How to alarm when a particular access card is presented at a door

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to alarm when a particular access card is presented at a door
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1157 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to alarm when a particular access card is presented at a door

Picard Product_Support
‎2018-09-06 02:01 PM

Issue

Alarming on specific card swipes

Environment

CyberStation

CX9702

CX9900

CX9680

ACX5720

ACX5740

ACX700

ACX781

Cause

Need for alert alarm when a given credential holder(s) is attempting access at a door

Resolution

Write a PE program in the controller that monitors the door for access attempts and check whether the last card presented at the door is in a list of cards that been designated for alarming.

In the sample program below CardAlertList is an InfinityNumeric array containing the list of card numbers to alarm on. An Alarm Enrollment configured to alarm when Value > 0 is attached to CardAlertList

It is assumed that all cards have the same site code, if multiple site codes are used then the program needs to be modified to take site code in consideration.

SAMPLE PROGRAM:

'This program triggers an alarm when any card which number is contained
'in the CardAlertList array is presented at the door.
'Program flowtype is fall thru
'Triggered by the Second system variable

Numeric n

CardAlertList = 0

'If a card has been presented at the door
If Door1 InvalidEntryTime > Dr1LastInvalTime or Door1 TimeEntered > Dr1LastValidTime then

'Check to see if the card is in the list
  For n = 1 to CardAlertList Size 
'if the card number is in the list send alarm
    If CardAlertList[n] = Door1 EntryLastCard then CardAlertList = Door1 EntryLastCard

  Next n

Endif

'store last card transaction time for comparison next time program runs
Dr1LastInvalTime = Door1 InvalidEntryTime
Dr1LastValidTime = Door1 TimeEntered


Stop

E:

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4784
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore