Issue
A MN-Sx sensor is installed more than 200 feet away (the maximum specified) from a MNL controller.
The dynamic temperature value drops in and out at the controller. Is there a repeater that can be installed to improve communications?
Environment
MNL
MN-Sx
Cause
Cable run extends beyond the specified 200 feet.
Resolution
There is no repeater available that can be used for the MN-Sx cable run.