Issue
Unable to set up a TTS100 Sensor on an MR88.
Environment
I/NET Controller with MR88 Sublan devices.
Cause
Hooking up a sensor on an MR88 and it is not reading the correct temperature on the Summary page.
Resolution
Verify that there is a 10K Ohm Resistor in the B Slot of the MR for the required point. Using an m=0.018 and b=-148, with counts of 0-255, since it is an 8 bit converter and Lookup Table #2 if it is on one of the Universal Inputs, or Lookup Table #1 if wired to the I/Stat port. It is connected to Red=Signal and Green=Ground.