Incorrect email's sent time when emailing from controller via SMTP
  • Incorrect email's sent time when emailing from controller via SMTP
  • AbeMeran
    AbeMeran
‎2018-09-06 02:13 PM
Sending an email from the controller via PE or Web Page shows incorrect sent time.
NC2 - CX968x
ACX2 - ACX57xx
bCX
Time settings not configured correctly from controller's web page.
  1. From a web browser login to the controller's web configuration (point your browser to the IP of the controller)
  2. Go to "Controller Configuration\Time Setting"
  3. Enter the appropriate UTC offset for your time zone, for example if the controller is in the Eastern time zone enter -300
  4. Use the "Daylight" Savings option to specify whether daylight savings time is in effect
  5. Finally click on the "Submit to Controller" button, there is no need to commit changes and re-start the controller.
  • 4454