Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 264
    • 265
    • 266
    • …
    • 509
  • Next »

Limit what is available to the user on a dedicated I/NET host on the Ethernet

Issue Limit what is available to the user on a dedicated I/NET host on the Ethernet. For example, I do not want the user to be able to get to a DOS prompt then modify the Routing Table. Environment I/NET site Cause Limit what is available to the user on a dedicated I/NET host on the Ethernet. For example, I do not want the user to be able to get to a DOS prompt then modify the Routing Table. Resolution This can be done. Remove the DOS icon from Windows. Or, it may be better to edit the permission rights of the user.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
975 Views

On Screen Indication of a Telnet session into a NPR

Issue On Screen Indication of a Telnet session into a NPR Environment Telnet NPR Cause Indicating to the user when a telnet session has been initiated into an NPR. Resolution "CSI NetPlus Router Telnet Server" "Connected to remote NPR” (Name of the NPR) followed by version number, build, and date "Type help for a list of commands"
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
910 Views

Add entries in the host's routing table

Issue How to add entries in the host’s routing table Environment Command Prompt Cause Routing Table Errors Resolution As an example: add the address 157.0.0.0 Go to a DOS screen and type the following: Route add 157.0.0.0 Then type: Route Print This address should appear.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
973 Views

Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchron...

Issue Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchronous if they install an integrated dial modem on the serial port of the same PCU? Environment I/NET site Cause Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchronous if they install an integrated dial modem on the serial port of the same PCU? Resolution No, but you do need to use the correct modem, cables, settings, profiles, etc.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1174 Views

The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP?

Issue The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP? Environment I/NET site Cause The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP? Resolution Yes, by design the 78010 TAP emulation is still functional.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1321 Views

Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded

Issue Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded Environment I/NET site Cause Should the site change the EPROM? Resolution We strongly recommend you do. If the PCU goes to “Boot-State”, the SYNCHRONOUS EPROM in the PCU will not reset the asynchronous ADAA modem correctly. You won’t be able to dial into the ADAA port of this controller until this is corrected by doing a download or changing the EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
953 Views

Add a stand-alone 7798 to the existing controller LAN

Issue Add a stand-alone 7798 to the existing controller LAN Environment I/NET site Cause How to add a stand-alone 7798 to the existing controller LAN Resolution A CLX card is required. Refer to TCON 138.
View full article
Picard Product_Support
‎2018-09-06 11:09 PM

Labels:
  • TAC INET
1146 Views

Sync LED on FOI still on after correcting the line fault on the output of the CRR.

Issue I never reset the "Sync" LED on the FOI after I corrected the line fault on the output of the CRR. Will this cause any communication problems? Environment I/NET CRR Cause Line Fault Resolution Reset the sync LED If you can NOT extinguish the Sync LED you should find the fault. Leaving this light “on” does not cause communication problems.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1013 Views

ADAA problems: can not dial in or out of the site

Issue ADAA problems: can not dial in or out of the site A PCU is set up as a 06 TAP. The RX and TX LEDs are flashing on the RS-232 card. A CBL048 cable is connected from the RS-232 card to the modem. The RD and SD lights are flashing. Environment ADAA Cause The wrong BIN file is in the PCU. Resolution You have the wrong BIN file in the PCU. If the PCU is at the “Boot State”, you may have the wrong EPROM too. Install the correct BIN file; and it is strongly recommend to put in a compatible Asynchronous EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
952 Views

Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU

Issue Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Environment I/NET Site Cause Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Resolution The outputs from these locations are DC. This may cause the AC relays to “chatter” or not work at all. It is recommended to use a P8UI8DO at the expansion board or place DC powered, form “C” contacts, pilot relays on the outputs of the PCU. Refer to TCON106 for more details.
View full article
Picard Product_Support
‎2018-09-06 11:12 PM

Labels:
  • TAC INET
1287 Views

Door show Deny Entry Schedule after deleting a special day schedule on the special day

Issue Door show Deny Entry Schedule after deleting a special day schedule on the special day Environment I/NET Access Control Cause The process to execute the Special Day begins at midnight on the first day of the duration, and ends at the end of the last day of duration. If you delete the Special day while it is running you will get denied entry. Resolution Do not Delete special Day schedules on special days Modify the special day schedule to match the desired access control results. On the next non-special day, Delete the schedule If you have already deleted the special Day or special Schedule Option A - Delete the special day from the Host and the Controller     Perform a station restore to force the controller to use the current programming Option B - Determine which special day schedule type the controller is operating on Modify or create a schedule for that special day with the desired access privileges On the next non-special business day, enter the desired programming for special days.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1101 Views

Docutrend data import fails while connected to a physical 78010 tap.

Issue Docutrend data import fails while connected to a physical 78010 tap. Environment I/NET site Cause Docutrend data import fails while connected to physical 78010 tap. Resolution The system or hardware number in your active profile is different compared to the 78010 tap. Change the profile to match the site 78010 tap.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1115 Views

DPU required signal to add fingerprint verification to a card read before access is granted

Issue In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Environment I/NET Access Control Site Cause In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Resolution DPUs require a 26-bit Wiegand format.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1145 Views

Does Configuration Server for an i.Lon 1000 have to be running all of the time?

Issue Does Configuration Server for an i.Lon 1000 have to be running all of the time? Environment i.LON 1000 Cause The Config Server provides the path for communication to the iLon when used as an RNI. Resolution If using the i.Lon 1000 as an RNI to communicate with the LonWorks network, then the Config Server must be open.   If the i.Lon 1000 is being used as a router (not RNI), it is not necessary to have Config Server running unless you are in the configuration process for the router.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1177 Views

Dial Network and LNS Network in the same Vista Network

Issue Is it possible to have a Dial Network and LNS Network in the same Vista Network? Environment Vista Network Dial Network LNS Network Cause  A dial up network communicates via the PC comport directly (no LTA driver), therefore there is no conflict with LTA card drivers (like the conflict that occurs between Classic and LNS networks). Resolution There is no problem having both types of communication in a single Vista network.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1312 Views

When will the connection in a Dial network disconnect?

Issue When will the connection in a Dial network disconnect? Environment Xenta 901 Cause The 901 connection will continue as long as live values are being viewed. Resolution If the Status window is open (for example), the connection will continue until that window (and any other window viewing live data) is closed.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
873 Views

Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit?

Issue Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit? Environment XBuilder Cause Regional settings can be project wide or per point. Resolution When creating a new TAC Xenta 511 project, select to use US values. You can also select conversions to occur per object.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
931 Views

Is it not possible to have multiple Xenta 901s from multiple sites in a single LNS network

Issue Is it possible to have multiple Xenta 901 controllers from multiple sites in a single LNS network and access the remote sites as needed? This would leave any controllers not connected offline. Environment TAC Xenta 901 LNS Network Cause TAC Xenta 901 is an "LTA" and in TAC Vista there can only be one per LonWorks network. Resolution Create one LNS database per TAC Xenta 901. You can have up to 240 TAC Xenta 901 networks per TAC Vista Server (all can dial up the same TAC Vista Modem(s)). Add another TAC Vista Server if you need more dial up connections.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
977 Views

How to adjust the illumination level on the 7798 (B)

Issue How to adjust the illumination level on the 7798 (B) Environment I/NET site Cause How do you adjust the illumination level on the 7798 (B) Resolution Function Keys F7 increases the level; F8 lowers the level. Older 7798s do not have this feature.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1127 Views

Conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC

Issue Conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC Environment I/NET site Cause Need for conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC Resolution M = 0.01666; B = -2.1333. The resolution counts range is 68 to 188.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1056 Views
  • « Previous
    • 1
    • …
    • 264
    • 265
    • 266
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of