Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2208 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 107
    • 108
    • 109
    • 110
    • 111
  • Next »
Label: "Andover Continuum" Show all articles

Continuum controller compliance with the most recent BACnet standard.

Issue Are the BCX4040, BCX4000 and b3 line of controllers compliant with the most recent BACnet specification, ASHREA 135 2012? Environment Continuum Controllers Cause The consultant is requiring that all BACnet controllers be compliant with ASHREA 135 2012. Resolution As of August 27, 2014 the BCX1 and b3 family of controllers do not comply with ASHREA 135-2012. This is noted in the PICS statements as the Protocol Revision. The 2004 version of the spec correspond to Protocol Revisions 4, 5 & 6. The 2012 version is Protocol Revision 14 & 15. As of August 27, 2014 the BCX1 and b3 family of controllers comply with ASHREA 135-2004 spec revision.  
View full article
Picard Product_Support
‎2018-09-06 09:25 AM

Labels:
  • Andover Continuum
1254 Views

NetController IO Bus Speed.

Issue What baud rate is the NetController IO bus speed set for and can this be changed? Environment NC1 NC2 CX99xx CX9680 Cause Need to know the bus speed of the NetController IO bus. Resolution The NetController IO Buss runs at 19200 baud.  This is a hard setting and cannot be changed.
View full article
Picard Product_Support
‎2018-09-06 09:22 AM

Labels:
  • Andover Continuum
1129 Views

AccDataServices crash on launch of Continuum CyberStation

Issue AccDataServices crash on launch of Continuum CyberStation Environment CyberStation Cause Bad installation. Looking in Control Panel Add/Remove Programs we see 2 different instances of Continuum Resolution Remove Continuum  in Control Panel Add/Remove Programs Delete the Continuum folder in C:\Program File (or x86) Re-install Continuum
View full article
Picard Product_Support
‎2018-09-06 09:21 AM

Labels:
  • Andover Continuum
1458 Views

Pulse Width Modulation applications with triac digital outputs speed limitations

Issue With triac digital outputs, such as those in the i2866-V, what is the fastest they can switched for Pulse Width Modulation (PWM) applications? Product Line Andover Continuum Environment Continuum controllers with triac digital outputs. Cause Require information on using triac outputs for Pulse Width Modulation control. Concerns over minimum pulse times and frequent switching. Resolution The triac outputs on some Continuum controllers (such as the i2866-V) will be able to perform pulse width modulation from a minimum of 0.1s pulses. As apposed to relays, outputs using triac's have negligible wear and tear during extended use. Switching the outputs frequently, such as once a second, should not cause any premature failure issues.  Further data on the triac outputs on the i2866-V: Specification sheet Installation Guide for wiring details. i2 Technical Reference Manual
View full article
Picard Product_Support
‎2018-09-11 02:03 PM

Labels:
  • Andover Continuum
1743 Views

NetController IO Bus Comm parameters.

Issue What is baud rate of the Netcontroller IO Bus? Environment NetController IO Bus ACC Lon FTT-10A Cause         Parameter      ACC LON       FTT-10A Baud Rate    39,063            78,125 Duplex         Half                 Half Data Bits      8                    8 Stop Bits      1                    1 Parity           None               None Resolution The ACC LON data signal is Differential Manchester Encoded.  The packets therefore cannot be viewed with a generic sniffer like a UART based comm signal. 
View full article
Picard Product_Support
‎2018-09-06 09:21 AM

Labels:
  • Andover Continuum
1334 Views

BACnet Dent PS3 PowerScout Meters Issue.

Issue When trying to discover via BACnet they broadcast the same instance ID. Need Dent Viewpoint software and RS485 converter to change the Instance ID prior to doing Find New BACnet Devices. Environment BACnet MSTP Cause Documentation Resolution Use Dent Viewpoint software and RS485 converter to change the Instance ID prior to doing Find New BACnet Devices.
View full article
Picard Product_Support
‎2018-09-06 09:21 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1302 Views

Conversion of BCX from an BCX9640 to BCX4040 or BCX4040 to BCX9640 is fails.

Issue When trying to update the OS of a BCX9640 to a BCX4040, the update process seems to succeed but the controller remains unchanged after the update process completes. Continuum indicates no errors during the update process. Environment Convert BCX BCX9640 BCX4040 Update OS Firmware Cause Incompatible bootloader. Resolution Update the controller to the most current version of OS for the same controller model before updating the OS with the new model firmware.
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • Andover Continuum
1555 Views

BCX4040 goes offline and ping failed

Issue For unknown reason, BCX4040 goes offline with solid CPU light, and failed to ping, Webpage can't be accessed, Environment BCX4040 Cyberstation 1.80 and above Cause Not clear what cause this issue, Not all the BCX4040 with solid CPU light can be recovered. Resolution Press "reset" button on PCB board for a long time, at least over 10 seconds, if the CPU light goes off, it is possible to recover the BCX4040 Press "IP Reset" on PCB board for over 60 seconds, Maybe not bring the controller into factory default setting Ping the BCX4040, if success, go to the next steps Start Continuum, and bring BCX4040 online, then downlaod, According to the steps above, I have recovered at least 4 BCX4040 and AX5720/5740.
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • Andover Continuum
1552 Views

Monitoring an external variable outside of SmartStruxure Lite to trigger a lua script

Issue At times it is necessary to monitor an external variable to trigger action in SmartStuxure Lite Environment Smart Struxure Lite Smart Struxure Continuum AS MPM Windows 7 Windows Server 2008 Cause Need the ability to trigger actions from an external variable to run a lua script Resolution Use a lua script in your MPM that copies the value of ME.PG#_ENABLE.value to an Analog/binary value. This value can then be seen from the AS or BCX through bacnet and you can have the AS or BCX do different functions depending on that value
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
1190 Views

Are there pull-up/pull-down resistors on the RS-485 port in the ACX57xx controllers?

Issue Having communication issues with Schlage PIM devices attached to ACX2's 485 port. Environment ACX57xx Cause Documentation Resolution The ACX57xx RS485 port has 47K resistors on the +/- lines. The 47K on the plus line is pulled up to 3.3v. The one on the minus line is pulled down to ground. They are both 1/16 watt resistors.  
View full article
Picard Product_Support
‎2018-09-06 09:14 AM

Labels:
  • Andover Continuum
1107 Views

Fields in Personnel Manager does not show with default value.

Issue Site has a personnel database with about 10K records, the site is switching to dual credentials and has configured the Personnel Manager to use HIDCorp1000 as the default for card type 2 and xxx as the default for Site Code 2. Problem is when going to change the personnel the Card Type 2 field still comes up with Infinity37 and Site Code 2 of 0 instead of the configured defaults. Environment CyberStation Cause Any existing personnel in the database will come up with Infinity37 for the card number 2 and 0 for the site code 2 as those were the values populated in the SQL database for those fields when the system was configured for only one credential. When creating NEW personnel objects the fields show the configured default values. Resolution When creating NEW personnel objects the fields show the configured default values.
View full article
Picard Product_Support
‎2018-09-06 09:14 AM

Labels:
  • Andover Continuum
1685 Views

What are the RS-485 parameters used for Infinet communications?

Issue What are the RS-485 parameters used for Infinet communications? The baud rate can be set but the other parameters are not exposed in the Comm Port settings. Environment Continuum Infinet Cause Values not exposed in Comm Port settings dialog. Resolution The Infinet Protocol RS-485 parameters used:   1 start bit 8 data bits No parity 1 stop bit No flow control
View full article
Picard Product_Support
‎2018-09-06 09:13 AM

Labels:
  • Andover Continuum
1291 Views

Why is the i2/ b3887 RAM memory not saved on power failure?

Issue i2887/ b3887 Cool starts on Power failure Environment i2887, b3887 i2887-L-230, b3887-L-230 i2887-L-115, b3887-L-115 Cause The i2887 and b3887 do not have a RAM battery backup. Resolution The i2/b3887 is one of the range of low cost i2/b3 controllers that does not have a RAM backup battery. It has no concept of a Warm start that would save working values in the RAM. It does however have Flash Memory that allows the controller to save all of its points and programs. After a power outage these points / programs will be copied into RAM and start running from their first line (if they are Autostart) in what is called a Cool Start. Its ACCRestartMode mode will be ACCCoolStartOnly.   Other i2/b3 controllers that do have a RAM backup battery will allow the ACCRestartMode to be changed as required.
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
959 Views

What is the Operating System used in the Continuum Controllers?

Issue What is the Operating System used in the Continuum Controllers? Environment Continuum Field Controllers Cause Customer wants to know if a common Operating System is used. Resolution The Operating System for the Continuum Controllers is a proprietary Operating System developed in-house specific for each Controller's Hardware platform. 
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • Andover Continuum
999 Views

Unstable Communications

Issue The PIM seems to be timing out or bouncing Online and Offline, indicating loss communications. Environment Schlage Integration with Continuum Version 1.94 Cause The PIM seems to be timing out or becomes unresponsive due to invalid setting of Parameter 5, it needs go be set at 0 and not 1. Resolution The resolution for this is as follows: NetControllerII - ONLY Comm2 (RS485) is supported for this application, with Parameter 5 of the Global Config set to ZERO, regardless of the symptom or setup. ACX57XX - ONLY Comm1 (RS485) is supported for this application, with Parameter 5 of the Global Config set to ZERO, regardless of the sympton or setup. Once changes have been made, open the Global Config Numeric and change the value from 3 to 99 Apply the changes and then click on the Refresh Button until the value comes back to 3.
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • Andover Continuum
1126 Views

Is there a way to concatenate access events from two Personnel objects into one Personnel object?

Issue Is there a way to concatenate access events from two Personnel objects into one Personnel object?  Environment Continuum Cyberstation Cause A Personnel object had a history of events and was then mistakenly recreated as a duplicate object. The original object was disabled and new events have now been tied to the new duplicate Personnel resulting in events for the same person being spread across two Personnel objects. Resolution The Access events produced are linked to each individual Personnel object that created them. There is no way to transfer these events from one Personnel to another.
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • Andover Continuum
1187 Views

Unable to launch Continuum Reports Suite on a Windows 7 64 bit workstation

Issue Unable to launch Continuum Reports Suite on a Windows 7 64-bit workstation Product Line Andover Continuum Environment Windows 7 64 bit workstation Cause "Continuum_Reports" directory permissions Invalid "Reports.exe" launch path in PE Program "Reports_Suite" (or other PE Program) is Disabled Attempting to launch Continuum Reports directly Resolution "Continuum_Reports" directory permissions Log into the workstation with Administrative privilege Edit the "Continuum_Reports" directory properties Click on the "Security" Tab Click on "Edit" button Highlight "Users" Click on the "Allow Full Control" checkbox Click on "Ok" button Invalid "Reports.exe" launch path in PE Program Edit PE Programs, such as "Reports_Suite" Change the statement: RepPath = "c:\progra~1\continuum_reports\" -to- RepPath = "c:\progra~2\continuum_reports\" Save change Enable the PE Program if Disabled "Reports_Suite" (or other PE Program) is Disabled Edit the PE Program Review the Program Configuration Enable the Program if Disabled Run the PE Program Attempting to launch Continuum Reports directly Continuum Reports cannot be launched directly from the Windows Explorer by double-clicking on "Reports.exe".  Continuum Reports are launched by running a workstation PE program from a Menu Page button or a Pinpoint button
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • Andover Continuum
1454 Views

What are the Continuum door's attribute which values persist for ONE scan only.

Issue What are the Continuum door's attribute which values persist for ONE scan only. Environment Plain English Cause Documentation Resolution DURESS VALID ACCESS VALID ATTEMPT ENTRY EGRESS VIOLATION INVALID ATTEMPT DATABASE FAULT ENTRY KEYPAD TAMPER EXIT KEYPAD TAMPER
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • Andover Continuum
931 Views

b3 program not work properly some time

Issue B3 program not work properly some time, but be correct at some time, for example, the function called program response slowly, only output the upper limit and lower limit. Environment Continuum B3 Cause This issue caused by lack of freemem for the b3s although there is not too much program and objects or logs entries. Some customer edit the program in Microsoft office word enviroment and paste it into Plain English , this result in a lot of Blank line in the  program and occupies many memory, When the freemem is under 2000bytes, some program will not work properly. Resolution Remove some blank line or comment charcaters in the programs and keep the freemem is above 2000bytes.
View full article
Picard Product_Support
‎2018-09-06 09:10 AM

Labels:
  • Andover Continuum
1234 Views

WebPinpoint will not install or error finding WebclientPinpointSetup.cab

Issue WebPinpoint will not install or error finding WebclientPinpointSetup.cab Environment WebClient WebPinpoint Cause Partial WebPinpoint installation or WebClientPinpointSetup.cab is not located in the expected folder. Resolution 1. In the browser machine look in control panel program and features, if you see WebPoinpoint is the list of programs when it is already installed, if you suspect the installation is no right then unistall Webpinpoint then try to open a Graphics which will cause the Webpinpoint installation to run again. 2. If WebPinpoint istallation can't locate the installer then go to the machine where the Web Server Continuum software was installed and... a) Look in C:\Program Files(x86)\WebServer\Redist, there should be a file called WebClientPinpointSetup.CAB if the file is not there you need to locate it on the machine and copy it to said folder.
View full article
Picard Product_Support
‎2018-09-06 09:09 AM

Labels:
  • Andover Continuum
1133 Views
  • « Previous
    • 1
    • …
    • 107
    • 108
    • 109
    • 110
    • 111
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login