Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to move I2 controllers from one port to another on the same parent controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to move I2 controllers from one port to another on the same parent controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116827
    sesa116827
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1402 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to move I2 controllers from one port to another on the same parent controller

Picard Product_Support
‎2018-09-06 02:17 PM

Issue

Cyber 1.82: 9400: Infinet commports 1 and 2: what happens if he surpasses the threshold of 127 per commport for infinet. Currently he has one commport that has 14x controllers on it. Wants to move some controllers to a different port.

Product Line

Andover Continuum

Environment

Cyber Station Version 1.xx

CX9400 controller.

Various versions of I2 controllers.

Cause

Reached the max controller limitations a single comm port. of 127 per port.

Resolution

  1. Get a Current Database Backup and create dmp files as needed.
  2. Go offline editing
  3. Change the serial numbers of the original controllers to a false serial number.
  4. Manually create all the Infinet controllers on the new destination commport assigning them the same or available Infinet ID as the controller that is on the original commport but a false serial number.
  5. Drag and drop copy all the points and programs from the original controller to the new controller.
  6. Verify that all the points and programs were correctly copied and are intact.
  7. Then go into the new controllers and change their serial numbers to what the serial numbers of there originating controllers were.
  8. Then move the physical infinet connection from the original commport to the new commport.
  9. Next go back to online editing. At this point you should see all your infinet controllers come back on line.
  10. Reload the controller that previously owned the Infinet controllers
  11. Reload the controller that how owns has the Infinet controller
  12. Finally reload the complete site. This last step is essential to ensure that there are not lingering handle conflicts.

It is important to note that any controllers that are referencing points in the relocated controllers will have to have these object references verified and repaired in cases where the references have been lost.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4310
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of