Can I use the RS485 port on a bCX Comm 2 for a Plain English driver?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can I use the RS485 port on a bCX Comm 2 for a Plain English driver?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1360 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can I use the RS485 port on a bCX Comm 2 for a Plain English driver?

Picard Product_Support
‎2018-09-06 09:06 AM

Issue

How to select between the RS232 and RS485 port on a bCX1 controller when sending / receiving ASCII data.

Environment

Serial port Plain English Driver

RAW Mode

Bcx1 9640, 4040

Cause

Unable to select RS485, the controller only transmits/ receives through RS232.

Resolution

There is no switch exposed to Plain English that allows you to use the RS485 port on Comm2 of a bCX.

 A Netcontroller II would be able to do it as on Comm1 & 2, it has both RS232 & RS485 full circuits that work in parallel. So when you print from Plain English, the data goes out of both ports. You just need to control the RTS line of the port to switch between transmitting or receiving on the RS485 as it is half duplex.

The way the bCX Comm2 is wired internally it defaults to RS232 but there is no exposed parameter to switch to RS485. In the Modbus RTU X Driver there is the special parameter (Function 99) that has to be set to switch between the ports, but this switch is at a level that only an X Driver can access.

The options are: Use a Netcontroller II , or use a RS232/ RS485 converter (ensure it is not line powered), with the PE program sending / receiving on the RS232 port of the bCX. Possibly move to Comm1 of the bCX freeing up Comm2 for use with Infinet or BACnet controllers (assuming the node count is not 0).

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 17665
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore