ReadPropertyMultiple Property Identifier: all (8) is not supported by the BACnet/IP Xdriver
  • ReadPropertyMultiple Property Identifier: all (8) is not supported by the BACnet/IP Xdriver
  • BillNeville
    BillNeville
‎2018-09-06 10:25 AM
A third party BACnet browser is trying to query Xdriver points. It sends ReadPropertyMultiple with a Property Identifier of "all (8)". The CX9680 responds with an error. Is this property supported by the BACnetIP Xdriver?
BACnet IP Xdriver
The ReadPropertyMultiple property identifier: all (8) is not supported by the Xdriver.
The ReadPropertyMultiple property identifier: all (8) is not supported by the Xdriver. The Xdriver only supports the following properties:
Value Access BACnet Property
85 R/W Present-Value
111 R Status-Flags
36 R Event State
81 R Out of Service
In the Xdriver manual the Quick Reference table in Appendix A indicates "Property 1-25 Service Limit". This is only for the DeviceSelf object and determines the number of asynchronous BACnet messages the Xdriver can send at a time. It effects the speed of polling (1 = slowest, 25 = fastest).
  • 13193