Issue
When generating a 'List Object' report using SigView_ATK (or SigView), object titles and segment titles appear duplicated throughout the report columns.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma 4.05 SP1/SP2
- Sigma SEB
- Sigma ATK
- SigView ATK
Cause
Sigma version 4.05 no longer automatically generates the pointer.bin file. This file is essential for SigView_ATK to retrieve object data (e.g., Object Titles) from the Sigma Index file.
Resolution
To resolve the duplication issue, manually generate the pointer.bin file using one of the following methods:
Option 1: For Engineers
- Run SigmaX (v6) on your laptop. This will create the required
pointer.binfile.
Option 2: For Customers Using Sigma 4.05 SEB
- Copy the utility
GeneratePointerBin.exeto:C:\Sigma\Binutils - Run the utility from this location.
Option 3: For Customers Using Sigma 4.05 SP1/SP2
- Copy
GeneratePointerBin.exeto:C:\Sigma\Bin -
- Run the utility from this location.
Note: The utility requires
Fileutils.dllto operate correctly, which is why the specified directories must be used.
Additional Information
- The Sigma 4.05 Pointer Bin Generator utility is available for download from the Exchange Download Center.