Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,837
  • TAC IA Series 1,820
  • TAC INET 1,458
  • Field Devices 720
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 403
    • 404
    • 405
    • …
    • 507
  • Next »

TTS100 Sensor Set Up

Issue Unable to set up a TTS100 Sensor on an MR88. Environment I/NET Controller with MR88 Sublan devices. Cause Hooking up a sensor on an MR88 and it is not reading the correct temperature on the Summary page. Resolution Verify that there is a 10K Ohm Resistor in the B Slot of the MR for the required point. Using an m=0.018 and b=-148, with counts of 0-255, since it is an 8 bit converter and Lookup Table #2 if it is on one of the Universal Inputs, or Lookup Table #1 if wired to the I/Stat port. It is connected to Red=Signal and Green=Ground.
View full article
Picard Product_Support
‎2018-09-06 02:19 PM

Labels:
  • TAC INET
1004 Views

The SigView_ATK (or SigView) 'List Object' report shows duplicated Object Titles.

Issue Using SigView_ATK to create reports the object title is duplicated in the Object List report.   Similarly, the various segment titles are also duplicate down the report columns. Environment Sigma 4.05 SP1/SP2 Sigma SEB Sigma ATK SigView ATK Cause Sigma 4.05 no longer automatically creates the pointer.bin files that is used by SigView_ATK to collect object data from the Sigma Index file, such as Object Titles. Resolution Create the pointer.bin files by either; 1.  Running SigmaX (v6) on the Laptop (engineers only) 2. For customers 4.05 SEB systems copy the utility 'GeneratePointerBin.exe to the C:\Sigma\Binutils location and run it.  3. For customers 4.05 SP1/SP2 systems copy the utility 'GeneratePointerBin.exe to the C:\Sigma\Bin location and run it Note: The utility needs to use the 'Fileutils.dll' to run and hence the above locations are used. The Sigma 4.05 Pointer Bin Generator utility is available in The Exchange Download Center.
View full article
Picard Product_Support
‎2018-09-07 04:15 AM

Labels:
  • Satchwell BAS & Sigma
1074 Views

Will a Power Supply PS 120/240 AC 85 work with a Netcontroller 1?

Issue Will a Power Supply PS 120/240 AC 85 work with a Netcontroller 1? Environment CX 9900 CX 9901 CX 9940 Cause Verifying power supply compatibility Resolution The PS120/240 AC 85 model power supply will work with CX 99xx model controllers.
View full article
Picard Product_Support
‎2018-09-06 02:15 PM

Labels:
  • Andover Continuum
1033 Views

Warranty claim or repair of I/NET 7910 controller (Purchased at Västerhaninge Sweden)

Issue Where to send broken/mal-function I/net hardware RMA Environment I/NET  Hardware Cause Can't find where to return a broken I/Net product Resolution Västerhaninge handles repairs, advance replacement and repurchase. Repair and advance replacements shall be added into their warranty claim system. http://warranty.tac.com   NOTE: The warranty starts from the day of purchase
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Labels:
  • TAC INET
1046 Views

Sigma WinCE - Device PCID changes.

Issue The PCID changes from the original registered code. Environment Sigma WinCE PDA devices. Cause This can be caused by leaving the Sigma WinCE device connected to a PC/Laptop. Resolution When registering the Sigma WinCE software ensure that the PDA is disconnected from the PC or Laptop. When starting the WinCE software ensure that the PDA is disconnected from the PC or Laptop.
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Labels:
  • Satchwell BAS & Sigma
1047 Views

Can Continuum software be run as a service

Issue Can Continuum software be run as a service Environment Continuum Cyberstation (all versions) Webclient (all versions) Cause Is Continuum software running as a service supported Resolution The Continuum Cyberstation  and Webclient Software cannot run as a service.
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Labels:
  • Andover Continuum
1086 Views

Cannot communicate to a third party device using the MODBus RTU X-Driver

Issue Values for a MODBus address are not coming in while using the MODbus RTU X-Driver Environment Controller MODBus X-Driver Cause The data type configured in the X-Driver point did not match the data type from the address on the third party device Resolution Review the data type from the third party documentation and configure the X-Driver point with the correct data type
View full article
Picard Product_Support
‎2018-09-06 02:13 PM

Labels:
  • Andover Continuum
1003 Views

Incorrect email's sent time when emailing from controller via SMTP

Issue Sending an email from the controller via PE or Web Page shows incorrect sent time. Environment NC2 - CX968x ACX2 - ACX57xx bCX Cause Time settings not configured correctly from controller's web page. Resolution From a web browser login to the controller's web configuration (point your browser to the IP of the controller) Go to "Controller Configuration\Time Setting" Enter the appropriate UTC offset for your time zone, for example if the controller is in the Eastern time zone enter -300 Use the "Daylight" Savings option to specify whether daylight savings time is in effect Finally click on the "Submit to Controller" button, there is no need to commit changes and re-start the controller.
View full article
Picard Product_Support
‎2018-09-06 02:13 PM

Labels:
  • Andover Continuum
1024 Views

Vista timestamp for alarms or Xenta trend logs are off by 1 hour

Issue Alarm time logged into Vista from a Xenta controller 1 Hour earlier than actual alarm time even though the Xenta and Vista Server have the same time. This can also cause issues with Xenta trend logs where they will have estimated values for the past hour worth of logs. Environment Workstation Xenta Controllers Cause The offline (Engineering) Daylight / Standard time (DST) settings do not match the online (Operating) Daylight / Standard time settings. Resolution The Daylight saving and Standard time settings need to be corrected in the Xenta controller as follow: Place Vista into Engineering mode using the drop down list on the tool bar. Select the controller that is having the alarm time error. Right mouse click and select Properties. Select the Time Settings tab. Correct the Daylight saving and Standard Time settings. Return the Vista into Operating Mode using the drop down list on the tool bar. Retest alarm for correct time stamp or recheck your Xenta trend logs.
View full article
Picard Product_Support
‎2018-09-06 02:11 PM

Labels:
  • TAC Vista
1048 Views

How to prevent times schedules from being overwritten when downloading an updated version of the XBuilder project to a Xenta Server

Issue How to prevent times schedules from being overwritten when downloading an updated version of the XBuilder project to a Xenta Server. When uploading new configuration to Xenta 7xx device, all the scheduling is deleted. TSCH changes made from web interface are deleted when downloading the XBuilder project again Environment TAC XBuilder TAC Xenta server Cause There is no automatic check to see if time schedules have been modified since the last download. Information must be manually uploaded to the project. Resolution Before sending the updated Xbuilder project to target: Go to Project - Get from target Select Get online changes, click ok. Now the updated schedules are saved in XBuilder.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • TAC Vista
1013 Views

Delay on a change of state object in Vista

Issue Is it possible to set a delay on a change of state object in Vista? Environment TAC Vista 5.1.5 Cause Need to set a delay on a change of state object in Vista Resolution No it is not possible.
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • TAC Vista
1021 Views

Deny Entry Tenant when entering new badges after restoring from a system crash

Issue Deny Entry Tenant when entering new badges after restoring from a system crash on a New Host workstation Environment I/NET Cause Devices in the field may still be looking for the former workstation due to a system setting such as automatic DPU restore. Resolution Connect to the controller Select Edit>Controller>Station Save Select Edit>Controller>Station Restore Select The DPU option Select the affected DPU and click okay Try a badge to verify results This error should only occur when badges are added immediately after a system recovery.  If the issue continues, contact product support.
View full article
Picard Product_Support
‎2018-09-06 02:08 PM

Labels:
  • TAC INET
1062 Views

Linking to a File from a TMGL Graphics page in Vista Workstation

Issue Having trouble Linking to a File from a TMGL Graphics page in Vista Workstation Environment TGML Vista Workstation Cause Most likely cause is not using the correct button type or script feature.  Below is the most basic means to link to a file. Resolution Add the "FileButton" object found in the Basic Controls Component Library to the TMGL file Select the object In the Properties Window, scroll down to the heading "Custom" and the property "File" Type in the complete path and filename. Example C:\Vista_Files\TGML.pdf Save the TGML graphics page Test the link in Vista workstation
View full article
Picard Product_Support
‎2018-09-06 02:08 PM

Labels:
  • TAC Vista
1094 Views

Inactivation of Remote Alarm Manager alarm message

Issue The Remote Alarm Manager sends a message to the recipient indicating that an alarm has been inactivated. The screen shot below shows how a typical message will appear on the receiving mobile phone. Product Line Other, Satchwell MicroNet, Satchwell Sigma, TAC Vista Environment Remote Alarm Manager version 1.2 Cause An alarm message is generated, and the Remote Alarm Manager processes it in the normal way. After three days and at midnight, the Remote Alarm Manager will send a inactivation message to the on-call recipient, indicating that this alarm has been inactivated. Resolution This is not a fault with the system, it is operating as designed. When a new alarm is received by the Remote Alarm Manager, it is acted on in the way the configuration dictates. If the alarm remains on the system, without being retransmitted, then after three days the inactivation takes place. The 3 days is the default setting and can be changed if required.
View full article
Picard Product_Support
‎2018-09-07 06:17 AM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
1085 Views

Time of day displayed on an I/A Series R2 (Niagara) Enterprise Server system is off by one hour for several weeks each spring and fall.

Issue Between the second Sunday of March and the last Sunday of April, the I/A Series R2 Enterprise Server clock is one hour earlier that the time shown on the host computer. Between the last Sunday of October and the first Sunday of November, the I/A Series R2 Enterprise Server clock is one hour later that the time shown on the host computer. The noted times apply to the North American time zones.  Similar errors may also be seen in other time zones. Environment Any supported Windows operating system. I/A Series R2 (Niagara) software release 522 or newer Cause The Windows operating system has not been updated with the current daylight savings time rules update. The I/A Series R2 (Niagara) software, release 522 and newer includes the updated daylight savings time rules.   Resolution Download and install the appropriate Microsoft Windows operating system software update, per the Microsoft Knowledgebase article 955839 to update the computer's daylight savings time rules. The update can be downloaded from the Microsoft support web site at http://support.microsoft.com/kb/955839.  This Microsoft  Knowledgebase article contains links to the downloadable upgrade file for each of the affected versions of the Windows operating system as well as any related installation prerequisites.
View full article
Picard Product_Support
‎2018-09-07 12:42 PM

Labels:
  • TAC IA Series
1006 Views

When applying a Continuum Service pack, will this need to be installed on all workstations?

Issue Site has 26 Continuum workstations at 1.74 and wants to install SP2 for 1.74. Does this service pack need to be installed on all 26 Continuum workstations. Environment Continuum Cyberstation 1.74 Service Pack 2 Cause Continuum workstation and service pack compatibility Resolution When a Continuum service pack for specific versions is applied to one workstation, it will need to be applied to all workstations. Please review the readme file located in all service pack zipped files.
View full article
Picard Product_Support
‎2018-09-06 02:07 PM

Labels:
  • Andover Continuum
1064 Views

Updating a Continuum database in a LAN system

Issue Do you have to update the DB from multiple workstations in a CyberStation LAN environment Environment CyberStation Database Update Upgrade SQL Server LAN Cause Update of the Continuum database on a LAN environment Resolution You only need to update the database from one workstation when upgrading a LAN system
View full article
Picard Product_Support
‎2018-09-06 02:03 PM

Labels:
  • Andover Continuum
1062 Views

B_Link Fiber devices cannot be used on the IP network

Issue Can B_Link Fiber devices be used on the IP network? Environment Network Topology Windows XP B-link Repeater BCX 4040 B4920 BACnet Repeater RS-485 Cause Configuration of Fiber Network Resolution No. The B-Link Repeater is used on the RS-485 Network not IP.
View full article
Picard Product_Support
‎2018-09-06 02:02 PM

Labels:
  • Andover Continuum
1048 Views

How to alarm when a particular access card is presented at a door

Issue Alarming on specific card swipes Environment CyberStation CX9702 CX9900 CX9680 ACX5720 ACX5740 ACX700 ACX781 Cause Need for alert alarm when a given credential holder(s) is attempting access at a door Resolution Write a PE program in the controller that monitors the door for access attempts and check whether the last card presented at the door is in a list of cards that been designated for alarming. In the sample program below CardAlertList is an InfinityNumeric array containing the list of card numbers to alarm on. An Alarm Enrollment configured to alarm when Value > 0 is attached to CardAlertList It is assumed that all cards have the same site code, if multiple site codes are used then the program needs to be modified to take site code in consideration. SAMPLE PROGRAM: 'This program triggers an alarm when any card which number is contained 'in the CardAlertList array is presented at the door. 'Program flowtype is fall thru 'Triggered by the Second system variable Numeric n CardAlertList = 0 'If a card has been presented at the door If Door1 InvalidEntryTime > Dr1LastInvalTime or Door1 TimeEntered > Dr1LastValidTime then 'Check to see if the card is in the list   For n = 1 to CardAlertList Size  'if the card number is in the list send alarm     If CardAlertList[n] = Door1 EntryLastCard then CardAlertList = Door1 EntryLastCard   Next n Endif 'store last card transaction time for comparison next time program runs Dr1LastInvalTime = Door1 InvalidEntryTime Dr1LastValidTime = Door1 TimeEntered Stop E:
View full article
Picard Product_Support
‎2018-09-06 02:01 PM

Labels:
  • Andover Continuum
1022 Views

Replacement of AVUE Mk 1 Actuator installed on VEU, MEU or FEU Mk 2 Unit Control Valve Body due to Actuator obsolescence.

Issue Replacement of AVUE Mk 1 Actuator installed on VEU, MEU or FEU Mk 2 Unit Control Valve Body due to Actuator obsolescence. Environment AVUE Mk 1 Actuator installed on VEU, MEU or FEU Mk 2 Unit Control Valve Body. Cause AVUE Mk 1 Actuator obsolescence. Resolution Replace AVUE Mk 1 Actuator. AVUE Mk 5 Actuators are not compatible with the VEU, MEU or FEU Mk 2 Unit Control Valve Bodies. It will therefore be necessary to replace both the AVUE Mk 1 Actuator and the Valve Body on which it is installed. Replacement products may be selected from the following :- AVUE Mk 1 Actuator = MZ20A or MZ20A-R VEU Mk 2 Valve Body (2-port) = VZ219 series of appropriate connection type / size / Kv rating MEU Mk 2 Valve Body (3-port) = VZ319 series of appropriate connection type / size / Kv rating FEU Mk 2 Valve Body (4-port) = VZ419 series of appropriate connection type / size / Kv rating   N.B. It should be noted that there may be dimensional variations between the existing and replacement Valve Bodies.
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Labels:
  • Field Devices
1039 Views
  • « Previous
    • 1
    • …
    • 403
    • 404
    • 405
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now