Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC INET
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac inet"

View in: "Building Automation Knowledge Base" | Community

1444 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 21
    • 22
    • 23
    • …
    • 73
  • Next »
Label: "TAC INET" Show all articles

DbCreate now displays the revision level and description of SQL in the Help About box

Issue How can I determine what version of SQL I/NET is using? What version of SQL is installed on the I/NET PC? Product Line TAC INET Environment I/NET Seven 2.10 and above For previous versions of I/NET refer to How to determine the SQL version you are running with I/Net Seven. Cause To find out what version of SQL is installed and used by I/NET Seven site PC. Resolution A new feature was introduced in I/NET Seven Revision 2.10 that allows you to view both the I/NET revision and SQL revision installed.  To view this all I/NET applications and the IO Server must be shutdown before performing the following steps: Start DBCreate >Start> All Programs> INet>DBCreate Login screen is shown, select either Windows login or enter the SQL Server Authentication details and click OK Right-click on the Title area shown in red below:   After Right-clicking, select from the menu options About...   The About DBCreate screen will then be shown and you can see both the I/NET Seven Version and SQL Versions as shown and highlight below: For I/NET Revisions prior to 2.10 then refer to How to determine the SQL version you are running with I/Net Seven on how to view what version of SQL is installed.      
View full article
Picard Product_Support
‎2018-09-11 08:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:17 PM

Labels:
  • TAC INET
1455 Views

I/NET DBCreate database restore fail

Issue DBCreate database restore fails with error message: "The backed-up database has on-disk structure version 611. The server supports version 539 and cannot restore or upgrade this database. [Microsoft][ODBC SQL Server Driver][SQL Server]RESTORE DATABASE is terminating abnormally." Product Line TAC INET Environment I/NET Seven SQL Server 2000 all editions and SQL 2005 all editions Cause It is not possible to restore a SQL Database which was backed up using SQL 2005 back into a SQL 2000 database. Resolution The simplest method to rectify this problem would be to uninstall I/NET and SQL (Refer to Procedure for uninstalling I/NET Seven on a stand-alone host on how to do this) and then re-install I/NET using SQL 2005. The second method would be to upgrade the installed MSDE Default instance to SQL 2005 Express. There is a published white paper from Microsoft on this and is attached here: MSDEtoSQLExpress.doc.  Refer to the steps on page 11 to 14. The SQLExpress installation file is available on the I/NET CD under the folder SQLExpress\.SQLEXPR32.EXE. After performing these steps its advisable to run up DBCreate and upgrade the SQL database.
View full article
Picard Product_Support
‎2018-09-11 08:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:16 PM

Labels:
  • TAC INET
2916 Views

Import all converted I/NET graphic folders into EcoStruxure at one time

Issue In order to make page links between different I/NET graphic folders work fine, the same folder structure needs to be created manually in EcoStruxure / SmartStruxure. Refer to Converting I/NET graphics to TGML using the "Create Source Tree" option to realize this. Product Line EcoStruxure Building Operation, TAC INET Environment EcoStruxure / SmartStruxure 1.4 or higher I/NET Cause The I/NET graphic folder structure will not be created automatically before SmartStruxure 1.4.0. Resolution Starting in version 1.4.0, there was a new feature called Data import for I/NET graphic. Using this feature, all the converted I/NET graphic folders structure can be imported at one time without any need for manual work. Here are the steps to make it work: Convert the I/NET graphics according to Converting I/NET graphics to TGML using the "Create Source Tree" option, but do not create the folder structure manually in EcoStruxure / SmartStruxure. Create the default Inet Graphics folder by right clicking on I/NET Interface-->New. Right click on Data Import and choose the root folder of all of the I/NET graphics. Click OK. Data importer will check all the file names and bindings. If any error happens, check and fix it before importing again. (Currently apostrophe is not supported in SmartStruxure. Change the name and relative link and do it again. It may be fixed in later version) Check whether all the bindings and links work fine. Important: Currently this feature doesn't support export/import in SmartStruxure. It will fail to import if any sub folders are contained under INET interface. This may be fixed in later version. The workaround is to still create the whole structure according to Converting I/NET graphics to TGML using the "Create Source Tree" option.
View full article
Picard Product_Support
‎2018-09-11 10:10 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:13 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1648 Views

BMS Application assistance

Issue Need help with programming Need help to make graphic Installation questions Forum Environment BMS Security Video Cause A great way of getting help with various application programming and graphic making is to spread knowledge between all the great technician out there. A forum exist for this and people worldwide that works with SE Solution share their knowledge here. Resolution Please enter the forum by the link below. http://community.se.com/welcome
View full article
Picard Product_Support
‎2018-09-06 12:13 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:59 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • Field Devices
  • TAC IA Series
  • TAC INET
  • TAC Vista
3498 Views

HID PIN Pad reader for I/NET Part Number

Issue HID PIN Pad reader for I/NET Part NumberHID PIN Pad reader for I/NET Part Number Product Line TAC INET Environment I/NET Access Control Cause HID PIN Pad reader for I/NET and which part number to use? Resolution iPortal shows several PIN pad readers from HID (HID-6136CKD000214 HID-6136CKD000009) but only one works with I/NET.  Here is a pdf document which helps to explain which part number works with I/NET. The 09 means the 8 bit blast which is required for compatibility.  Want to use Pin Pad only without using the proxcard? The RK40  will do Prox only or Prox + Pin but not Pin only. See Essex Pin Pad Reader programming for Pin Only or for higher security Pin Only see Code-Guard Scramble Pin Pad Reader Programming.
View full article
Picard Product_Support
‎2018-09-10 07:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:42 PM

Labels:
  • TAC INET
1898 Views

DVR incorporated with I/NET Seven and Pelco Integral or Digital Sentry

Issue DVR incorporated with I/NET Seven and Pelco Integral or Digital Sentry Product Line Pelco, TAC INET Environment I/Net Seven Pelco Integral or Digital Sentry DVR CCTV Cause Send back a Integral DVR and it comes back as a Digital Sentry or confusion revisions of I/NET Seven and Pelco Integral of Digital Sentry Resolution This chart to clarifies which versions of I/NET Seven are compatible with which Pelco DVRs: For the latest products (after 2.31 revision) please visit Software and Firmware compatibility matrix for older versions of the traditional product lines which has the most recent Pelco compatibility.
View full article
Picard Product_Support
‎2018-09-07 03:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:38 PM

Labels:
  • CCTV
  • TAC INET
2012 Views

NPR 2000 offline despite power cycle

Issue What if an NPR 2000 goes away and never comes back even after cycling power to it? Product Line TAC INET Environment I/NET site Cause Cold starting an NPR 2000 is a common troubleshooting technique to clear up a number of communication problems that may arise. Resolution If said NPR stops communicating and doesn't come back no matter what, you should cold start it and do a software restore. (See that procedure in How to cold start an NPR 2000.)
View full article
Picard Product_Support
‎2018-09-06 11:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:37 PM

Labels:
  • TAC INET
1574 Views

"No entries in data base" when attempting software restore

Issue Edit > Host Computer > Software Restore results in pop-up error "No entries in data base" Product Line TAC INET Environment I/NET Seven host Cause The network configuration does not have any entries saved in the database. Resolution Go to Edit > Host Computer > Network Configuration In the Link Summary window, find the correct Link. If the Cnf column has a plus sign (+) in it, then this link is not saved. If the correct link is not shown, reference Error: "No Entries in Database" for more information. Highlight the correct link and press "Save" With the correct link highlighted, click "Penetrate" Any controller with a + in the Cnf column has not been saved. Click "Save All" Hit "Close" on the Station Summary and "Close" on the Link Summary. There are now entries in your database. The software restores should now show the correct options. For instructions on performing a software restore, see How to upgrade bin and SAV files in I/NET controllers
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:31 PM

Labels:
  • TAC INET
1768 Views

Deny Entry Tenant Messages in I/NET AMT

Issue A Deny Entry Tenant Message is given instead of a valid card read. Product Line TAC INET Environment I/NET Seven AMT Cause The Deny Entry Tenant message is delivered when the credential read is not known to the controller for any of the following reasons: The door being read is not part of the individuals tenant. The SLI does not have the correct database Card Translation is incorrectly enabled/disabled in the door editor There is a hardware error with the Card reader. Resolution General Steps: Determine if the issue only happens to a single individual or a group or all cards. Select Access>Tenant. Verify that the door has been added to the correct tenant(s) Select Edit>Individuals and browse to the card(or a test card) in question. Verify that the card has the been added to the door correctly. Follow the directions in How to force a download of card data to force a download. If this fixes the issue, go to the "SLI does not have the correct database section" In AMT, select window options and add the message column to the window Find a Deny entry tenant message and see if the message column matches up with Hex card number for the badge that was read. If all you get is a scrambled number, There is probably a hardware error. Verify Card Translation is Enabled (this section assumes you are using large card number format) Select Access>Doors Modify the door in question Check the box next to "Card Translation". If this option is not available you will need to flip Dip switch 7 on the SCU Compare this setting to a few other doors on the system. Thy should all have the same setting Hardware Error The easiest way to prove a hardware error is to plug a spare card reader directly into the DPU or SCU. If the problem is immediately solved replace the field reader. If not, try unplugging other readers on the controller and see if the problem goes away for that reader. It is possible that the controllers power supply is no sufficient to power the reader. Use an external power supply instead. Various known fixes for SLI database Errors: Take the SLI to it's boot state and restore bin file and database files from the Server If you are using I/NET 2.15-2.21, upgrade to 2.31 Insufficient memory: The SLI will allocate memory for all possible individuals in a tenant regardless if they are used or not. For example, if the site has only 500 cards, but the tenant is set to 32000 individuals, this will use the same controller memory as a site with 25000 individuals.  Reducing the number of individuals allocated in the tenant has been shown to clear up Denied Entry Tenant messages. System traffic: In I/NET 2.31 and above, the filemaster or server will indicate when badge data is being downloaded on a status bar in the bottom right hand corner of the screen. If this indicator is constantly showing downloads, it is due to poor system communication causing constant polling of the database.  Follow these steps to fix this issue. Turn Automatic DPU restore off on all links and wait for the download messages to stop. (this is done by selecting Edit>Host Computer>Network Configuration, then modifying each link) Wait for the automatic downloads already requested to finish. Re-enable Automatic DPU restore on each link, one at a time. Wait for the system to finish individual downloads before moving on. When you find a link that take an excessive amount of time (compared to others) to finish downloading, troubleshoot that links controller LAN wire.
View full article
Picard Product_Support
‎2018-09-06 12:20 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:26 PM

Labels:
  • TAC INET
1911 Views

I/NET Alarms to SMS (TAC Informer options)

Issue If using TAC Informer (Product development within Australia / New Zealand region), product has no further support and now longer works with I/NET Seven 2.40 or higher.  Receive either of the following errors: * I/Net Alarms     'Alarms' I/Net connect failed - I/O Server create failed OR * I/Net Alarms     'Alarms' failed to start - I/O Server create failed Alternatives with sending SMS alarms with I/NET Emailing alarm solutions for I/NET  Product Line TAC INET Environment I/NET Seven 2.4x or above TAC Informer (Pager TAP) - Product sold within Australia / New Zealand region. Cause Application developed by Australia (support for this product ended in 2005) now does not work with I/NET 2.40 or above. There are a few alternatives and possible workarounds, but this product is no longer supported. Resolution There are couple of alternatives: Currently the TAC Informer software will work with 2.31 or lower, so you can use these versions of I/NET Seven software. It may be possible that loading the I/NET 2000 compatibility files from the I/NET Seven CD may allow connection to the current INetIoSrv.exe file. The steps for this are as follows: Copy DbSrv2K.exe and INetIoSrv2K.exe from the CD “Support \ INET2000_Backward_Compatibility” directory into I/Net Seven's Program Files directory. From a DOS command and from the C:\Program Files\Inet Seven\ folder; Register both programs from the command line: DbSrv2K /regserver INetIoSrv2K /regserver Note: If you need to unregister these files use the following syntax: /unregserver  Alternatively it is recommended to use the email feature within Xenta 527 Web Server (Refer to Troubleshooting sending emails from a Xenta Server) which can then be configured with a third party mobile message service provided by Redcoal (www.redcoal.net).  They provide a set of simple Desktop applications which allow SMS to be sent via desktop application or via email.  Click Here for further information.  Customer will require to setup an account and charges do apply. Note: This provider only operates in Australia.  Third alternative is to use a solution provided by a company called NotePage, product name is PageGate - Refer to PageGate I/NET Seven Programming Instructions for further information.  Benjamin Roswall has developed a tool which is available on the community: TAC INET Notifier.  The program will look for alarm events in the SQL database, and process then according to the settings. The program has its own alarms list, and if the service is stopped, it will save the alarm list so that only new alarm events are processed when the program comes back online. For emails you just need to know your SMTP server configuration, and for SMS it uses the SysManSMS program that has a SMTP to SMS feature. Also, the program can write to a text file, and SysManSMS can then look for this text file. Please note Schneider Electric do not endorse this product but provide this option as a workable solution. All support issues related to these products should be directed to the developers / providers of the respective software.
View full article
Picard Product_Support
‎2018-09-10 01:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:24 PM

Labels:
  • TAC INET
1828 Views

How to use the Beeper of the Card Reader in I/NET

Issue There is a beeper inside some of the card readers. In some cases when alarms happen, such as Door Forced or Door Open Too Long, the beeper can be activated with a sound to deliver alarms. Product Line TAC INET Environment I/NET Cause In some cases this application is needed. Resolution Open the Door parameter in I/NET. Set the relative alarm message. For example, set the Door Open Too Long or Door Forced to Alarm.   Click the "Sounder" button Change the polarity to "Low". Set the relative beeper type and condition. For example, when the Door Open Too Long or Door Forced happens, the beeper activates continuously. For more issues about beeper in I/NET, refer to Reader beeps continually when connected to the door controller.
View full article
Picard Product_Support
‎2018-09-10 11:48 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:20 PM

Labels:
  • TAC INET
1709 Views

Fail to Restore the Backup from I/NET with SQL Database Size Limit is Reached

Issue When restoring I/NET database backup from another server in DBcreate, it shows an error: Error dropping PRIMARY KEY 'PK_DvrServers': Could not allocate space for object 'sys.sysserefs'.'clust' in database 'InetDb' because the 'PRIMARY' filegroup is full. Create disk space by deleting unneeded files, dropping objects in the filegroup, adding additional files to the filegroup, or setting autogrowth on for existing files in the filegroup. Product Line EcoStruxure Building Operation, TAC INET Environment I/NET SQL Server Cause Each SQL express version has its own database size limit. Refer to SQL and version compatibility for Filemaster, Equalized Client, Remote Client, Limitations of SQL. If the database size limit is reached, I/NET database will fail to update. The backup of the database will be fine, but when trying to restore onto another computer, it will also fail. Resolution 1. If the original I/NET server is still running, try to enable archive function to shrink the database in I/NET. And also follow Archiving and SQL database size keeps growing to set the database cap. 2. If the original I/NET server can't run, or the original database has been deleted, try to use SQL server version with higher size limit or full version SQL server which hasn't physical size limit. Like try to restore the backup from SQL 2005 Express (4GB limit) to SQL 2008 R2 Express (10 GB limit) or Full version of SQL 2005/2008. Refer to How to Troubleshoot on DBCreate for more issues about DBCreate.
View full article
Picard Product_Support
‎2018-09-11 07:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:13 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1755 Views

Reader beeps continually when connected to the door controller

Issue The card reader beeps continually when connected to the door controller with the Sounder cable connected. Product Line TAC INET Environment I/NET Cause There may be several causes for this situation: The door which this reader belongs to isn't configured. The polarity setting of the reader beeper isn't correct. This reader port is damaged due to certain cause. Resolution The following steps need to be followed: For cause 1, configure the door and reader in Door parameter. For cause 2, click "Sounder" button in the Door parameter window and change the "Polarity" setting correctly. Usually change from "High" to "Low". For cause 3, send the door controller to repair. For how to set up a beeper in I/NET, refer to How to use the Beeper of the Card Reader in I/NET.
View full article
Picard Product_Support
‎2018-09-10 05:01 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:59 PM

Labels:
  • TAC INET
1851 Views

CLX Expansion Card for 7798B

Issue Expanding a system with a 7798B and unable to connect to other controllers. Product Line TAC INET Environment All versions of I/NET Cause There is no expansion card to connect the LAN Controllers together. Resolution The 7798B requires a CLX Expansion Card to be plugged into the slot to allow it to communicate to other controllers. The part number for this is LAN EXPANSION OPTION FOR RS-485, CLX. See Additional information on CLX LAN Expansion Option for RS-485 for more information on the CLX part. Take the device off the wall, unplug all wires including power. Insert the CLX card into the slot on board, be careful not bend any pins while doing this. Connect the wires again in their respective terminal with the LAN wire connecting to the CLX card, Sublan to those devices and power. Put the device back on the wall, set up accordingly and it should be communicating to the controllers now.
View full article
Picard Product_Support
‎2018-09-10 12:24 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:48 PM

Labels:
  • TAC INET
1866 Views

I/NET Security Control Unit (SCU) firmware releases

Issue Should we upgrade to the latest revision for the SCU 1284 If we do not upgrade the SCU will I/NET work properly. Product Line TAC I/NET Environment I/NET Seven Security Control Unit (SCU) 1200 series firmware 3.2x and above Cause The recommendation is to always upgrade to the latest revision. In some cases this is not always possible. Please review the information below to determine if these features and fixes are required for your installation. Resolution I/NET Seven is backward compatible with all previous hardware firmware revisions of the SCU. The recommendation is to always upgrade to the latest revision to enable all of I/NET's features and fixes included in these revisions. In some cases this is not always possible. Please review the information below to determine if these features and fixes are required for your installation. If you have any additional concerns then please contact Product Support. The following table lists the release firmware revisions and associated fixes and new features: Rev Date DCN Changes 3.21 05/06 5593 Add support for SCU tamper to the SCU1200 and SCU1280 3.22 01/07 5610 Start adding intrusion alarm support to SCUs Add issue level support to SCU1284 Fix defect where deleting last tenant from DPU causes incorrect schedules Add door code 3.23 08/07 5627 Fix defect where changing a door to "unselect" did not prevent access through door 3.24 10/07 5631 Expand individual count from 24,000 to 32,000 per tenant 3.25 07/08 5657 Implement various changes to intrusion alarm system that were identified during EN50131 certification 3.26 01/10 5677 Fix corrupt reader LED due to OP5 monitoring board Fixes to SCU1284 expansion board for IAS power monitoring 3.27 07/11 5717 Make AMT show person who commanded PIN functions 3.28 12/12 5739 Fix for bad card read on reader number 4 with internal AO at bit offset 04 3.29 08/13 5745 Fix so that a change of date from one month to the next will work correctly when using special days 3.30 10/14   Support for 130-bit Wiegand card New event named “Key reassignment” 3.31 12/14 5754 Support for 86-bit Wiegand card For DPU range of controllers refer to I/NET Door Processing Unit (DPU) 7910A / 7920A EPROM Feature matrix.
View full article
Picard Product_Support
‎2018-09-11 07:03 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:46 PM

Labels:
  • TAC INET
2571 Views

Host number conflict on a computer with dual Network Interface Cards (NIC)

Issue When there are dual NICs on the computer, you will get host number conflicting error. The IP address causes this conflict is just the local IP address. Product Line EcoStruxure Building Operation, TAC INET Environment I/NET prior to Version 2.44a Win 7 or higher OS Cause When there are two NICs on the computer, I/NET needs to know which NIC is used for communication. I/NET support for dual Network Interface Cards (NIC) can be used for dual NIC configuration for I/NET. But under Win 7 and higher OS, wireless NIC can't be recognized in I/NET, which makes it impossible to choose wireless NIC to be used for I/NET. In the I/NET configuration, it just shows 0.0.0.0. Resolution I/NET will fix this issue in the new release. For I/NET prior to version 2.44a, there are two workarounds for this issue currently: Refer to I/NET support for dual Network Interface Cards (NIC) to choose onboard NIC to be used for I/NET communication. Disable onboard NIC or just disconnect it from the network. Then you will see the option for choose NIC for I/NET communication will be grayed out. That will force I/NET to communicate with wireless NIC. Remember to reboot I/NET I/O server after this to make it take effect. 
View full article
Picard Product_Support
‎2018-09-11 07:04 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:41 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1680 Views

Using XBuilder to Control I/NET points

Issue When a specific application request exceeds the standard capability of I/NET it is sometimes possible to use XBuilder to expand possible applications. Product Line TAC INET, TAC Vista Environment I/NET XBuilder I/NET Host Tool Cause When a specific application request exceeds the standard capability of I/NET it is sometimes possible to use XBuilder to expand possible applications. Resolution This is a sample access control application to demonstrate the possibility. Minimum requirements for this are :Xenta 527 Web Server. If you wish to use Menta Programming, use a Xenta 731 or Xenta 913. Application: Customer Requests an Audible Buzzer be triggered when a door is forced open, but not shut off until the alarm has been acknowledged. Create a DO point to controller your buzzer/light/alarm indicator (buzzer DO) Create an internal AO point to function as a translator (logic AO) Add a Calc to the buzzer DO: ~(P0=C0) where P0 is the logic AO and C0 is 80 Perform a Station save In XBuilder, create a project for the 527 Web Server Insert or re-insert the I/NET network Add a connection object Drag the Flags attribute of the Doors DO point to the "from" part of the connection object Drag the Value attribute of the logic AO point to the "to part of the connection object Generate the Project and Send to Target. The response time of the buzzer coming on or going off is dependent on the Scan interval of the buzzer DO.  The reason it works is that the flag attribute of the Door point will equal exactly 80 if you have an alarm flag and the point is still in alarm (the alarm has a value of 64 and unack has a value of 16 totaling 80. See Decoding the I/NET signal "flags" attribute for more information). The door point will stay in alarm until it is acknowledged so this will stay at 80 until someone acknowledges the alarm, or puts the point in Manual/Test.  The Buzzer will not activate if the point is in Manual or Test The above solution will trigger off any alarm specified from the door editor (Door Open To Long, Door Forced, Bad Card read, etc).  Turn off the other possible alarms, or create an addition internal point labeled Door Forced.  The Door DO point can trigger an event sequence based on Forced door to control the additional point. If you do this the calc will need to be modified to ~((P0=C0)|(P0=C1)|(P0=C2))  C0=16 C1-64 C2=80. This will allow for the buzzer to be on until the point has been acknowledged and return to normal
View full article
Picard Product_Support
‎2018-09-10 06:29 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:39 PM

Labels:
  • TAC INET
  • TAC Vista
1991 Views

I/NET Crashes Randomly with SQL 2008/SQL 2008 R2

Issue When using SQL 2008 or SQL 2008 R2, I/NET will crash randomly. Referring to the system Event Log, you can see a SQL error happened just before I/NET crashed, called "There is insufficient system memory in resource pool 'internal' to run this query." Product Line EcoStruxure Building Operation,TAC INET Environment I/NET SmartStruxure Cause According to Microsoft Knowledge Base, this problem occurs for all the following reasons: There is a bug in the code that is used to evaluate how many rowsets are required to perform a sorting operation. Therefore, the code greatly overestimates the numbers of rowsets. The required grant estimate in full-text is 64 pages for each rowset that is required to sort. There is a large request that blocks the system from using the memory that is reserved for the full-text query. Resolution Install the newest SP to the SQL 2008 or SQL 2008 R2 being used. Download Microsoft SQL Server 2008 SP3 Express Edition or Microsoft SQL Server 2008 R2 SP2  Express Edition from the Microsoft website. If this doesn't help, please follow Create Error Log for I/NET to turn on the error log for I/NET and then send the log in to your local country product support group for further troubleshooting.
View full article
Picard Product_Support
‎2018-09-11 07:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:38 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1691 Views

I/NET trends not working on a Xenta 527 version 5.1.6

Issue No Trends are showing up in the Data/Enquiry Editor when a point is selected. Product Line TAC INET Environment Xenta 527-NPR Webserver 5.1.6 Cause Changes in the Xenta 527 firmware in version 5.1.6 and later have resulted in some problems I/NET trend data displaying in the Xenta 527-NPR. Resolution To resolve this, the best option is to downgrade the Xenta 527 to version 5.1.5, per Download an .MOT file into a Xenta Programmable controller and restart the device and I/NET again.
View full article
Picard Product_Support
‎2018-09-10 11:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:34 PM

Labels:
  • TAC INET
1744 Views

Operating System Selection when using SQL Server

Issue Operating System Selection when using SQL Server Product Line TAC INET Environment I/NET Seven Site Cause Making decisions on operating system selection while using SQL Server 2000 Resolution If your site has grown beyond the capabilities of the Microsoft SQL Desktop Engine (MSDE) as discussed in Customer Advisory CA-2004-04 then you need to decide upon an operating system to use when you upgrade to SQL Server 2000. SQL Server 2000 Enterprise Edition and Standard Edition can run on the following operating systems: Windows Server 2003, Standard Edition Windows Server 2003, Enterprise Edition Windows Server 2003, Datacenter Edition Windows® 2000 Server Windows 2000 Advanced Server Windows 2000 Datacenter Server Source: http://www.microsoft.com/sql/evaluation/sysreqs/2000/default.mspx An option to consider based on the needs of the customer is whether Windows Small Business Server 2003 Premium Edition can meet their needs. This version sells at almost the same cost as SQL Server 2000 (5 CALs), however it includes much more. Windows Small Business Server 2003, Premium Edition includes the following components: Microsoft Windows Server 2003 Microsoft Exchange Server 2003, Standard Edition Microsoft Shared Fax Services Microsoft Office Outlook 2003 Microsoft Windows SharePoint Services 2.0 Health Monitor 2.1 Remote Web Workplace Microsoft Internet Security and Acceleration Server 2000, Standard Edition with Service Pack 1 (SP1) Microsoft SQL Server 2000, Standard Edition with Service Pack 3a (SP3a) Microsoft Office FrontPage 2003 It is important to note that there are some restrictions built into this version of Windows Server 2003. These restrictions limit it to only a single domain solution and can only expand up to 75 users or device connections. Windows Small Business Server restrictions Windows Small Business Server provides a cost-effective suite of programs for small businesses that have 75 or fewer users or devices. To help you prevent unapproved network installations and to help you protect your networks against viruses and other attacks, Microsoft has placed the following restrictions on the use of Windows Small Business Server: You must install all the component server programs in Windows Small Business Server on a single computer. No component may be installed on a separate computer. If you want to run one or more of the component services on a computer other than the Windows Small Business Server-based computer, the other computer requires separate licenses. You can connect a maximum of 75 users or devices to a Windows Small Business Server-based network. This requirement limits the number of users or workstations that can access one or more of the component server programs. Windows Small Business Server is a single-domain solution that is not intended to be integrated with other Windows-based domains. You are not permitted to establish explicit trusts to other Microsoft Windows NT-based domains or to Active Directory directory service domains. Also, Windows Small Business Server does not let you create child domains. The computer that is running Windows Small Business Server must have all operations master roles and must be at the root of the Active Directory forest. The following features that are available in earlier versions of Small Business Server are not available in Windows Small Business Server: Microsoft Shared Modem Service Microsoft Terminal Server Windows Small Business Server supports up to two physical CPUs and up to four virtual CPUs with hyperthreading. Note: Earlier versions of Windows Small Business Server support up to four physical CPUs. You can have other domain controllers and member servers in your Windows Small Business Server-based network. However, the computer that is running Windows Small Business Server must be set up as the root domain controller of an Active Directory forest. This requirement may prevent the computer that is running Windows Small Business Server from serving as a corporate branch office server or as a department server of a large organization that is based on Active Directory or on Microsoft Windows NT 4.0. You cannot add Windows Small Business Server to an existing domain. You must install a Windows Small Business Server-based domain and then add additional domain controllers or member servers to the domain. When you run Exchange 2003 on a Windows Small Business Server-based network, Exchange 2003 cannot be part of a larger Exchange 2003 organization. Because Windows Small Business Server is installed at the root of the Active Directory forest, you cannot install Exchange 2003 components that belong to an existing Exchange 2003 organization. Source: http://support.microsoft.com/default.aspx?scid=kb;en-us;842690 Windows Small Business Server 2003 Premium Edition is a good solution for jobs where the controls contractor will be managing the server operating system that is the core of the BMS.  Many customers today will allow controls contractors to utilize their IP infrastructure but want the system managed and maintained by that same controls contractor.  This software allows that contractor to provide a turn key installation and include all PC hardware and software.  Windows Small Business Server 2003 Premium Edition is also a very cost effective solution for jobs where the specification requires a server operating system or a full version of SQL server that the contractor must provide.  It is recommended that if Windows Small Business Server 2003 Premium Edition is used, any software that is not needed on the server is disabled (i.e. Exchange Server, Fax Services, SharePoint Services).  In conclusion, Windows Small Business Server 2003 Premium Edition is a cost effective way to provide SQL Server at a site if all criteria are met.  Update: If using I/NET 2.40 and above, please check this compatibility matrix for Operating Systems when using SQL Server For other compatibility issues, see Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Satchwell Sigma, I/A Series, and StruxureWare Building Operation.
View full article
Picard Product_Support
‎2018-09-07 12:50 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:33 PM

Labels:
  • TAC INET
1873 Views
  • « Previous
    • 1
    • …
    • 21
    • 22
    • 23
    • …
    • 73
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore