Are there pull-up/pull-down resistors on the RS-485 port in the ACX57xx controllers?
  • Are there pull-up/pull-down resistors on the RS-485 port in the ACX57xx controllers?
  • AbeMeran
    AbeMeran
‎2018-09-06 09:14 AM
Having communication issues with Schlage PIM devices attached to ACX2's 485 port.
ACX57xx
Documentation
The ACX57xx RS485 port has 47K resistors on the +/- lines. The 47K on the plus line is pulled up to 3.3v. The one on the minus line is pulled down to ground.
They are both 1/16 watt resistors.