from source nvo. If nvi does not have the binding then manually set the value. If nvi is a multistate SNVT it returns to default value.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1263 Views

Cross reference for Controlli MVL56PS56

Issue Schneider Electric portfolio replacement actuator for Controlli MVL56PS56 Environment MVL56PS56 Forta M700 Cause A replacement for Controlli MVL56PS56 is requested by customer. Resolution MVL56 is replaced by the Forta M700. "PS56" is a production specific specification for another manufacturer (unknown). Linkage kit required is depending on application. Part no MVL56 is replaced by MVH56 at Controlli.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
1279 Views

Increasing the Security for Webstation

Issue Method for increasing the security of Vista Webstation. Environment Vista Webstation 5.1.7 Internet Information Server (IIS) Internet Security and Acceleration Server (ISA) Cause Increased Webstation security is limited by the security of  Internet Information Server (IIS). Webstation is only a web application running on the IIS, therefore to make webstation more secure is to make the connections to the IIS more secure. Resolution Security can be increased by using an Internet Security and Acceleration Server (ISA). The IIS would then reside on a computer behind the ISA server.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC Vista
1111 Views

SPD910 Hose connectors as spare parts

Issue Requesting replacement hose connectors for SPD910  Environment SPD910 Cause If the hose connectors are lost or broken, they may want to be replaced. Resolution The hose connectors are not listed as replacements or spare parts. However, if there is a need for numerous units, a request to the manufacturer may be done.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
967 Views

Running I/NET on a Virtual PC.

Issue Installing I/NET on a Virtual PC and how to get it to work properly. Environment All versions of I/NET Server 2008R2 (64bit) Server 2003 Windows 10 64bit (Inet 2.49 only) Windows 8 Windows 7 Windows XP SQL versions 2005, 2008 VMWare Cause This is an unsupported application as I/NET was not tested in this environment due to the various operating systems that are out there. Resolution This is a use at your own risk, it works in most instances when set up correctly but if for some reason it does not, it is an unsupported application.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC INET
1346 Views

Can I use one SQL database with two Vista servers

Issue I have two Vista databases that log many points. Can I just use one full version of SQL or do I need one for each server. Environment Vista 5.xx Cause When more that 1 Vista server is installed each server will write and read from their own SQL databases. Resolution Each Vista server requires a separate SQL database to write to. The SQL database does not need to remain on the server PC, it can be on a network pc the server has access to.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC Vista
1262 Views

Deny Entry Schedule

Issue Getting a Deny Entry Schedule on a card read in the Transaction Window. Environment All versions of I/Net. Cause The time on the schedule could be off based on what the parameters were when it was created. Resolution To resolve this issue, there are a few steps that needs to be followed. 1. Verify that the Host PC is running the correct time so that the schedule is effective. 2. Connect to the controller and verify if that matches the Host PC. 3. Download the correct time to the controller if it does not. 4. Read a card and again after the changes and it should be functional again.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC INET
1505 Views

Take long time for a alarm in Vista to appear.

Issue Take long time for a alarm in Vista to appear. A change of state object in Vista is monitoring a signal on a Lon node but it takes up to 15 minutes before the alarm appears in Vista.  Environment Vista 5.1.7 Cause When a object is monitored by Vista Vista will start to poll this signal but the poll have a pretty low priority in Vista so for example graphics and trend logs have higher priority than the polling. If there is many trend logs and many signals is polled in Vista it can take a long time for Vista to go thru the poll list. Vista can maximum read around 40 values per second. So depending on how much other communication there is on the Lon interface it can take several minutes before Vista will see that the value have changed. Resolution Analyze how much communication there is in Vista via a Communication log and try to reduce the communication on the Lon network interface.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC Vista
1147 Views

Damper actuator replacement AM230

Issue In 2006, a new line of damper actuators was presented, replacing the previous generation. Environment M-AM230 (871-0000-010) MD20B-230 (875-1021-000) Cause Replacing old series damper actuator with new. Resolution The M-AM230 (871-0000-010) is replaced by MD20B-230 (875-1021-000). For a complete list of replacements, please see MA-430_0
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Field Devices
1287 Views

Cannot create database backup from Vista

Issue Vista appears to run normally, but when creating a backup using the $backup_VDB object no backup is created. The message "Unable to copy $thisdb\*.*" appears in b0cfglog.txt in the $log folder, but there are no other indications that the backup has failed. Environment TAC Vista 5 Cause An additional folder has been placed in the $thisdb folder, possibly while manually copying or moving the database.  The folder name is not important, but any change in the internal structure of $thisdb prevents Vista from taking a backup.  Additional files in $thisdb do not have this problem. Resolution Delete any sub-folders from the $thisdb folder.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC Vista
1201 Views

Getting error code 5227 ( 0x0146B ) when opening editor of the existing PE program in a controller.

