Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,835
  • TAC IA Series 1,820
  • TAC INET 1,458
  • Field Devices 720
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 9
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 365
    • 366
    • 367
    • …
    • 507
  • Next »

Displaying setpoint values on the Proview User Interface

Issue The setpoint values are displayed briefly and then change to 621.X on the Proview display? Environment All LON proview installations. Cause This occurs when the setpoints are being written into network variable inputs (nvi).  The nvi's default to using the receive heartbeat and will fallback to default after the timeout occurs.  Proview does not perform a send heartbeat function as the connection is an nv update and not an actual binding. The receive heartbeat mechanism in the MNL controllers cause the nvi values to fallback to NA upon heartbeat timeout. Resolution The heartbeat can be disabled for the setpoint nvi, however nvi values are stored in RAM (not EEPROM) and will return to default upon a controller power cycle.  The best solution is to use network configuration inputs (nci) for setpoint displays on the Proview.  These do not have the heartbeat issue and the values are maintained in EEPROM so they are not lost following a controller power cycle.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Labels:
  • TAC IA Series
762 Views

Continuum analyzer errors in IETableCheck.

Issue Continuum analyzer reports errors in the IE Table Check. Environment Cyberstation Cause Errors need to be cleaned up using the Continuum analyzer. Resolution Clean up the errors using the Continuum analyzer then run the tests again to verify errors where corrected. If everything appears to work correctly then there is no need to reload the IE table to the controllers, otherwise: Send the IE table to CX level controllers. To send only the IE table select the 'Do not reload attached objects' in the 'Send To Controller Options' dialog window.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Labels:
  • Andover Continuum
994 Views

MNL-800 will not communicate with the programming or network management software tools.

Issue The MNL-800 controller will not communicate with the WorkPlace Tech tool nor will it communicate with LON network management software tools such as LonMaker or the I/A Series (Niagara) R2/G3 LON Device Manager software. Symptom - Controller LEDs (top to bottom) Green Power and Transmit Data (Green) – on solid (normal power condition) Receive Data (Yellow) – may be flashing if data present on the bus Service (Red) – flashing a repeated abnormal pattern (long flash / short flash) Heartbeat (Green) – alternates on and off at a half second rate (normal) Environment MNL-800 on existing or new LON network WorkPlace Tech Tool software or LON Network Management software Cause An analysis of field returns has identified a condition where the MNL-800 fails to communicate and appears to be resetting continuously. The controller has entered a condition where the Neuron’s image has been deemed corrupted due to an application checksum error or signature inconsistency. When this occurs, the Neuron is unable to complete the startup sequence resulting in the MNL-800 continuously resetting. Resolution Follow the procedure documented in TPA-RKFD-09-0005.00 to reconfigure the communications processor in the MNL-800 controller. In the unlikely event that this procedure does not correct the communications issue, please contact Product Support Services for additional assistance.
View full article
Picard Product_Support
‎2018-09-06 01:38 PM

Labels:
  • TAC IA Series
2644 Views

M-Bus Protocol Information

Issue What resources are available to get more information on the M-Bus protocol? Product Line Andover Continuum, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment M-Bus Cause The M-Bus protocol information is available on www.m-bus.com. Select The M-Bus: A Documentation Rev 4.8 Resolution The M-Bus protocol specifications is broken down in multiple chapters. Basics of Serial Bus System Overview of the M-Bus Physical Layer Data Link Layer Telegram Format, Meaning of Fields, Communication Process Application Layer Structure of fixed and variable data blocks. Network Layer Appendix Table of units, medium, data field codes, VIF extensions.
View full article
Picard Product_Support
‎2018-09-10 12:11 AM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2558 Views

Adding rows to the device editor in Xbuilder

Issue The Xbuilder device editor by default only allows 200 lines, and some integration efforts require more than 200 points to be programmed. Environment Xbuilder Device Editor Cause The device editor only has 200 rows by default. Resolution The device editor is designed with excel functionality meaning, new rows can be added to allow for more points to be programmed. To add rows to the device editor follow these steps: Open the device editor. Right click on the row number. Choose insert row. Type in the desired number of rows (up to 100) If more than 100 are needed repeat steps 2-4.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC Vista
851 Views

Is there a way to keep resending alarm notifications until they get acknowledged in R2?

Issue Is there a way to keep resending alarm notifications until they get acknowledged in R2? Environment R2, WorkPlace Pro (all versions) Cause N/A Resolution R2 does not provide a way to resend an alarm, already in an alarm state, until it gets acknowledged.  Resending alarms is possible in G3
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
848 Views

Will Access Events in controller buffer persist on power failure or reset?

Issue A power failure at the site causes all CyberStations to shut down, will the CX controllers buffer access events? what happens if the controller resets as a result of power glitch? Environment Cyberstation CX9702 CX9900, CX9940 CX9680 ACX5740, ACX5720 Cause -Power failure or controller reset due to electrical noise during thunder storm. Resolution 1. All controllers will buffer access events when they lose communication with the primary and secondary access server. 2. If the controller resets as a result of a power loss that exceeds the UPS capacity or due to a glitch or spike in the power line then whether the events will persists or not depends on the controller type. CX9702, CX9900 and CX9940 Access events in controller buffer will be lost CX9680, ACX5740 and ACX5720 Internal battery will keep RAM intact for up to 30 days Controller will warm start after a glitch or spike in the power line and maintain the events in its buffer. *** NOTE If controller has to cool start (restore its objects from flash memory) then the access events in the buffer WILL BE LOST. 
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • Andover Continuum
979 Views

Event time stamps in SQL database do not match those viewed in Vista

Issue When a SQL query is run on taclogdata to view events or trend logs, the time stamps returned differ by an hour or more from the those of the same events when viewed in Vista. Environment TAC Vista 4.3 and higher MS SQL Server Cause All time stamps are stored in taclogdata as UTC (Universal Coordinated Time) regardless of your local time zone and DST (Daylight Saving Time) settings. When you view events or trend logs in Vista, the Time Zone and DST settings of your Workstation are added to the UTC time so that you see time stamps synchronized with your local time. This does not occur when a SQL query is run directly on taclogdata. Resolution If you need to query the Vista SQL database directly, you could use the DATEADD function to calculate your local time from the UTC values, e.g. in SQL Server Management Studio run the following query to show the EventId, UTC time and local time for all events that occurred in the last 24 hours. USE taclogdata; SELECT EventId, EventDatetime, DATEADD(hour, datediff(hour, getutcdate(), getdate()), EventDatetime) AS LocalTime FROM Event WHERE EventDatetime > DATEADD(day, -1, GETUTCDATE()) Please note:  DATEADD adds a fixed offset to the input time.  It does not compensate for start and end dates of DST. 
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC Vista
1587 Views

Upgrading the version of WorkPlace Tech from 4.x to 5.x. What is the correct part number to select in the "Purchase WorkPlace Tech software" program?

Issue An end-customer purchased WorkPlace Tech 4.x several years ago and is retiring the computer.  The new computer will have the latest version of WorkPlace Tech.  Which part number applies to this upgrade from 4.x to 5.x? Environment WorkPlace Tech 5.x Cause Host computer is being replaced. Resolution In the "Purchase WorkPlace Tech software" program, choose the part number:  WP-TECH-50U. When submitting the unlock code request, ensure that the original order number and/or PO number is included so that Customer Service can confirm that it is an upgrade, and invoice using the lower cost upgrade cost.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
1161 Views

A 3rd party BACnet controller (Cisco Mediator) can read exposed objects in the Niagara R2 station but cannot write values to them.

Issue A Cisco Mediator controller is connected via BACnet/IP to a Niagara R2 UNC.  The UNC station provides data to and receives commands from the controller.  The Cisco Mediator controller can read BACnet values but when it attempts to overwrite setpoints and issue commands, they do not work. Environment Niagara R2 all versions Cause The installation contains 3rd party BACnet controllers that must share data and commands. Resolution To allow other BACnet controllers to write values or issue commands to exposed Niagara objects, a special "BACnet" user is required for the station. To create this special user, follow the steps listed on pages 4-6 & 4-7 of Tridium's BACnet Integration Guide.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
1209 Views

Repeated FLEXnet License errors warning that license is about to expire or has already expired

Issue Multiple FLEXnet License File errors warn that the license file is about to expire or has already expired. Errors may be logged in Windows system log that may look something like this: (2372) Feature: Micronet.VisiSat.Core, expires on 30-apr-2011. This is a two week notice. Multiple errors may pop up at once or may only occur daily. Here are two examples of messages you might see. Event Type:      Warning Event Source:    taclic_LicenseServer Event Category:          FLEXnet License File Event ID:        718 Date:            30/04/2011 Time:            12:00:52 AM User:            N/A Computer:        BMSSERVER Description: (2372) Feature: Micronet.VisiSat.Core, expires on 30-apr-2011. This is a two week notice   Event Type:      Error Event Source:    taclic_LicenseServer Event Category:          FLEXnet License File Event ID:        716 Date:            5/17/2012 Time:            2:55:15 PM User:            N/A Computer:        G15HVAC Description: (2516) This license (Vista.Server.LNS) has expired. Environment FLEXnet License Server Cause A valid site license and demo license have been left in the Vista license directory. The system message is letting you know that the demo license will or has already expired. Resolution Remove or relocate the demo license once it is no longer required on site. This will prevent this error message from appearing in the Windows Event Viewer.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC Vista
1231 Views

