Can a port-powered RS232-to-RS485 converter be used on bCX comm1?
  • Can a port-powered RS232-to-RS485 converter be used on bCX comm1?
  • BillNeville
    BillNeville
‎2018-09-06 10:31 AM
Can bCX comm1 power a port-powered RS232-to-RS485 converter?.
bCX
Need to connect Modbus RTU devices on RS485 bus to Xdriver on bCX comm1.
This has been done successfully according to posts on the Exchange commnuity. It is not a configuration that Product Support Services supports as it is not tested and there are many different devices on the market - some of whch may work and some which may not.