Deny Entry Schedule
  • Deny Entry Schedule
  • Roger_Bently
    Roger_Bently
Deny Entry Schedule
‎2018-09-06 12:37 PM
Getting a Deny Entry Schedule on a card read in the Transaction Window.
All versions of I/Net.
The time on the schedule could be off based on what the parameters were when it was created.
To resolve this issue, there are a few steps that needs to be followed.
1. Verify that the Host PC is running the correct time so that the schedule is effective.
2. Connect to the controller and verify if that matches the Host PC.
3. Download the correct time to the controller if it does not.
4. Read a card and again after the changes and it should be functional again.
  • TAC INET
  • 7410