Issue When you have a PE program in bCX controller which is quite long and works good in the controller.  But when you open the editor of the program to modify it,  you get the error code 5227 ( 0x0146B ) and cannot  open the editor.  Environment Continuum workstation. BCX4040. BCX9640. Cause When editing a long PE program of  the controller in online mode, the controller fails to respond to workstation when the controller is too busy due to high scan rate or the busy network.  Resolution Resolution 1) - Modify / change other existing PE programs to alleviate the controller's CPU load ( reduce the scan of the controller ) enough for the controller to respond to workstation in time.  Resolution 2 - Edit the long PE program of the controller in offline mode ( offline workstation ) , and then reload the program to the controller from online mode ( online workstation) .
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Andover Continuum
1526 Views

Creating a new Tool.

Issue How to create a new Tool for an application to run. Environment All versions of I/Net Seven. Cause How to create a new Tool to be functional on a graphic page. Resolution User Tool Type TAC I/NET Seven displays this dialog when you add, copy, or modify a tool from the User Tool Configuration editor. Use this dialog to define a name for a tool, and to choose the tool type. Define a Name for the tool (up to 50 characters). Choose a tool type. The following options are available:  Event – Choose this tool to execute an event sequence defined in a controller.  Shortcut – Choose this tool to launch another application, run a batch file, open a file, visit a website (via a batch file), etc. Select OK to accept these settings. If you chose Event in the previous step, TAC I/NET Seven displays the Event Selection dialog. If you selected Shortcut in the previous step, TAC I/NET Seven displays a file selection dialog, allowing you to choose the file or application to be launched by the tool. Example of Creating a Tool to Open a URL The following example describes how to create a tool that will open http://www.msn.com in your system's default web browser. Using Notepad, create a new text file and type the following line of text: start http://www.msn.com Save the file to your PC as OpenMSN.bat. Add a new tool using the steps described at the beginning of this help topic. Use the following guidelines:  For the tool type choose Shortcut.  When the file selection dialog appears, select the OpenMSN.bat batch file that you just created.
View full article
Picard Product_Support
‎2018-09-10 07:34 AM

Labels:
  • TAC INET
1447 Views

Change a door name when there is an * in Netcon

Issue How to change a door name when there is an * in Netcon. Environment All versions of I/NET Seven Software Cause The name that the save file has does not match what is currently in the controller. The * represents a change either on the controller's database or what is currently on the resident I/O Points. Resolution Verify that the name on the Resident I/O Point is the correct one that is needed. Connect to the controller and penetrate down to the DPU Level. There would be an * next to the door in question. Modify the door and change it to the desired name. It can also be deleted and a + sign will be displayed in the cnf column. Saving that plus sign ensures that everything is system is correct again. Note: When the delete is used, it will remove this door not from the Tenants, Groups and Individuals. They would have to be revisited and saved again.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • TAC INET
1451 Views

Can I use the new STR500 Continuum Room Temperature Sensor on a Smart Sensor port?

Issue Can I use the new STR500 Continuum Room Temperature Sensor on a Smart Sensor port? Environment Continuum Controllers Cause Need an extra temperature input and the Smart Sensor port is not being used. Resolution As well as the Smart Sensor, the Smart Sensor port can support 10Kohm temperature sensors. The STR500 is a 10Kohm temperature sensor for the Continuum controllers. It will work on the smart sensor port but will only be usable as a temperature input, it will not have the full Smart Sensor abilities. 
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Andover Continuum
1653 Views

WebPinpoint does not work through external network connection. Receive Pinpoint error: "Unknown error. Server:http://:/DNWACServerFactory/WACServerFactory.soap".

Issue WebPinpoint does not work through external network connection. Receive Pinpoint error: "Unknown error. Server:http://:/DNWACServerFactory/WACServerFactory.soap". This error is not seen when the WebClient browser machine is connected to the same LAN as the WebClient Server. Environment Continuum WebClient Browsing through a Firewall using port forwarding. Cause Port forwarding was used to forward external port 16540 to the WebClient Server to overcome the fact that port 80 (normally what is used for IIS) was being used by another Server on this LAN. Resolution Change the internal port in IIS to use 16540 (or any other unused port) instead of 80. On the router, route external port 16540 to internal port 16540. Reboot the WebClient Server. Connect to the WebClient server specifying the new port: http://serveraddress:16540/    
View full article
Picard Product_Support
‎2018-09-10 01:03 PM

Labels:
  • Andover Continuum
1315 Views

Error 1001 could not load file or assembly sorttbls.nlp

Issue Continuum application fails to start with error 1001 could not load file or assembly Sorttbls.nlp Environment CyberStation Cause .Net corruption. Resolution Uninstall and re-install .net May have to re-format the hard drive and re-install windows if problem is not fixed by the above.
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Andover Continuum
1563 Views

Access Events show up in active event viewer but are not logged in the database.

Issue Primary access server stops logging access events. A list view of access events shows that no events have been recorded in days even though doors are working file and people get access. ACCTrace taken at the primary access server shows the events are received but there is no line indicating that the events are logged. (Don't see line AccDataServices, Logger, SUCCESS logging access event) Environment CyberStation Cause The module that takes care of logging the access events in the Primary Access server has stopped working even though all other functionality in the CyberStation seems to be working fine. Resolution Close CyberStation Reboot the machine Re-start CyberStation
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Andover Continuum
1311 Views

Door Modes.

Issue Door goes to Secure mode even when there is no ATS on it. Environment All versions of I/net Software. Cause The software puts the door in the secure mode by default. Resolution The access control functions within TAC I/NET Seven depend partly on schedules to determine when access will be granted to individuals or groups. The following door related schedules are used for access control: 1. Mode Schedules — You can assign a mode schedule to each door in order to control what mode the door will operate in during specific times of the day. When a door is in the Locked mode, access will not be permitted regardless of any other schedules. 2. Personnel Schedules — You can define up to 31 personnel schedules for each door. Personnel schedules are only used to control access when a door is operating in the Secure or PIN Enable mode. Mode Schedule A door Mode Schedule controls the operating mode of the door at specific times of the day. The following door Mode Schedule actions are available:  APB Reset — Use this action to reset anti-passback memory for this door.  Lock — This mode inhibits entry and exit through the door. All readers and release buttons for the door are disabled while this door mode is in affect.  Unlock — This mode allows open access through the door.  Secure — This mode allows access only after a valid key/card has been read. All key/cards will be validated based on personnel schedules, tenant, key/card issue number, anti-passback, and access level.  When a door equipped with a PIN pad is operating in the "Secure" mode, the PIN pad will not be enabled (that is, entry of a personal identification number will not be required in order for an individual to gain access).  PIN Enable (firmware version 3.20 or earlier)  OR Sec/PIN (firmware version 3.21 or later) — When this mode is active, the PIN reader on the DPU will be enabled. This mode is the same as the "Secure" mode except that it also requires the individual to enter a valid PIN after a valid key/card read. If an individual enters an invalid PIN, the setting of the PIN Retry Count parameter in the Door Extension Editor will determine how many retries (if any) the individual can use to enter a valid PIN.  You can schedule a door's PIN pad to become disabled without unlocking the door by following this mode with a "Secure" mode. When the "Secure" mode becomes active, individuals will no longer be required to enter a PIN in order to gain access through the door.  Sec/Code (firmware version 3.22 or later) — This mode is similar to the "Secure" mode; however, rather than using a key/card to gain access, the user simply uses the PIN pad to enter the door's assigned code. If the individual enters the correct door code, the door will open.  When the door is operating in the Sec/Code mode, user-definable door attributes or PIN pad functions are not available. Note: If the door needs to be unlocked then they can manually be unlocked for that period then return to the secure mode when needed.
View full article
Picard Product_Support
‎2018-09-06 12:36 PM

Labels:
  • TAC INET
1403 Views

Multiple Pinpoint graphics on multiple display monitors from one Cyberstation

Issue At times there is a need to display Pinpoint graphics on multiple displays from one Cyberstation Environment Continuum Windows XP Windows Vista Windows 7 Windows 2003 Windows 2008 Cause There is a need to display multiple graphics, but opening multiple graphic panels opens them in the same Pinpoint window Resolution Open up one pinpoint graphic normally through Cyberstation Start>Programs>Continuum>Pinpoint  then File>Open and select the graphic (launches another session of pinpoint.exe) Drag and drop the second pinpoint session to your second display Repeat Caution: Pinpoint.exe can be resource intensive, so opening multiple sessions will increase the number of resources consumed at least by the number of sessions that are open. This method does not get tested in QA.
View full article
Picard Product_Support
‎2018-09-06 12:36 PM

Labels:
  • Andover Continuum
1424 Views
  • « Previous
    • 1
    • …
    • 422
    • 423
    • 424
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore