Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 421
    • 422
    • 423
    • …
    • 501
  • Next »

Attempting to connect the I/A Series G3 Enterprise Network Server to an ENC and getting a Niagara Station Fault Cause License Exception. Authentication Failed: Exceeded Device lim...

Issue Attempting to connect the I/A Series G3 Enterprise Network Server to an ENC and getting a Niagara Station Fault Cause License Exception. Authentication Failed: Exceeded Device limit of 0. Environment I/A Series G3, Enterprise Server, ENC-410, ENC-520 Cause Communications between the I/A Series G3 Enterprise Network Server and ENC-410/520 requires that both are licensed to for peer-to-peer (Niagara Driver) support.  The error indicates the ENC is not licensed for peer-to-peer. Resolution Use Workbench License Manager to "view" the license in the ENC. Locate the feature for niagaraDriver and verify the device.limit is none.  A device.limit of 0 indicates the ENC requires the addition of the P2P option. To add the peer-to-peer option ... ENC-410-1 ... purchase ENC-410-P2P. ENC-520-2 ... purchase ENC-520-P2P.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC IA Series
1365 Views

Does Niagara G3 provide a method to throttle rapidly changing BACnet proxy point values so they don't overwhelm the network with traffic?

Issue Does Niagara G3 provide a method to throttle rapidly changing BACnet proxy point values so they don't overwhelm the network with traffic? Environment Niagara G3, ENC-410, ENC-520 Cause Rapidly changing BACnet proxy point overwhelming the network with traffic. Resolution The Min Write Time property applies to writable proxy points, especially ones that have one or more linked inputs. It specifies the minimum amount of time allowed between writes. It provides a method to throttle rapidly changing values so that only the last value is written. If this property value is 0 (default), this rule is disabled (all value changes attempt to write). The Min Write Time of the Tuning Policy can be set to limit the frequency of rapidly changing proxy points being sent. 1. Open the station and expand its BACnetNetwork 2. Expand Tuning Polices 3. Double-click on the policy you want to update 4. Enter a minimum time to be used in the Min Write Time property. 5. Save change  
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC IA Series
1268 Views

Can SIGNAL send alarms to a pager?

Issue Can SIGNAL send alarms to a pager? Environment SIGNAL all versions Cause End customer has requested pager numbers be added to alarm notification.  Currently just visual display on the SIGNAL computer via Alarm Manager and printouts to the connected printer are available. Resolution SIGNAL does not have the ability to dial out alarms to a pager.  Years ago, a 3rd-party product called Alarm Flash was used to provide this capability.  If a similar product is available today, it may work with SIGNAL's Alarm Manager. Another alternative is to use a modem connected to the field panel (GCM or DMS) that can dial a pager number via a modem when an alarm occurs.  There are also several 3rd party products which can interface serially to the field panels and be programmed with several phone numbers and customized text messages.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC IA Series
1026 Views

Webpinpoint will not run Plain English script that works in Cyberstation Pinpoint

Issue Nothing happens or an error ' You have insufficient rights to perform this operation' happens when clicking a webpinpoint graphic that is set up with a Plain English script. Environment Webclient Web Pinpoint Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Webpinpoint does not support running PE programs like Cyberstation Pinpoint does. Resolution Webpinpoint does not support running PE programs like Cyberstation does. A possible work around to this would be to set up a numeric that gets changed when a button is pushed. A program can be set up as looping to be triggered by this numeric and the code executed to perform the operation needed.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • Andover Continuum
1237 Views

Lost CD Key, can the license information be retrieved quickly

Issue Lost CD Key, because the CD case is missing Environment Any Windows OS Cause The site has lost the I/Net CD case and for some reason they cannot log into the I/Net system anymore Resolution If this is the issue, please contact the Product Support Services Department in your area.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC INET
1837 Views

The Momentary Start / Stop (SS) object in a MNB-1000 controller is not working. No output pulses are not being generated.

Issue The Momentary Start / Stop (SS) object in a MNB-1000 controller is not working.  The OutStrt and OutStp outputs never pulse on as programmed.  The OnPulse and OffPulse times are set to 1 second each. Environment MNB-1000 with firmware 1.501 or newer Cause The On and Off times for a Momentary Start/Stop object fails with a start time or stop time below 2 seconds. The Plant and Remote I/O Module can't do accurate timing below 2 seconds or so by design. Resolution Release 1.501 firmware for the MNB-1000 controller allows the Momentary Start / Stop (SS) object to be used with OnPulse and OffPulse intervals of 2 seconds or greater.  This is described in the Release Notes for WPT 5.7 / MNB-1000 1.501 Firmware (F-27526).     On and Off Pulse timing wrong for Momentary Start/Stop.     PRN 4677     Issue:     The Momentary Start/Stop times in the MNB-1000 are not accurate     when set for small second increments (1 to 12 seconds)     Resolution:     This has been partially fixed in the MNB-1000 firmware.     Small increments greater than 2 seconds are now accurate.     See the note on PRN 5011 describing limitations on increments     less than 2 seconds.     On and Off Pulse timing wrong for Momentary Start/Stop.     PRN 5011     Issue:     The On and Off times for a Momentary Start/Stop object fails with     a start time or stop time below 2 seconds. The Plant and Remote IO     Module can't do accurate timing below 2 seconds or so by design.     The object still works, but the timing is inaccurate.     Resolution:     A note has been added to document F-27356 (revision 3) "WorkPlace     Tech Tool 5.7 Engineering Guide Supplement" to warn of the     limitations of this object in the MNB-1000.  
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC IA Series
1246 Views

'Unable to request license' message when using Demo license with Remote Workstation.

Issue 'Unable to request license' message when using Demo license with Remote Workstation. Product Line TAC Vista Environment Vista 5 Vista 4 Cause The Demo license only works when installed on the same PC as Vista Server. Resolution Install demo license on the Vista Server PC and run Workstation on the same PC.  If remote Workstation operation is required or the license server is on a different PC to Vista Server, purchase an end user license.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC Vista
1620 Views

Trying to talk to Trane Controller (MP580) and will not update. (LON)

Issue Trying to talk to Trane Controller (MP580) and will not update. (LON) Environment G3/R2 Niagara Cause Run Frequency is a property that defines how often the program executes. If set to 0 values will not update in LON shadow object. Resolution Run frequency to a value other than 0.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • TAC IA Series
1210 Views

Xdriver points will not save properly

Issue Trying to create Modbus RTU 2nd Generation XDriver points. Filled in Xdriver tab attributes and pressed "Apply" or "OK". When refreshing or re-opening the point editor the Xdriver tab info has not saved.     Environment Modbus RTU Xdriver CyberStation Cause The name attribute of the Xdriver comm port was changed to Modbus Comm 4 and the Alias was changed to CommX. Resolution Change the Xdriver comm port name and alias attributes back to the default settings - in this case comm4. Points now save correctly.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1326 Views

Modbus TCP/IP xdriver points update time is extremely slow.

Issue Modbus points on a CX9680 have very long update time.  Points can take hours to update.  LAN capture file shows no issues. Down reving the NetController to firmware 2.000014 restored normal point update times.  This problem recurs when the controller is upgraded to any higher version. Environment Modbus TCP/IP xdriver CX9680 Cause Slow update times may be related to a known issue that was corrected in the new Modbus TCP/IP xdriver v 200017 that was released 2/14/2012 Resolution Replace xdriver with version 2.00017.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1346 Views

Is it necessary to commission an MNB series controller if it is being used in a standalone application?

Issue  Is it necessary to commission an MNB series controller if it is being used in a standalone application?   Environment Single standalone MNB series controller Cause Using an MNB-300 controller to control a small RTU via an attached MN-sx sensor during construction.  Resolution No. Commissioning is needed only when the device is being configured to communicate via its BACnet interface.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC IA Series
1389 Views

Can not change schedule object property list in Viconics thermostat model VT7652H5X18

Issue From Continuum edit the schedule that comes built in with the Viconics device and change the Object Property List then save the schedule. The schedule object saves without error, but re-opening the schedule reveals that no change took place. Environment CyberStation Viconics thermostat Cause Viconics does not allow changes to the built in schedule object property list. Resolution A workaround is to put the schedule that is in the Viconics device out of service then create a schedule in the bCX that drives the desired objects in the thermostat.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1314 Views

What are the part numbers to order the back plate and controller separately for an MNB-1000?

Issue What are the part numbers to order the back plate and controller separately for an MNB-1000? Environment MNB-1000 Cause MNB-1000 part number break down. Resolution The MNB-1000 controller breaks down as follows: MNB-1000 - Controller and Base Assembly MNB-CNTLR-1000 - Controller only, less Base MNB-BASE-1000 - Base only, less Controller  
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC IA Series
1357 Views

Dump file imports fail, have errors, or have blank programs with no code.

Issue Dump file imports fail, have errors, or have blank programs with no code. Environment Continuum Cyberstation Cause Large dump file imports (such as an entire site database) can have problems where the import gets out of sync and fail. Making any changes to the dump file with an editor such as Word, Wordpad, or Edit applications. These text editors cause problems formatting, the bytecode of InfinityPrograms do not have a carriage return and the editor can end up pushing all the lines of code up onto one line. This can't be imported properly due to the line now being greater than the maximum line size. Resolution The following recommendations should be considered when importing dump files: Usually breaking these large imports up into smaller chunks (each controller) results in a smoother import and more success. Use a true ASCII text editor such as Notepad++ to make changes to dump files. Always save changes to a new filename so the original is left untouched.  You may also need to remov the Workstation Folder and Workstation, re-initialized the Continuum Workstation and then retry the import.  
View full article
Picard Product_Support
‎2018-09-10 12:59 PM

Labels:
  • Andover Continuum
1339 Views

How to print a value padded so as to always get the same number of digits.

Issue Need to print a variable such as DayOfYear and have the value always printed using three digits. Environment All CXs All i2s All b3s Cause Documentation Resolution Use the 'Right' function as follows... Print Right("000",DOY,3) to MyString The above will print the day of the year to MyString padded with zeros to the left when day of year contains less than three digits.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1115 Views

Cannot add the ReportService to the Services container of a Niagara G3 ENC.

Issue The Platform Software Manager indicates the Report module is installed on the ENC, but ReportService cannot be added to the Services container of an ENC. The following error message is displayed in the Program Director window: WARNING [22:25:05 12-Jan-12 CST][sys.xml] Type "report:ReportService" not found: null [3:55] javax.baja.xml.XException: Error parsing value [4:4] at javax.baja.io.BogDecoder.err(BogDecoder.java) at javax.baja.io.BogDecoder.decode(BogDecoder.java) at javax.baja.sync.AddOp.decode(AddOp.java) at javax.baja.sync.SyncBuffer.decode(SyncBuffer.java) at com.tridium.fox.sys.broker.BBrokerChannel.syncToMaster(BBrokerChannel.java) at com.tridium.fox.sys.broker.BBrokerChannel.circuitOpened(BBrokerChannel.java) at com.tridium.fox.sys.BFoxConnection.circuitOpened(BFoxConnection.java) at com.tridium.fox.session.SessionCircuits$ServiceThread.run(SessionCircuits.java) at java.lang.Thread.run(Thread.java:823)   Environment Niagara G3 all versions, ENC-410, ENC-520 Cause The ReportService Module in the ENC Platform may have become corrupted. Resolution Uninstall and reinstall the module in the ENC, making sure the module content filter is set to ui+runtime.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC IA Series
1371 Views

Wiring detail using STR602 temperature sensor inc. remote adjust with a CXR5805 Controller

Issue Wiring detail using STR602 temperature sensor inc. remote adjust with a CXR5805 Controller Environment STR602 CXR5605 CXR 5605 Cause The STR datasheet instructions are not clear, it details terminals 22, 23 and 24 and not what each terminal is for e.g. 0V Com, Setpoint, 'C. The CXR5805 User Guide details the old part numbers. Resolution The STR602 combines the RPW4425 and DRT3453 into one temperature and setpoint unit. The STR602 is a 3 wire device using a common 0V between the setpoint adjust potentiometer and the temperature sensing thermistor. The terminations are STR602 term 22 (Setpoint) STR602 term 23 (Temp 'C) STR602 term 24 (0Vcom) And if used on a CXR5805 STR602 term 22 (Setpoint) is wired to term 5 on the CXR5805 STR602 term 23 (Temp 'C)  is wired to term 22 on the CXR5805 STR602 term 24 (0Vcom)  is wired to term 27 on the CXR5805 Link terminals 6 and 27 on the CXR5805 
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
1647 Views

Mirrored point's value is still transferred to the destination controller even when the value is not changed at all.

Issue When a program in the source controller keeps setting a point's value to the same value (i.e. set MyPoint = On) every scan, the point's value is being transferred to the destination controller even if the point is subscribed in the Import/Export table. Environment Infinet controllers ( i1 & i2 ) Net controllers ( CX9xxx & ACX57xx) Cause When the value of the source point is changed, it is transferred to the destination Infinet controller(s) by the IE engine.  But when the source point's value is set to the same value (most likely output and numeric points set by calculation programs in the same controller), the IE engine still transfers the same value to the destination controller, in order to have the destination controller get the value that might have been lost due to the controller being offline.  This does not happen to Input points due to the threshold attribute of the object.  Resolution Modify the calculation program in the source controller to compare its value with the previous value before setting the value to the calculation (or condition check) result.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1118 Views

Personnel Manager opening delay.

Issue Personnel Manager takes longer to open than Personnel Editor. Environment Continuum 1.93 Cause When the personnel folder is selected it will take time to complete the object list. (Contents of the folder)   10,000 records = approx. 45 seconds. Resolution Wait until the object list populates before you select a personnel record. There will be a 10 to 20 second opening difference between the personnel manager and the personnel editor. This is due to opening process differences.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Andover Continuum
1058 Views

Browser locking up with blank screen after viewing several graphics.

Issue Browser locking up with blank screen after viewing several graphics.  Java console says java.lang.OutOfMemoryError: PermGen space. Environment IA Series Niagara G3 Cause This can occur when viewing graphics screens from different ENC stations that have differing versions of modules. The browser will load the modules it needs from each ENC which can eventually use up all the available PermGen memory. Resolution Make certain all ENC stations are using the same version of the modules needed.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • TAC IA Series
1264 Views
  • « Previous
    • 1
    • …
    • 421
    • 422
    • 423
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore