Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 420
    • 421
    • 422
    • …
    • 501
  • Next »

Where can I find the details for UK and Ireland Vista partners.

Issue Locating partners Environment Partner Vista Cause Require engineer to visit for maintenance, servicing, installation or advice. Resolution Click here to be linked to the available UK and Ireland Vista partner list.
View full article
Picard Product_Support
‎2018-09-10 07:04 AM

Labels:
  • TAC Vista
1119 Views

Node or XDriver Upgrade of BCX Inf (9640) to BCX BACnet (4040) or reverse

Issue When upgrading a BCX Inf to BCX BACnet or vice versa , the BCX could lose any node count or X Drivers added using a post shipment factory *.upd cookies. The settings return if the controller is flashed back to the original model type. Product Line Andover Continuum Environment Continuum 1.xx 2.xx Windows Infinet  BACnet Node Count, X Driver, X-Driver Cause This is because the cookie upgrade to add the node count (or other features) will be sent out for the format it is intended for, i.e. if the controller was BACnet then the file will be sent as BACnet, and if the controller was Infinet then the cookie will be Infinet Resolution New controllers shipped from the factory can be flashed either way between a 4040 and 9640 and it will not affect the settings for Node count, X Drivers or other options. If a controller was to lose additional setting when it is convert from BACNet to Infinet or vice versa, there is a need to re-apply for the cookie upgrade file for the new model type. (it would of originally been ordered as additional options for the controller) To re-apply for the cookie, contact your local repairs department with the controller details i.e serial number, controller type, etc, this will enable them to find your order and reissue the upgrade in the version it has been changed to.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
3005 Views

How can LON communications be throttled in standard MNL series controllers?

Issue Too much LON communications traffic can cause LON communications errors. Environment MNL-50, MNL-100, MNL-150, MNL-200, MNL-110, MNL-130, MNL-VxRVx controllers Cause Sending output LON SNVT values too frequently or more often than reasonably needed. Resolution In a particular application the engineer needs to consider the amount of data being transmitted on the LON network due to LON network bandwidth limitations.  On an FTT-10 LON network, the bandwidth is limited to approximately 72 packets (messages) per second.  Because the LON network is operating using CDMA (Collision Detect, Multiple Access) communications techniques, data collisions will reduce the practical data limit to approximately 1/2 of the maximum.  Typically the LON network designer will limit the packet transmission rate of 30 to 35 packets per second.  There are a series of NCI (configuration) objects that control the transmission and reception of these data values on the LON network. The nciSndHrtBt determines the maximum amount of time that is allowed before all bound NVOs are updated, that is, the data is marked to be "re-sent" to all bound nodes.  This value is typically set to 120 seconds, causing all bound NVO SNVT values to be transmitted at least once every two minutes. The nciRcvHrtBt sets the fallback timer value for each NVI object.  If a value is not received via a binding in this time period, the NVI object will revert to its application defined default value.  It should be noted that this value does not directly affect the LON bandwidth but it does affect how the controller handles the loss of the bound data communications.  This value is typically set to about 2.5 times the nciSntHrtBt to allow for occasional lost communications packets and delays due to data collisions occurring on the network. The nciMinOutTm controls how often a bound NVO value will be transmitted when the value is changing within the controller.  Each specific SNVT type has a specific data resolution and any time the data value changes by one count, the value will be sent.  For example a temperature value bound through a NVO as a SNVT_temp_p type has a resolution of 0.01 degrees Celsius.  If bound this temperature NVO will be transmitted each time the value changes by 0.01 degrees C.  The setting of the nciMinOutTm throttles this bound NVO value transmission by forcing the controller to ignore any changes to that NVO value for a specific time interval each time it is transmitted.   The nciMinOutTm value defaults to NA causing the bound NVO value to be transmitted each time it changes.  Typically the nciMinOutTm is set to a value in the 1 to 5 second range causing the controller to throttle the transmission of the changing NVO values.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • TAC IA Series
1235 Views

VideoLaunch has stopped working error when accessing video

Issue An error pops up 'Video Launch has stopped working' when previewing in Video Administrator, selecting a camera in Video Layout or when a video alarm comes in. AppCrash on TAC.VideoLaunch.exe Environment Continuum Webclient Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause A standard VGA driver is being used on the Video card instead of the manufacturer's video driver Resolution Install the manufacturer's video driver. i.e. Nvidia, Ati, etc.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
1250 Views

Cannot connect to ENC from Workbench or ENS on computer with AVG Internet Security Suite Business Edition 2012

Issue AVG Internet Security Suite Business Edition 2012 has been installed on Enterprise Network Server computer at customer site.  After the installation, no connection can be made between either the ENS or Workbench from that computer even though all Windows firewall functions have been disabled. Environment I/A Series G3 ENS installation on Windows computer. Computer protected with AVG Internet Security Suite Business Edition 2012 Cause The Link Scanner function of the AVG Internet Security Suite Business Edition 2012 acts as a smart firewall Resolution The Link Scanner function of the AVG Internet Security Suite Business Edition 2012 must be configured to allow point to point Ethernet connections between the ENS/Workbench computer and each ENC used on the jobsite.  Refer to AVG Internet Security Suite Business Edition 2012 documentation for more information and instructions.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • TAC IA Series
1015 Views

When do I need the -U (unlimited I/O) option enabled on my Continuum Security Key?

Issue When do I need the -U (unlimited I/O) option enabled on my Continuum Security Key? Environment Continuum Cyberstation Cause Ordering new Continuum Security Key for existing site. Unsure if -U option is require if specific Workstation is only going to be viewing less than the 1000 I/O limit, even though there are more than 1000 I/O on this entire site. Resolution If your site has more than 1000 combined inputs and outputs then you will need to use the unlimited (-U) option for the Continuum Security Key to be able to see all I/O. Without the -U option, the Workstation will be limited to the first 1000 input and output points. You are unable to pick and choose which 1000 points you wish to see at each workstation, if your site has more than that defined then you will need to order the -U option on your Continuum Security Key.  
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
1294 Views

Is it possible to rebuild a Continuum Database from the BACnet controllers in the field?

Issue Is it possible to rebuild a  Continuum Database from the BACnet controllers in the field? Environment Continuum BACnet Cause The SQL server has failed and there are no acceptable backups of the ContinuumDB to restore once the server has been repaired. The controllers in the field are still functioning and have valid application programming. Resolution Although it is possible to recover the database from the field controllers, the best method of recovery is to have a recent backup of the ContinuumDB and to restore this once the Server gets fixed up. You can load the data from your field controllers into a new Database. Note that all objects will have their name now set the same as the alias, as this is what is stored in the controller. To load the bCX and attached b3's, do the following with a blank database. 1. Create and configure a network folder. 2. Create and configure you bCX1 device object to bring it online in the Infinet view. 3. Right-click on the bCX1 object in the Infinet view and select "Send to -> Database". 4. This will save the controllers database to a temporary dump file on the Workstation then load from this dump file, creating the objects and populating the database. 5. When done, this should have also found all b3's that were defined in the bCX1 and loaded their contents as well. 6. This will load the BACnet objects as well as the Infinet objects. Note: Recreating the Network from the field does not recreate any objects that were stored in Workstations or in folders off the root. These objects; such as listviews, programs, reports, etc...; are not stored in the controllers and will need to be recreated. 
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
2662 Views

How to filter a list view to only show certain entries?

Issue When opening one of the pre defined list views there are many entries and can not find text required. Environment List views Filter, Qualifier, Query Wizard, Wildcard. Cause Default list views show all entries, how to define a qualifier to only show required data? Resolution Create a new list view and define the Class and path, add in the required columns. In the Qualifier tab select the "Query Wizard", for text comparisons use the required attribute e.g. Description, and "Is Like" as the Operator, enter the comparison text between wild card * characters (e.g. *Test* for the objects which contain the word Test) and it will filter only on objects whose attribute contain that text.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
999 Views

Can array elements be used in a trend log.

Issue Bacnet Trend logs do not support array elements in Continuum. Environment Continuum Bacnet Trendlog Cause Trying to create a trendlog based off of array elements. Resolution Bacnet Trend logs do not support array elements in Continuum.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
1259 Views

Unlocking a door after First Valid Access

Issue At times there is a need to keep a door unlocked with a schedule, but this can cause a problem if there is extreme weather and no one is at the building.  Environment Continuum AC1/AC1A AC1 Plus ACX5740 ACX781 Cause Leaving a buildings door open when there is no one at the building is a security risk. This work around will take care of this problem. Resolution The way around the issue of having a door open from a schedule when no one is in the building due to inclement weather is to set up a Plain English program to set the Unlock InfinityNumeric On only if the schedule InfinityNumeric is On AND there has been a valid access to the door. InfinityProgram FlowType Loopin Objects required Door1 - the name of the door to control SchedNum - InfinityNumeric controlled by the schedule UnlockNum - InfinityNumeric linked to Door1 Door Unlock Schedule Code Example (This must be edited to reflect the door name and schedule numeric that has been created) WaitForSched:      UnlockNum=Off      If SchedNum=On then GoTo WaitForValid WaitForValid:      If Door1 ValidAccess is True then         UnlockNum=On         GoTo WaitForEnd      Endif WaitForEnd:      If SchedNum=Off then GoTo WaitForSched
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • Andover Continuum
1298 Views

Critical Error registry access denied when launching the Wireless Maintenance Tool on Windows 7 or Windows Server 2008

Issue After successfully installing the Wireless Maintenance Tool on Windows 7 an attempt to launch is unsuccessful. The following error is received. 'Critical Error InitInstance() Reason : Access to the registry key  'HKEY_CLASSES_ROOT\.wmt' is denied. Environment Wireless Maintenance Tool Windows 7 Windows Server 2008 Cause User Account Control is restricting access to this portion of the registry needed to launch the Wireless Maintenance Tool Resolution Disable User account control If using Windows 7 Go to Windows Control Panel>User Accounts>Change User Account Control Setting link Drag the slider to the bottom Restart the PC Launch the Wireless Maintenance Tool without error If using Windows Server 2008 Go to Windows Control Panel > User Accounts> Turn User Account Control On of Off Deselect Use User Account Control (UAC) to help protect your computer Restart the PC Launch the Wireless Maintenance Tool without error
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • Andover Continuum
1421 Views

Object not available when trying to add an object reference to a Continuum object editor.

Issue When trying to add a point to a Group or graphic using the object browser in the object editor Continuum says the object is not available.  When an occupancy point is added to the configuration page of a Continuum schedule and  the change is applied and the editor closed, upon re-editing the schedule the point is no longer attached. Environment Continuum CyberStation Object Editor Browse Cause An object name violation has occurred. Resolution Check for objects that have been given the same name as the Continuum Network under which the controller resides in the object tree.  Once a Continuum Network is given a name the name should not be used for any other object in the database.
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • Andover Continuum
1327 Views

When a OPC client is connecting to Vista the updates of values in Vista get really slow .

Issue When a OPC client is connecting to Vista the updates of values in Vista get really slow. The OPC client is asking for values from a Lon network Environment TAC Vista 5.1.7 Vista OPC server IFix OPC client in this case but could be any Cause The problem here is that the OPC clients asks for more values per second from the Lon network then the Vista server can deliver. The Visa server can read around 40 values per second using a Loytec network interface in a classic Lon network.  Resolution Make sure the OPC client doesn't read more then maximum 30-40 values per second from Vista.
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • TAC Vista
1064 Views

Rehosting licenses: max rehosts exceeded

Issue There is a limit of allowed rehosts per year. If this limit is reached and a rehost is attempted, the following error message is given: "The rehost of the fulfillment is denied by the rehost policy because max rehosts exceeded " Environment Vista 5.x Cause If the rehost is motivated and necessary, the policy can be overridden by PSS. If required, please contact PSS Malmö. Resolution Manually override rehost policy by using Administrative rights on the Licensing web.
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • TAC Vista
1691 Views

Trend Logs not working error decoding message Id:57356 Msg: Illegal value

Issue Error message: 'Illegal value'  when displaying Xenta Server trend logs in browser. Environment Xenta 731 Xenta 721 Xenta 711 Xenta 701 Xenta 511 Cause Log space in trend log definition set to 0. Resolution Set trend log space to be greater then the size of the log interval. 
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • TAC Vista
1633 Views

Why does "Change Inherited Attribute?" dialog box with "Cancel," "Change the value," "Break the connection," "Change the data source&...

Issue When changing attached Template of a Personnel object from one Template to another Template, why does " Change Inherited Attribute ? " dialog box with " Cancel " , " Change the value " , " Break the connection " , " Change the data source " selections pop up? Environment Continuum Access / Security system with personnel template objects. Cause It happens only when below two conditions are met : When you change the personnel object's attached Template object to a different Template object.   AND   When the old Template's RefTemplate attribute value is "InheritFromTemplate" and the new Template's RefTemplate  attribute value is "CopyFrom Template". Resolution Change the value of RefTemplate attribute of the attached Template from "InheritFromTemplate" to "CopyFrom Template".
View full article
Picard Product_Support
‎2018-09-06 12:40 PM

Labels:
  • Andover Continuum
1261 Views

Webclient launch from a URL gets an error 'Failed to access IIS metabase'

Issue On a new install an error is received when launching webclient using the URL. The error is 'Failed to access IIS metabase' Read access error. Environment Webclient Windows XP Windows Vista Windows Server 2003 Windows Server 2008 Cause The .Net installation connection to IIS was made properly or the .net installation has been corrupted.  Resolution Register the .Net Framework on the webclient PC From a DOS prompt (Start>Run cmd+enter) Cd\Windows\Microsoft.net\framework\v2.0.50727 (this places you in the correct folder) Run aspnet_regiis.exe -i (This command re-registers the .net framework with IIS) Restart IIS (Right click on default web site in IIS Manager, select stop the start) Re-test Uninstall/Reinstall .Net on the webclient PC If the first step doesn't correct the issue then do the following Remove the versions of .net that you can from Windows Control Panel>Add/remove programs (Try one at a time 4.0, 3.5,etc) There are dependencies when uninstalling some .net versions, so you may need an uninstall tool from the following web site: (Use at your own risk - please read the information first) http://blogs.msdn.com/b/astebner/archive/2006/05/30/611355.aspx   Install .Net framework 20 using the following file provided on the webclient installation (C:\program files\webserver\redist\dotnetfx20.exe) Restart IIS (Right click on default web site in IIS Manager, select stop the start  Re-test
View full article
Picard Product_Support
‎2018-09-10 07:38 AM

Labels:
  • Andover Continuum
1456 Views

Connecting the RoamIO / BACnet Service Tool to a stand alone B3 device

Issue Can the RoamIO connect to a stand alone b3 device? Environment RoamIO BACnet Service Tool b3s Cause Need to connect to b3 device that is not on any MSTP Resolution Yes, the RoamIO and BACnet Service Tool can be used to connect to a stand alone b3 device as long as the device already has been assigned a MAC id If the b3 is brand new and has not yet been assigned a MAC id, you'll have to attach a second b3 that has a MAC id, the RoamIO needs to see traffic on the MSTP in order to perform its auto baud and join the bus. Connect the RoamIO to the service port on the device. NOTE: In the View menu make sure the 'View by networks' menu item is NOT selected.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • Andover Continuum
1211 Views

Error when viewing trendlog report.

Issue View report in trend log object returns error "No data was returned for this report. Please check the report time interval and filter. Environment bCX4040 b3s Cause Trendlog object has not been sent to the database Resolution In the Continuum Explorer, expand the BACnet Devices folder then select the device Right click on the device and select Sent To -> Database Make sure the Trendlog object now appears in the BACnet view View report from the Trendlog object should now display  without error
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • Andover Continuum
1333 Views

Personnel Import Utility (PIU) and import options in Continuum Explorer.

Issue Does the PIU follow the 'Import Into Options' in the Continuum Explorer? Environment CyberStation PIU Cause Documentation Resolution When importing personnel objects via the PIU the 'Import Into Options' in the Continuum Explorer DO NOT apply. The PIU always overwrites all area links if an import from the PIU is done to an existing personnel object.
View full article
Picard Product_Support
‎2018-09-06 12:39 PM

Labels:
  • Andover Continuum
1305 Views
  • « Previous
    • 1
    • …
    • 420
    • 421
    • 422
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore