After the power cycle the nvi values in any LON device will be "Invalid value/null".
  • After the power cycle the nvi values in any LON device will be "Invalid value/null".
  • sesa194431
    sesa194431
‎2018-09-06 12:38 PM
When any LON device is power cycled the nvi values will change to invalid / null / last changed / default value.
LON Devices
  1. Using the device for the first time or after re-flashing the firmware.
  2. Power cycling the device.
If nvi has any binding it receives the value from source nvo.
If nvi does not have the binding then manually set the value.
If nvi is a multistate SNVT it returns to default value.
Labels (2)