Fields in Personnel Manager does not show with default value.
  • Fields in Personnel Manager does not show with default value.
  • AbeMeran
    AbeMeran
‎2018-09-06 09:14 AM
Site has a personnel database with about 10K records, the site is switching to dual credentials and has configured the Personnel Manager to use HIDCorp1000 as the default for card type 2 and xxx as the default for Site Code 2.
Problem is when going to change the personnel the Card Type 2 field still comes up with Infinity37 and Site Code 2 of 0 instead of the configured defaults.
CyberStation
Any existing personnel in the database will come up with Infinity37 for the card number 2 and 0 for the site code 2 as those were the values populated in the SQL database for those fields when the system was configured for only one credential.
When creating NEW personnel objects the fields show the configured default values.
  • 17196