Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 487
    • 488
    • 489
    • …
    • 509
  • Next »

Replacement for sensor DEGA strap-on temperature transmitter

Issue Sensor DEGA is obsolete and no longer available for ordering. Environment DEGA: 00690080 00690543 00691544 00090563 STC300: 006920041 006920061 006920021 Cause Strap-on temperature transmitter with 4-20mA output signal Resolution The STC300 series sensor is replacing the DEGA series. Make sure to choose the appropriate sensor range for your application.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • Field Devices
887 Views

Xenta 301XT/N/P is not available

Issue Xenta 301XT/N/P is not available Environment Vista Xenta Cause Xenta 301XT/N/P is a Xenta unit made for the US market where some facilities needed some extra range of temperature. The XT stands for Extended Temperature. Resolution This unit is obsolete now and can no longer be ordered.
View full article
Picard Product_Support
‎2018-09-06 10:54 AM

Labels:
  • TAC Vista
887 Views

"Loading Properties" pop up displays but never finishes when an object is accessed in a Xenta controller.

Issue When extended trend object was opened in the Xenta 401 the "Loading properties" does not close down.  The controller appeared fine in all other respects. Environment Xenta 401 Cause In this case two technicians coincidentally attempted to access the same object at the same moment. Resolution Problem was resolved once the controller was downloaded.
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • EcoStruxure Building Operation
885 Views

How can a Network 8000 GCM-84000 or GCM-86000 be connected to the Niagara R2 UNC-520 RS-232 port?

Issue How can a Network 8000 GCM-84000 or GCM-86000 be connected to the Niagara R2 UNC-520 RS-232 port? Environment Network 8000 GCM-84000 GCM-86000 Niagara R2 Cause To use Network 8000 GCM-84000 or GCM-86000 with Niagara R2, connect using a pre-built adapters and silver satin cables. Resolution Pre-built adapters and silver satin cables for this type of connection are available for order.   The RJ-45 to DB-9 adaptor (UNCC-405) will interface to the GCM-86000. The RJ-45 to DB-25 adaptor (UNCC-430) will interface to a GCM-84000. A series of pre-terminated silver satin cables are available in three standard lengths: CBL-RJ45-4 Silver satin patch cable, 4 feet in length CBL-RJ45-10 Silver satin patch cable, 10 feet in length CBL-RJ45-25 Silver satin patch cable, 25 feet in length
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
899 Views

Is there a way to keep resending alarm notifications until they get acknowledged in R2?

Issue Is there a way to keep resending alarm notifications until they get acknowledged in R2? Environment R2, WorkPlace Pro (all versions) Cause N/A Resolution R2 does not provide a way to resend an alarm, already in an alarm state, until it gets acknowledged.  Resending alarms is possible in G3
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
886 Views

The No Server Light is illuminated on ACX78x Controller.

Issue Following a clean upgrade from Continuum 1.74 to 1.93, all ACX78x controllers show their No Server LED illuminated.  Environment ACX780 ACX781 Cause The SystemStatus system variable value is No Database. The AccessServer system variable on the ACX78x controller is not set to the ACCID of the primary access server workstation. Resolution Set the value of SystemStatus to Normal. An ACX78x controller must have it's AccessServer system variable set to 0 or to it's own ACCID.  While setting it to any other value, including the value of a workstations ACCID will cause the No Server LED to illuminate. 
View full article
Picard Product_Support
‎2018-09-06 01:14 PM

Labels:
  • Andover Continuum
894 Views

LonWorks group limitations in a single LON network in Vista

Issue How many LonWorks groups is it possible to have in one LON network in Vista? Environment LNS Vista networks Cause When designing a LON network, it is important to consider both the physical and the logical organization of the network. When dividing controllers into logical LonWorks groups, the limitations should not be exceeded. Resolution There is a limitation of 50 LonWorks groups in one LON network.
View full article
Picard Product_Support
‎2018-09-06 12:43 PM

Labels:
  • TAC Vista
881 Views

When editing an object, the Apply button works but changes are not saved.

Issue When an object is edited the Apply button becomes selectable, but when selected no changes are saved. Environment Continuum ContinuumDB SQL ContinuumServer Cause Insufficient space on hard drive. Resolution Move database backup files. Truncate log tables. Install automated log table truncation routines. 
View full article
Picard Product_Support
‎2018-09-06 12:23 PM

Labels:
  • Andover Continuum
892 Views

VG221F and Glycol

Issue Is it possible to use the VG221F valve in applications with a glycol content up to 50%? Environment VG221F Cause Some valves are not suitable for use in applications with glycol content in media. Resolution The VG221F can be used in applications with deaerated water with glycol-type antifreeze agent (max 50%)
View full article
Picard Product_Support
‎2018-09-06 12:13 PM

Labels:
  • Field Devices
880 Views

Sigma IC-Lon Plugin - The plugin crashes when SNVT's are added to it.

Issue Multiple function blocks using the same SNVT names in each function block, cause the Lon plugin to crash. Environment IC-Lon Plugin Multiple function blocks Cause In LonMaker, controllers which has multiple function blocks, and use the same SNVT names in each function block, cause the Lon plugin to crash. Resolution Work around - This issue can be overcome by manually changing the SNVT names in the function blocks to be unique, before using the IC-Lon Plugin. Below is the standard function block.   Here is a SNVT name having been modified. The next screen shot shows the view in the Sigma IC-Lon Plugin with the modified SNVT names.  
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • Satchwell BAS & Sigma
891 Views

Sigma - Global communications, what happens to the controllers if the network fails?

Issue What happens to Sigma globals if the network fails? Environment Globals Communications Networks Cause Site is to have a planned network shutdown, how will the Sigma controllers react to this? Resolution The Sigma controller using the global update, will continue to operate normally, but will use the last value received, so any changes will not be responded to. If the Sigma controller controls critical plant then the loss of global communications should be taken into account when programming.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Satchwell BAS & Sigma
877 Views

Do any of the SmartStruxure Lite room controllers come with a morning warm-up cycle?

Issue Do any of the SmartStruxure Lite room controllers come with a morning warm-up cycle? Environment SmartStruxure Lite SE8x000 SE7x00 Cause Spec requirement Resolution None of the room controllers come with morning warm-up.  It would have to be provided at the network level (i.e. Automation Server).
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Labels:
  • EcoStruxure Building Expert
887 Views

Xenta 104-A controller will not start cooling outputs.

Issue Xenta 104-A will control heating outputs but not cooling outputs. Environment Xenta 104-A Cause U1 is setup as a discharge temperature sensor if the outside air is bound into the controller. Resolution If the outside air is bound in as a SNVT connection and Bit 4 on nciAppOptions is set to on. When this occurs, U1 terminal 7 and 8 on the 104 become a Supply temperature sensor. If no 1.8k resistor is installed across these terminal the Supply temperature will read less than 0 causing the controller to think no cooling is needed as the supply temperature is so low. Install a 1.8k temperature across terminal 7 and 8 and this will allow normal control of the Xenta 104-A controller.
View full article
Picard Product_Support
‎2018-09-06 01:03 PM

Labels:
  • TAC Vista
884 Views

Remote Alarm Manager - What happens to an alarm message when the BST/GMT changeover occurs?

Issue What happens to an alarm message when the clocks go back during the BST/GMT changeover? Environment RAM Remote Alarm Manager Time Changeover BST GMT Cause This is an issue relating to RAM and how it handles BST/GMT changeover. If an alarm occurs, is it handled correctly by the Remote Alarm Manager? What will happen if the PC  time goes back, and the alarm is then cleared before the time passes the original alarm time. Will this cause any issues when viewing the alarm on the Remote Alarm Manager?   Resolution  Tests confirmed that there were no issues with this scenario; An alarm was generated at 15:46 and a text message was received. The PC time was put back an hour, and the alarm cleared at 14;52. . The alarm and the alarm cleared messages are shown in the RAM log below as 15:46 and 14:52 respectively.     The screen shot below shows the alarm status after the alarm was cleared.     The screen shot below shows the alarm properties, and here there is an error, the cleared state shows 15:52 which is incorrect.     When the time catches up everything returns to normal.
View full article
Picard Product_Support
‎2018-09-06 03:14 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
885 Views

Power Failure on MPM, the clock goes back to 1/1/2000.

Issue Each time that a power failure happens on a sites MPM, the clock goes back to 1/1/2000. Environment StruxureWare Lite MPM Cause This is most likely due to the battery shelf life, this happens if the controller was purchased and left unused for over 5 months before being installed. Resolution ∙ BR1220 from Panasonic (Lithium Carbon-Monofluoride) ∙ nominal voltage 3V ∙ Capacity 35mAh ∙ Self-discharge 1%/year, under standard conditions ∙ Operating temperature range -30°C to 85°C Units manufactured after week 13 2016 have a super capacitor rather than a battery. The capacitor has a charge time of approximately 5 minutes after which it will provide backup for the RTC for approx. 48 hours
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • EcoStruxure Building Expert
893 Views

Error: NS #171 lcaErrNsLNSUpgradeRequired

Issue NSS program ID changed. Requires upgrade or revert back to old interface. (Subsystem: NS, #171)  Environment LonMaker NL220 Vista LNS Cause If you open the Network Properties dialog, change the network interface from an LNS legacy Network Interface (also called NSI) to an LNS Fast Network Interface (also called VNI), or vice versa, and at the same time change from Offnet to Onnet, the LonMaker tool will report an NS #171 error (NSS upgrade required).  Resolution Change the network interface only -- remain offnet Click OK. Re-enter the Network Properties dialog and then change from Offnet to Onnet
View full article
Picard Product_Support
‎2018-09-07 03:50 AM

Labels:
  • TAC Vista
887 Views

On Site not communicating.

Issue Can read temperatures but system does not control outputs. On the Site Stat Controller Interface the SS light is not flashing. Environment OnSite Cause Field wiring error. Resolution In this case someone had rewired the temperature sensor with the x1 and x2 terminations reversed. Once x1 and x2 were wired correctly normal operation resumed.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Andover Continuum
898 Views

When uploading a GCM with TreeTech, do the ASD devices also need to be uploaded?

Issue On a jobsite doing a backup of a GCM and its ASD controllers.  After an upload of the GCM is complete, the ASD controllers appear in the tree (the upload of the GCM created them).  Do they also need to be uploaded individually? Environment TreeTech (any version) Cause Understanding all the steps in a proper / complete upload of a GCM and its controllers. Resolution The first step is to upload the GCM. The second step is to upload each individual ASD controller (Microzone II, Microflo II, etc...).  Each upload will take less than a minute.
View full article
Picard Product_Support
‎2018-09-06 10:45 AM

Labels:
  • TAC IA Series
883 Views

Is there a version of the Web.Client software available that is CFR compliant?

Issue Adding Web.Client to an existing site that has Continuum installed with the CFR compliance option. Environment Continuum with CFR Compliance Cause Can't find any part numbers for Web.Client with CFR compliance or an option to add it. Resolution We do not have an option for Web.Client with CFR. One of the requirements for CFR is the inclusion of operator text when performing certain actions; there is no way to prompt for, or supply, this operator text when using a Web.Client browser client.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • Andover Continuum
896 Views

Is there a repeater available for a MN-Sx cable run that goes beyond the specified distance?

Issue A MN-Sx sensor is installed more than 200 feet away (the maximum specified) from a MNL controller. The dynamic temperature value drops in and out at the controller.  Is there a repeater that can be installed to improve communications? Environment MNL MN-Sx Cause Cable run extends beyond the specified 200 feet. Resolution There is no repeater available that can be used for the MN-Sx cable run.
View full article
Picard Product_Support
‎2018-09-06 10:05 AM

Labels:
  • TAC IA Series
883 Views
  • « Previous
    • 1
    • …
    • 487
    • 488
    • 489
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of