%N and %D showing in AlarmEnrollments instead of name
  • %N and %D showing in AlarmEnrollments instead of name
  • Chris_Asbury
    Chris_Asbury
  • AdamSteele
    AdamSteele
‎2018-09-06 02:16 PM
Upgraded site to Continuum 1.91, now get %N and %D in AlarmEnrollments
  • Windows Server 2008
  • SQL 2008
  • Continuum 1.91
  • Keywords %D %N
This is a known issue in Continuum version 1.91
Contact PSS for the %N %D hot fix file.
If using Continuum 1.90, Apply SP1 and then follow these steps: (1.91 and above contains the fix, but may still need the steps)
  1. Close the workstations
  2. Reboot the server
  3. Initialise the database making sure you have Enhanced Alarm Logging and Enhanced Alarm Delivery ticked
  4. Initialise workstations
  5. Reload all controllers
  6. Clear any old alarms and test by creating a new alarm
They should now display the correct text.
  • 4343