Sequencing Discrete Outputs without using an Event Sequence

Issue Need to sequence several outputs to be on for 10 seconds then off for 15 then the next on for 10 and so on, but the site has specified no event sequences are to be used. Environment I/NET DDC Cause Need to sequence several outputs to be on for 10 seconds then off for 15 then the next on for 10 and so on, but the site has specified no event sequences are to be used. Resolution Create a DDC relay for output 1 that is an interval timer relay with the time set to 10 (time the device is on) Set the DI select to an input trigger point Create a second DDC relay to function as a delay before make relay. Set its time to 25 seconds, or the device on time plus the interval time before the next output. Set the output of this relay as a Line and the DI select as the trigger point. Copy the DDC relay from step 1. Change the DI select to the line from the previous step and the Output to the next device in the series. Copy the DDC relay from step 2. Change the DI select to the output triggered in the previous step and change the Output to a new line. Copy the DDC relay from step 1. Change the DI select to the line from the previous step and the Output to the next device in the series. Copy the DDC relay from step 2. Change the DI select to the output triggered in the previous step and change the Output to a new line. Repeat steps 5 and 6 until you have completed the series. If you wish for this to cycle in a loop, have the output from the last Relay trigger the DI point which starts the series. If this is an internal point you may want to add a calc to keep it equal to 0.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC INET
1154 Views

Continuum Version 1.93 Fails to install

Issue Receive AccDataservice errors on startup. Environment Windows 7 Windows 2008 Server Continuum 1.93 Cause Security enhancements needs to be disabled during the install of Continuum. Resolution The list of services needs to be disabled before installing Continuum. These services can be re-enabled after the install completes. Windows Firewall.   Private, Domain and Public Windows Defender. Windows Software Protection Service. Antivirus Protection.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • Andover Continuum
1351 Views

Input (UI4) XP expansion module attached to BCX not updating.

Issue InfinityInput (digital) not changing value when dry contact on relay changes state. Tried disabling and changing value but will not change. On bacnet side the point is set to out of service and will not change. New input points created on the UI4 are also out of service on bacnet side and will not change. Tried powering down expansion module - no luck. Tried deleting point on Infinity side and saving to database on bacnet - works fine. But when recreating the input, comes up the same way.   Environment bCX, 4040, bCX4040,  XP Expansion Module UI4, UI-4  Cause InfinityInput (digital) not changing value when dry contact on relay changes state. Resolution Replace UI4 with bCX powered off. Delete the point on Infinity side, save controller to database on Bacnet side. Drag & drop input from another bCX on Infinity side.  Save to database on Bacnet side. Point starts updating and is no longer out of service.  See also
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • Andover Continuum
1118 Views

Automatic login into a Continuum system

Issue When a user logs off a Continuum workstation, they would like the workstation to login itself maybe via a program as a Guest so that the systems can be viewed (Guest Mode).   Environment Continuum Cyberstation and webClient (all versions) Cause Continuum is a security system, and as such, it requires a login for auditing purposes. Resolution There are no supported applications or features to provide auto-logins to Continuum.  Continuum is a security system, and as such, it requires a login for auditing purposes.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • Andover Continuum
1221 Views

Procedure for obtaining a Return Authorization (RA) for a defective I/A Series (Niagara) G3 ENC

Issue Procedure for obtaining a Return Authorization (RA) for a defective I/A Series (Niagara) G3 ENC Environment ENC-410, ENC-520 Cause Unknown - ENC is not functioning and needs to be repaired or replaced Resolution To request a Return Authorization for a defective ENC controller, the factory will need to know the following information: The product part number (ENC-???-?-?) Is the unit still under warranty? Warranty note: Warranty on a new UNC is 2 years from date of manufacture. The date code format is yyww. Example:  0815 is  2008 week 15 Serial number Job name (site name for unit) Factory order number Project ID Host ID (in the license file) The reason for return Network settings (IP, Subnet, name) Username and Password Station DB Username and Password Any special shipping instructions Have a purchase order number ready when you call. Note: Customer Support Services sends/bills for advance warranty replacement units. When the customer returns the correct unit within 30 days, a credit is then issued., Call Schneider-Electric at 888-444-1311 and select option 2 (Product Support). Product Support will enter a support case identifying the unit and that an attempt to troubleshoot was done prior to issuing the RA number. The caller should request the Product Support Case number and RA number for future reference. An RA will be issued based on the following criteria: Credit AWR (Advance Warranty Replacement). Customer is sending back an inoperable unit to the factory for credit and needs a replacement unit right away. OOWR&R (Out of Warranty Repair and Return). Customer sends back an inoperable unit to the factory for repair and return. IWR&R (In Warranty Repair and Return). Customer sends back an inoperable unit to the factory for repair and return. NOTE: When issuing an AWR, hold the defective unit and use the packaging from the replacement to return the UNC board. This will help guarantee that the units are not damaged during shipment. When the units are received damaged and improperly packed, they are returned as received and no credit issued.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
1122 Views

Configure a Niagara G3 ENC serial port for dialup modem

Issue How to configure a Niagara G3 ENC serial port for dialup modem. Product Line TAC IA Series Environment ENC-520-2 ENC-410-1 Cause Dialup modem setup. Resolution In the Station, under Platform Services, go to the SerialPortService In the Port Config field, change the setting to Com1_232_com2_modem. Save this setting. Now, go to the Platform of the ENC, and go to Dialup Configuration The Init String should look something like this: ATE0S0=0Q0V1X4&D2&K3\N3%C2&C1&Q5W2 Change the 0 just after the "=" sign to a 2.  This will tell the modem to answer on the second ring. Make sure that the Port field says COM2 Check the Enabled box next to Listen for Calls In the Local IP Address field, type in the IP address of the ENC In the Remote IP Address field, type in an unused IP address on the same subnet as the ENC. Type in a User Name (eg. invensys) Type in a password (eg. niagara) Save your changes, then click the Start button at the bottom of the page.  This will start up the dialup daemon. Re-boot the station in Station Director.
View full article
Picard Product_Support
‎2018-09-06 01:33 PM

Labels:
  • TAC IA Series
1593 Views

Can Continuum Add-On Report Suite objects be displayed in Webclient?

Issue Continuum add-on reports can be installed on the webclient PC, but can they display through a browser? Environment Continuum Webclient Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Continuum Add-On Report Suite were not designed to be displayed through a browser with webclient Resolution   Continuum Add-On Report Suite were not designed to be displayed through a browser with webclient. The reports can be installed and accessed on the Cyberstation part of the Webclient PC itself, but they will not display through any of the browser PCs that connect to that Webclient PC.
View full article
Picard Product_Support
‎2018-09-06 01:33 PM

Labels:
  • Andover Continuum
1184 Views

RAM - SMS messages are truncated.

Issue When Remote Alarm Manager sends a SMS message via a GSM to a mobile phone, the message is truncated.  Environment Sigma, Micronet, BAS, RAM Cause Message type - Long Message (Descriptive multi line message) Output interface - GSM to mobile phone. If an alarm is sent from an output interface e.g Sigma to an output interface e.g SMS mobile phone, the end of the message disappears (truncated).  Resolution The message sent to the mobile device is too long. A maximum length of 160 characters is permitted - this is a SMS message characteristic. Consider changing the message type to a Normal message or Short message or The Index Title and Point Title are very long, can these be shortened. e.g change Temperatures to Temps.
View full article
Picard Product_Support
‎2018-09-06 01:33 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
919 Views

Unable to backup an R2 UNC-520 database, receive error "java.net.ConnectException: Connection refused: connect at java.net.PlainSocketImpl.socketConnect(Native Method) at ja...

Issue Unable to backup an R2 UNC-520 database, receive error  "java.net.ConnectException: Connection refused: connect at java.net.PlainSocketImpl.socketConnect(Native Method)            at java.net.PlainSocketImpl.doConnect(Unknown Source)         at java.net.PlainSocketImpl.connectToAddress(Unknown Source)            at java.net.PlainSocketImpl.connect(Unknown Source)            at java.net.Socket.connect(Unknown Source)   at java.net.Socket.connect(Unknown Source)   at java.net.Socket. (Unknown Source)           at java.net.Socket. (Unknown Source)       at tridium.nre.drivers.SocketDriver$TcpSocketFactory.createSocket(SocketDriver.java:690)        at tridium.nre.drivers.SocketDriver.create(SocketDriver.java:216)            at tridium.nre.drivers.SocketDriver$ConnectThread.run(SocketDriver.java:510)" Environment I/A Series R2 UNC-520 I/A Series R2 WorkPlace Pro,  error reported in build r2.301.529 Cause The WorkPlace Pro cannot connect to the UNC-520 at the given IP address.  The error message stems from a bug in the Sun java, "The Socket constructor does not give an Exception on an unknown IP address. It just hangs."  http://bugs.sun.com/bugdatabase/view_bug.do?bug_id=4232651 Resolution Verify that the UNC is capable of communicating at the IP address specified. For example, if the UNC is rebooting constantly, it will not be able to communicate.
View full article
Picard Product_Support
‎2018-09-10 12:17 AM

Labels:
  • TAC IA Series
1236 Views
  • « Previous
    • 1
    • …
    • 365
    • 366
    • 367
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login