Issue
When upgrading a BCX Inf to BCX BACnet or vice versa , the BCX could lose any node count or X Drivers added using a post shipment factory *.upd cookies.
The settings return if the controller is flashed back to the original model type.
Product Line
Andover Continuum
Environment
- Continuum 1.xx 2.xx
- Windows
- Infinet
- BACnet
- Node Count, X Driver, X-Driver
Cause
This is because the cookie upgrade to add the node count (or other features) will be sent out for the format it is intended for, i.e. if the controller was BACnet then the file will be sent as BACnet, and if the controller was Infinet then the cookie will be Infinet
Resolution
New controllers shipped from the factory can be flashed either way between a 4040 and 9640 and it will not affect the settings for Node count, X Drivers or other options.
If a controller was to lose additional setting when it is convert from BACNet to Infinet or vice versa, there is a need to re-apply for the cookie upgrade file for the new model type. (it would of originally been ordered as additional options for the controller)