Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How can LON communications be throttled in standard MNL series controllers?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How can LON communications be throttled in standard MNL series controllers?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1079 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How can LON communications be throttled in standard MNL series controllers?

Picard Product_Support
‎2018-09-06 12:41 PM

Issue

Too much LON communications traffic can cause LON communications errors.

Environment

MNL-50, MNL-100, MNL-150, MNL-200, MNL-110, MNL-130, MNL-VxRVx controllers

Cause

Sending output LON SNVT values too frequently or more often than reasonably needed.

Resolution

In a particular application the engineer needs to consider the amount of data being transmitted on the LON network due to LON network bandwidth limitations.  On an FTT-10 LON network, the bandwidth is limited to approximately 72 packets (messages) per second.  Because the LON network is operating using CDMA (Collision Detect, Multiple Access) communications techniques, data collisions will reduce the practical data limit to approximately 1/2 of the maximum.  Typically the LON network designer will limit the packet transmission rate of 30 to 35 packets per second. 

There are a series of NCI (configuration) objects that control the transmission and reception of these data values on the LON network.
  1. The nciSndHrtBt determines the maximum amount of time that is allowed before all bound NVOs are updated, that is, the data is marked to be "re-sent" to all bound nodes.  This value is typically set to 120 seconds, causing all bound NVO SNVT values to be transmitted at least once every two minutes.
  2. The nciRcvHrtBt sets the fallback timer value for each NVI object.  If a value is not received via a binding in this time period, the NVI object will revert to its application defined default value.  It should be noted that this value does not directly affect the LON bandwidth but it does affect how the controller handles the loss of the bound data communications.  This value is typically set to about 2.5 times the nciSntHrtBt to allow for occasional lost communications packets and delays due to data collisions occurring on the network.
  3. The nciMinOutTm controls how often a bound NVO value will be transmitted when the value is changing within the controller.  Each specific SNVT type has a specific data resolution and any time the data value changes by one count, the value will be sent.  For example a temperature value bound through a NVO as a SNVT_temp_p type has a resolution of 0.01 degrees Celsius.  If bound this temperature NVO will be transmitted each time the value changes by 0.01 degrees C.  The setting of the nciMinOutTm throttles this bound NVO value transmission by forcing the controller to ignore any changes to that NVO value for a specific time interval each time it is transmitted.   The nciMinOutTm value defaults to NA causing the bound NVO value to be transmitted each time it changes.  Typically the nciMinOutTm is set to a value in the 1 to 5 second range causing the controller to throttle the transmission of the changing NVO values.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7306
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of