Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 99
    • 100
    • 101
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Continuum Analyzer not showing all of the test results in the report.

Issue Cyberstation V1.94 on a Windows 7 64 bit PC does not display all of the Analyzer results Environment Cyberstation V1.94 Windows7 64 bit O/S Cause This system combination runs all of the tests but not all results are shown. Resolution This issue is rectified in V1.94 Service Pack 1. V1.94 SP1 is to scheduled for release April/ May 2013.
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • Andover Continuum
1119 Views

Can a port-powered RS232-to-RS485 converter be used on bCX comm1?

Issue Can bCX comm1 power a port-powered RS232-to-RS485 converter?. Environment bCX Cause Need to connect Modbus RTU devices on RS485 bus to Xdriver on bCX comm1. Resolution This has been done successfully according to posts on the Exchange commnuity. It is not a configuration that Product Support Services supports as it is not tested and there are many different devices on the market - some of whch may work and some which may not. 
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • Andover Continuum
1213 Views

What are the valid ranges for the Infinet ID's?

Issue How do I know if an Infinet ID is a priority node? Environment Infinet Controllers i2, SCX, LCX,TCX,LSX Cause Some Infinet ID's are Priority nodes or reserved nodes. Resolution Some controllers can be defined as a Priority Node, which means it will receive the Infinet Token more often than a regular Infinet node. To promote a controller to be a Priority node change its Infinet ID to be in the Priority node range using a service tool.   The overall range of Infinet ID's is 0-255 and these are defined as follows: 0 - New or unassigned controllers have an ID of 0, they will not communicate until an ID has been assigned to them, usually by doing a "Learn" 1 - 127 Regular Infinet controller nodes 128 - 223 Invalid addresses and should not be used. 224 - 250 Priority nodes 251 - 254 Priority nodes usually reserved for a Service tool (i.e. LSX280 or RoamIO) 255 Used by the "Master" node i.e. CX, bCX or Netcontroller When a learn is performed a regular controller will be allocated the next available regular node, the exceptions are the DCX250, ACX700 and ACX780 which will be allocated the next available Priority node.
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • Andover Continuum
1580 Views

BACnet Alarms from BCX controller are no longer being logged to the database while alarms from b3 and third party controllers continue to be delivered.

Issue All alarms were working originally. Several weeks ago the BCX alarms stopped being logged to the database. B3 and third party controllers continue to log alarms to the database. Environment BCX4040 Guarantee Delivery BACnet alarms Cause Guarantee Delivery is not checked in the Event Notifications Resolution Once Guarantee Delivery is checked in the Event Enrollment configuration, alarms will begin to be delivered.
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • Andover Continuum
1364 Views

Method of Getting Report data into a Excel Spread Sheet.

Issue How do I get report data into a Excel spread sheet? Environment Continuum 1.6  thru  1.94 Microsoft Office 2003,  2007 Cause Exporting data to Excel allows it to be used and shared in a common format. Resolution Create a Report: Source Tab: Data Source = Extended Log Chart Type =  Text Chart Subtype=  AccTextXML Output Tab: Heading = %r SubHeading =  Report created at %t Display the full path in the report  = Selected OutPut to File  = Selected     Select the path. =  Example  c:\Report.txt Filter: Select Time interval Add Data points. Save:  then Run Report:  The file should have been created in the selected directory. Goto the selected directory  and right click on the file and Open with Microsoft Office Excel. You will be prompted with some choices select "As an XML List" Save to desired location as a xls file.
View full article
Picard Product_Support
‎2018-09-06 10:30 AM

Labels:
  • Andover Continuum
1524 Views

Object identity has been specified for an object that doesn't exist.

Issue Trying to edit bCX from BACnet side results in the above error. No problem from Infinity side. Environment CyberStation bCX4040 bCX4000 Cause Configuration issue Resolution a) Delete bCX from BACnet side. b) Perform find new BACnet devices from the root. c) After device is found and present under the BACnet devices folder, right click on it and send it to the database.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1383 Views

What is the working range for a thermistor temperature sensor?

Issue What is the temperature reading range for the STP500? Environment All Continuum controllers STP500 range STX500 range STD500 range Cause Clarification on read range required. Resolution When connected to a Continuum controller the operating temperature range is: -30°F to +230°F, -34°C to +110°C For readings outside this range, an active sensor with a 4-20mA or 0-10V output should be used.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
  • Field Devices
1017 Views

An Epibuilder Plugin is necessary for some badging devices to work

Issue For EpiDesigner or EpiBuilder to work with some devices a plug-in needs to be purchased. Environment Continuum EpiBuilder EpiDesigner Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause Epibuilder will not communicate with some approved devices without purchasing a special plug-in. Resolution ImageWare is the third party company that Continuum integrates with for badging and there are a number of devices that require a plug-in to work. Check the following web page for a list of tested and supported items and if the device indicates plug-in, then purchasing a plug-in is required. https://support.iwsinc.com/about/support/epi_builder/ The plug-in can be purchased through a ImageWare partner. https://www.iwsinc.com/partners/ Schneider Electric does not sell the plug-ins and has no access to any serial numbers that may be prompted for during the installation.
View full article
Picard Product_Support
‎2018-09-11 02:30 AM

Labels:
  • Andover Continuum
1331 Views

B4920 analog inputs read 8.6-8.9 volts instead of 10 volts for full scale

Issue analog input shows 8.6-8.9 volts instead of 10 volts Environment B4920 Cause The pull up resistor when disabled will drop the top end voltage slightly Resolution Pull up resistor on = 10 volts top scale Pull up resistor off = 8.6-8.9 volts top scale (by design) 
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1252 Views

Personnel Profiles are adding areas that are not included in the profile.

Issue Users are adding areas to a person which should be blocked by a security level. Environment Continuum V1.93, V1.94 Cause Object level security is allowing the personnel profile to attach areas that should be blocked. Users with limited access to the sites areas are having additional areas added when applying a profile. No problems are encountered if no object level security is applied to the areas. Resolution This issue is resolved in V1.94 SP1 release of Cyberstation.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1040 Views

What LDAP sources can the Personnel Import Utility interface to?

Issue Do we support LDAP sources other than Microsoft Active Directory? Such as interfacing to Oracle Databases, OpenLDAP, Apple LDAP, etc… Environment Continuum Personnel Import Utility Cause Customer wants to use an LDAP source other than  Microsoft Active Directory. Resolution The only LDAP scenario that has been tested for was interfacing with Microsoft Active Directory, no other LDAP source has been tested or qualified at this time. Other LDAP sources may work but as these have not been qualified we have no way of knowing for sure.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1230 Views

Can Personnel be deleted or disabled in Continuum utilizing the PIU and a third party system?

Issue Can Personnel be deleted or disabled in Continuum utilizing the PIU and a third party system? Environment Continuum Personnel Import Utility LDAP Cause Not sure what can be accomplished with the PIU to manage Personnel changes. Resolution The Personnel Import Utility, with the help of a transformation file, can be used to disable Personnel records in Continuum. This can be accomplished with an interface using LDAP, CSV, or XML. One method would be to use the expiry date field to disable Personnel Access.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1390 Views

Is it possible to run Continuum in the video server box?

Issue Site is using Pelco video server that runs in the same OS as Continuum, to minimize cost they want to run Continuum in the video server machine. Environment CyberStation Various Pelco video servers Cause Cost Resolution While it is technically possible to have Continuum run in the same machine as the Video server it is not recommended. Some of the possible problems that may arise are... 1. Performance issues 2. Compatibilities issues, some files required by both Continuum and the video server may have different version requirements.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1088 Views

How to generate a report of personnel that have not accessed the site via the Access Control system in X days/months.

Issue Need a report of personnel that have not accessed the facilities in some specified time. Environment CyberStation Cause Documentation Resolution Create a List View of the Personnel class Add desired columns (Name, Card Number etc) In the Qualifiers tab add the following advanced qualifiers TimeEntered <= MyCyberStation\Date - xxx where MyCyberStation is the name of the workstation object and xxx is a number that represents the number of seconds going back in time. For example to generate a list view report of all personnel that have not accessed the facilities in a day enter the following qualifier TimeEntered <= MyCyberStation\Date - 86400  (86400 is the number of seconds in a day) For a qualifier for a month enter... TimeEntered <= MyCyberStation\Date - 86400 * 30
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Andover Continuum
1161 Views

SmartStat gives faulty reading.

