Deny Entry Tenant Messages in I/NET AMT

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Deny Entry Tenant Messages in I/NET AMT
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1667 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Deny Entry Tenant Messages in I/NET AMT

Picard Product_Support
‎2018-09-06 12:20 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:26 PM

Issue

A Deny Entry Tenant Message is given instead of a valid card read.

Product Line

TAC INET

Environment

  • I/NET Seven
  • AMT

Cause

The Deny Entry Tenant message is delivered when the credential read is not known to the controller for any of the following reasons:

  • The door being read is not part of the individuals tenant.
  • The SLI does not have the correct database
  • Card Translation is incorrectly enabled/disabled in the door editor
  • There is a hardware error with the Card reader.

Resolution

General Steps:

  1. Determine if the issue only happens to a single individual or a group or all cards.
  2. Select Access>Tenant.
  3. Verify that the door has been added to the correct tenant(s)
  4. Select Edit>Individuals and browse to the card(or a test card) in question.
  5. Verify that the card has the been added to the door correctly.
  6. Follow the directions in How to force a download of card data to force a download. If this fixes the issue, go to the "SLI does not have the correct database section"
  7. In AMT, select window options and add the message column to the window
  8. Find a Deny entry tenant message and see if the message column matches up with Hex card number for the badge that was read. If all you get is a scrambled number, There is probably a hardware error.

Verify Card Translation is Enabled (this section assumes you are using large card number format)

  1. Select Access>Doors
  2. Modify the door in question
  3. Check the box next to "Card Translation". If this option is not available you will need to flip Dip switch 7 on the SCU
  4. Compare this setting to a few other doors on the system. Thy should all have the same setting

Hardware Error

  1. The easiest way to prove a hardware error is to plug a spare card reader directly into the DPU or SCU.
  2. If the problem is immediately solved replace the field reader.
  3. If not, try unplugging other readers on the controller and see if the problem goes away for that reader.
  4. It is possible that the controllers power supply is no sufficient to power the reader. Use an external power supply instead.

Various known fixes for SLI database Errors:

Take the SLI to it's boot state and restore bin file and database files from the Server

If you are using I/NET 2.15-2.21, upgrade to 2.31

Insufficient memory: The SLI will allocate memory for all possible individuals in a tenant regardless if they are used or not. For example, if the site has only 500 cards, but the tenant is set to 32000 individuals, this will use the same controller memory as a site with 25000 individuals.  Reducing the number of individuals allocated in the tenant has been shown to clear up Denied Entry Tenant messages.

System traffic: In I/NET 2.31 and above, the filemaster or server will indicate when badge data is being downloaded on a status bar in the bottom right hand corner of the screen. If this indicator is constantly showing downloads, it is due to poor system communication causing constant polling of the database.  Follow these steps to fix this issue.

  1. Turn Automatic DPU restore off on all links and wait for the download messages to stop. (this is done by selecting Edit>Host Computer>Network Configuration, then modifying each link)

  2. Wait for the automatic downloads already requested to finish.

  3. Re-enable Automatic DPU restore on each link, one at a time. Wait for the system to finish individual downloads before moving on.

  4. When you find a link that take an excessive amount of time (compared to others) to finish downloading, troubleshoot that links controller LAN wire.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 7954
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore