Object identity has been specified for an object that doesn't exist.
  • Object identity has been specified for an object that doesn't exist.
  • AbeMeran
    AbeMeran
‎2018-09-06 10:29 AM
Trying to edit bCX from BACnet side results in the above error.
No problem from Infinity side.
CyberStation
bCX4040
bCX4000
Configuration issue
a) Delete bCX from BACnet side.
b) Perform find new BACnet devices from the root.
c) After device is found and present under the BACnet devices folder, right click on it and send it to the database.
  • 12979