Issue The temperature reading randomly  fluctuates between 69.5 deg and 327 deg. Environment Controllers with SPWR / Smart  Sensor support. Cause This situation can be the result of running one 6 conductor cable for all of the wiring to the thermostat; including the 24 VAC for the LED light.  The 24 VAC is causing interference with the temperature  input . Resolution Use a different cable for the LED light 24 volt.  Use 0-5 VDC to feed the LED Light.
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • Andover Continuum
1288 Views

Configuring door access using keypad without access card.

Issue Is it possible to configure a door so that a card holder can gain access using only his unique pin number. Environment Continuum Access control Personnel objects unique PIN Cause Cardholders often lose their cards and need access to an area. Resolution For PIN only validation to work the Unique PIN option under Allowed Credentials must be selected. * On door object Deselect all Access Validation. Under General Access Validation, select Validate PIN. *  If Unique PIN is not selected, cardholders using a valid pin will be able to gain access through the door, but Continuum will be able to provide reliable cardholder information for access events at this door. There are security issues that make it necessary for the badging personnel to issue a predetermined and available pin number to the cardholder. 
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • Andover Continuum
1601 Views

Controller with Modbus TCP/IP xdriver dropping offline randomly.

Issue NCII controller with Modbus TCP/IP xdriver running in server mode drops offline every day or so. Environment Modbus TCP xdriver Cause The customer was using a very old version of the modbus xdriver file. Resolution Installed the current Modbus TCP/IP xdriver release.
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • Andover Continuum
2395 Views

An example on how to control a Door Request to Exit function with a Schedule.

Issue An example on how to control a Door Request to Exit function with a Schedule. Environment Continuum Access Control Door Plain English Cause Customer wanted an example on how to disable Exit Requests for a Door after hours. Resolution There are probably a couple of ways to do this depending on how you are currently controlling door access. The easiest method would be to use to the "OpenOnExitReqst" attribute of the Door object. Using a PE program to set this to False based on a Schedule point should give you the functionality required. The PE code for the InfinityProgram in your Access Controller would be similar to below. =================== ' Door_SCH - InfinityNumeric that is being set by a Schedule object ' Door1 - Door object where the Exit Request button is to be controlled ' ' Fall Thru program triggered by Door_SCH ' Functionality: Door_SCH calls this program to run when its value changes. ' This then sets the state of the OpenOnExitReqst attribute in the Door to the ' current state of your Schedule. Reverse this if you want to opposite action. ' "Door1 OpenOnExitReqst = not Door_SCH" Door1 OpenOnExitReqst = Door_SCH ===================
View full article
Picard Product_Support
‎2018-09-06 10:25 AM

Labels:
  • Andover Continuum
1401 Views

ReadPropertyMultiple Property Identifier: all (8) is not supported by the BACnet/IP Xdriver

Issue A third party BACnet browser is trying to query Xdriver points. It sends ReadPropertyMultiple with a Property Identifier of "all (8)". The CX9680 responds with an error. Is this property supported by the BACnetIP Xdriver? Environment BACnet IP Xdriver Cause The ReadPropertyMultiple property identifier: all (8) is not supported by the Xdriver. Resolution The ReadPropertyMultiple property identifier: all (8) is not supported by the Xdriver. The Xdriver only supports the following properties: Value Access BACnet Property 85 R/W Present-Value 111 R Status-Flags 36 R Event State 81 R Out of Service In the Xdriver manual the Quick Reference table in Appendix A indicates "Property 1-25 Service Limit". This is only for the DeviceSelf object and determines the number of asynchronous BACnet messages the Xdriver can send at a time. It effects the speed of polling (1 = slowest, 25 = fastest).
View full article
Picard Product_Support
‎2018-09-06 10:25 AM

Labels:
  • Andover Continuum
1453 Views

CPU light on ACX7xx flash rapidly (at bout twice the normal speed)

Issue After an attempt to cold start the controller by removing AC power with the batteries disconnected, the unit started up with its CPU light flashing very rapidly (hard failure mode) Environment ACX780 ACX781 Cause Partly cleared memory. The random access memory  (RAM) on the ACX78x take a long time to erase. Resolution Remove the batteries Power down the unit Wait 5 minutes Power up the unit
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • Andover Continuum
1071 Views
  • « Previous
    • 1
    • …
    • 99
    • 100
    • 101
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore