Unable to copy graphics components from one graphic to another
  • Unable to copy graphics components from one graphic to another
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:17 PM
When copying a graphic point, symbol, bitmap, table or anything from one page to another, everything is placed to the upper left of the new page and is all jumbled up. The user has to move each one separately and the attributes do not remain the same.
In I/NET 2.40 and above Windows will still cause text object to be placed in the upper left hand corner. This also occurs in the Windows Paint program.
I/NET Seven revision 2.16 and higher, but below 2.40
Copying a graphic point, symbol, bitmap, table or anything from one page to another.
This issue is resolved in I/NET 2.40.  If upgrading is not an option:
  1. Contact PSS and request the patch that is available to fix this issue.
  2. Copy the files into the root directory of I/NET
  3. Run the graphic again
Workaround for I/NET 2.40 and above
  1. Group the objects you wish to copy by pressing CTRL+G
  2. Copy the group
  3. Paste the group and move it as desired
  4. Ungroup the objects.
  • TAC INET
Tags (2)
  • 4326
  • ChrisAsbury22
100% helpful (1/1)