SmartStat gives faulty reading.
  • SmartStat gives faulty reading.
  • Carl_Slack
    Carl_Slack
  • Clifton_eakes
    Clifton_eakes
‎2018-09-06 10:27 AM
The temperature reading randomly  fluctuates between 69.5 deg and 327 deg.
Controllers with SPWR / Smart  Sensor support.
This situation can be the result of running one 6 conductor cable for all of the wiring to the thermostat; including the 24 VAC for the LED light.  The 24 VAC is causing interference with the temperature  input .
Use a different cable for the LED light 24 volt.
Use 0-5 VDC to feed the LED Light.
Tags (2)
  • 13104
  • tts-1