Issue
No Trends are showing up in the Data/Enquiry Editor when a point is selected.
Product Line
TAC INET
Environment
- Xenta 527-NPR
- Webserver 5.1.6
Cause
Changes in the Xenta 527 firmware in version 5.1.6 and later have resulted in some problems I/NET trend data displaying in the Xenta 527-NPR.
Resolution
To resolve this, the best option is to downgrade the Xenta 527 to version 5.1.5, per Download an .MOT file into a Xenta Programmable controller and restart the device and I/NET again.