Can not change schedule object property list in Viconics thermostat model VT7652H5X18
  • Can not change schedule object property list in Viconics thermostat model VT7652H5X18
  • AbeMeran
    AbeMeran
‎2018-09-06 12:38 PM
From Continuum edit the schedule that comes built in with the Viconics device and change the Object Property List then save the schedule.
The schedule object saves without error, but re-opening the schedule reveals that no change took place.
CyberStation
Viconics thermostat
Viconics does not allow changes to the built in schedule object property list.
A workaround is to put the schedule that is in the Viconics device out of service then create a schedule in the bCX that drives the desired objects in the thermostat.