Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Door Modes.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Door Modes.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1404 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Door Modes.

Picard Product_Support
‎2018-09-06 12:36 PM

Issue

Door goes to Secure mode even when there is no ATS on it.

Environment

All versions of I/net Software.

Cause

The software puts the door in the secure mode by default.

Resolution

The access control functions within TAC I/NET Seven depend partly on schedules to determine when access will be granted to individuals or groups. The following door related schedules are used for access control:

1. Mode Schedules — You can assign a mode schedule to each door in order to control what mode the door will operate in during specific times of the day. When a door is in the Locked mode, access will not be permitted regardless of any other schedules.
2. Personnel Schedules — You can define up to 31 personnel schedules for each door. Personnel schedules are only used to control access when a door is operating in the Secure or PIN Enable mode.

Mode Schedule

A door Mode Schedule controls the operating mode of the door at specific times of the day. The following door Mode Schedule actions are available:

 APB Reset — Use this action to reset anti-passback memory for this door.
 Lock — This mode inhibits entry and exit through the door. All readers and release buttons for the door are disabled while this door mode is in affect.
 Unlock — This mode allows open access through the door.
 Secure — This mode allows access only after a valid key/card has been read. All key/cards will be validated based on personnel schedules, tenant, key/card issue number, anti-passback, and access level.

 When a door equipped with a PIN pad is operating in the "Secure" mode, the PIN pad will not be enabled (that is, entry of a personal identification number will not be required in order for an individual to gain access).
 PIN Enable (firmware version 3.20 or earlier)
 OR
Sec/PIN (firmware version 3.21 or later) — When this mode is active, the PIN reader on the DPU will be enabled. This mode is the same as the "Secure" mode except that it also requires the individual to enter a valid PIN after a valid key/card read. If an individual enters an invalid PIN, the setting of the PIN Retry Count parameter in the Door Extension Editor will determine how many retries (if any) the individual can use to enter a valid PIN.

 You can schedule a door's PIN pad to become disabled without unlocking the door by following this mode with a "Secure" mode. When the "Secure" mode becomes active, individuals will no longer be required to enter a PIN in order to gain access through the door.
 Sec/Code (firmware version 3.22 or later) — This mode is similar to the "Secure" mode; however, rather than using a key/card to gain access, the user simply uses the PIN pad to enter the door's assigned code. If the individual enters the correct door code, the door will open.

 When the door is operating in the Sec/Code mode, user-definable door attributes or PIN pad functions are not available.

Note: If the door needs to be unlocked then they can manually be unlocked for that period then return to the secure mode when needed.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 7438
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore