b3 program not work properly some time
  • b3 program not work properly some time
  • YangboLIU
    YangboLIU
‎2018-09-06 09:10 AM
B3 program not work properly some time, but be correct at some time, for example, the function called program response slowly, only output the upper limit and lower limit.
Continuum
B3
This issue caused by lack of freemem for the b3s although there is not too much program and objects or logs entries.
Some customer edit the program in Microsoft office word enviroment and paste it into Plain English , this result in a lot of Blank line in the  program and occupies many memory, When the freemem is under 2000bytes, some program will not work properly.
Remove some blank line or comment charcaters in the programs and keep the freemem is above 2000bytes.
  • 17408