Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 488
    • 489
    • 490
    • …
    • 509
  • Next »

Controller locks up on configuration of the Modbus TCP-IP XDriver.

Issue Controller locks up on configuration of the Modbus TCP-IP XDriver. Environment Continuum Controller Cause The Device Comm Status point was created as an InfinityString instead of InfinityNumeric Resolution Delete the incorrect Device Comm Status point and re-create it appropriately as an InfinityNumeric.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
1168 Views

How to configure Modbus TCP-IP Xdriver for CLIENT or SERVER operation.

Issue  The Modbus TCP-IP XDriver can function as either a TCP Client or a TCP Server but not both at the same time. Environment Cyberstation Continuum Controllers Cause Documentation Resolution  It is the XDriver points themselves that define the mode of the driver, in every point created, Parameter 2 should be set to either “0” for Client Mode OR to “1” for Server mode. You can’t use both in one driver. ALSO, in Client mode you need to create the Remote Device Status point, one per server, but it is Parameter 2 in the points that determines the client/ Server mode. QUESTION: If the XDriver can only operate in one mode (client or server) why does each point need to be configured with the mode type? ANSWER: There is a historical reason for this, the original design envisioned the support of both client and server points simultaneously, but for reasons that are well beyond the scope of this article this was changed to support only one mode at a time.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
1725 Views

Sample code for "two man" rule card access.

Issue Require sample code to configure a Door for the "two man" rule, where two valid card reads are required before a door is opened. Environment Continuum Access Control ACX5720 ACX5740 Cause Require sample code to configure a Door for the "two man" rule. Resolution For this "two man" rule you would need to take control from the Door object and do this through a Plain English program. Make sure to remove the door status input from the Door and define this as an Infinity Input if you want to use it within the Door program, otherwise the door will never show a "ValidAccess" signal for the program to work as it will be waiting for someone to walk through the Door first. See below example code of one way to accomplish this.   ========== Sample Code ========== Numeric LastCard WaitForValid1:   Door1 = off     If Door1 ValidAccess is True then       LastCard = Door1 EntryLastCard       GoTo WaitForValid2     Endif WaitForValid2:   If TS > 5s then     goto WaitForValid1   else     If (Door1 ValidAccess is True) and (Door1 EntryLastCard <> LastCard) then       Door1 = on       goto TimeWait     endif   endif TimeWait:   if TS > 5s then goto WaitForValid1 ===============================  
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
1391 Views

Enable / Disable Email Delivery From a Graphic

Issue Have the ability in SBO to disable and enable the email delivery from a graphic with a simple switch Environment Automation Server (AS), Enterprise Server (ES) - all versions Cause - none - Resolution In order to enable / disable email delivery from a graphic, do the following: 1. Add a Switch component to a graphic. Save the graphic. 2. In Workstation, open the bindings window for the graphic. Bind the Status of the Email Notification to the Value of the Switch.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • EcoStruxure Building Operation
1545 Views

Error updating row in the database table when manipulating object.

Issue Error updating row in the database table when manipulating object. Environment Cyberstation Cause Workstation using unsupported SQL Native Client 10.0 Resolution Use supported version of the SQL Native Client
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
1036 Views

How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?

Issue How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers? Environment I/A Series G3, SE7000 Series Room Controllers Cause Setpoint values on the LON based SE7000 Series Room Controllers are maintained as a network configuration property (nciSetPts).  Local setpoint changes will not be seen at the I/A Series G3 station unless the value is polled or read. Resolution I/A Series R2 had an object (PollSnvtTempSetptCmd) in the lonextras jar that could be set to poll the nci values on a configurable time basis.  The same functionality can be setup in I/A Series G3 through the use of an interval trigger. Open the kitControl palette and expand the ControlPalette - Trigger folder Add an Interval trigger object and configure as Trigger Mode with the Interval required.  The Interval will determine how often the nciSetPts is updated (polled).  The recommendation would be 60 seconds. Right Click on the Trigger and select “Link Mark” Right Click on the SE Room Controller and display the property sheet for the device Locate and Right Click on the nciSetPts parameter.  Select Link From “Name of Your Trigger”. When the link window appears, select Fire Trigger and then select Force Read.  Select OK to complete the link. All setpoints included in the nciSetPts parameter will be updated at the time interval configured to read what has been set at the local device.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Field Devices
  • TAC IA Series
982 Views

"Invoke or BeginInvoke cannot be called on a control until the window handle has been created" Error when Installing SQL 2008

Issue When installing SQL server 2008 or SQL 2008 R2 to manually an instance for I/NET, Vista or Continuum, sometimes an error "Invoke or BeginInvoke cannot be called on a control until the window handle has been created" will show up. Environment SQL 2008 / SQL 2008 R2 Vista I/NET Continuum SmartStruxure Cause This issue is happening because of a behavior change in .NET that is exposing an issue with SQL Setup User Interface (UI). Resolution Generally, if you just rerun the installer, it won't hit the issue again. If this can't help, just manually create a C:\temp folder and it will work fine.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
2166 Views

Function Block applications made in TAC Menta may not import into StruxureWare Building Operation

Issue When importing a file from TAC Menta into StruxureWare Building Operation Functional Block Editor, the import of the application file fails. Environment TAC Vista TAC Xenta StruxureWare Building Operation Cause The following characters are not allowed in object names in StruxureWare Building Operation. • / • " • ? • * • ~ • White space is not allowed in the beginning or the end of an objects name. • . (period) is not allowed in the beginning of an objects name. Colon (:) is not allowed either, but will automatically be replace by an underscore (_) when importing   In TAC Vista, signal names could contain the character "/". In SmartStruxure, this character is not allowed. Resolution Remove illegal characters from object names in the Function Block program.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1763 Views

Access denied error creating ContinuumDB

Issue Access denied error creating ContinuumDB Environment Cyberstation SQL Server Cause Firewall blocking Resolution Ensure the firewall at both the WS and the SQL Server are not blocking the DB creation process. Turn off all aspects of McAfee or Norton Anti-Virus. In particular, McAfee On-Access Virus Scanning can cause this
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • Andover Continuum
1306 Views

Losing VAS client connection; getting error: java.lang.outofmemoryerror: unable to create a new native thread.

Issue Losing VAS client connection; getting error: java.lang.outofmemoryerror: unable to create a new native thread. Environment R2 VAS 2.50 Cause Users at the client were not signing off but rather switching users causing multiple connections to VAS from the same pc.  Resolution Ensure user is logging off, not just switching users.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • TAC IA Series
975 Views

Is RS-485 node activation required on a 57xx series acx to connect the SCH-PIM400-485

Issue Normally using RS-485 on an ACX 57xx requires nodes to be activated to work so ordering and price could be affected by this Environment ACX57xx Schlage PIM 400-485 Cause The Schlage PIM RS-485 unit uses RS485 for communication and it's important to know if node activation is required for the Schlage solution to work Resolution The Schlage PIM RS-485 does use RS-485 for communication, but it doesn't require node activation on the comm port. The Schlage solution uses an XDriver instead in order to communicate RS-485 to the PIM
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • Andover Continuum
1248 Views

Is it possible to use the analog output on the TAC Xenta 121-FC even if I want to have the Occupancy mode indicator on a STR150?

Issue When using STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device. Environment TAC Xenta 121-FC STR150 Cause When using a STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device. Resolution In ZBuilder, it is possible to move the Occupancy Mode indication from the default location at Y1 to K1-4. In this case you also need to have an external power supply with 5 Volt DC for the Occupancy Mode indicator.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • TAC Vista
1287 Views

Can a G3 / AX Jace do fox tunneling?

Issue Customer has a Jace-7 installed with two NICs.  It's installed with 3.7.106. NIC 1 (192.168.1.101) is communicating with 3 other jaces on-site with IP addresses of 192.168.1.102, 103, & 104. NIC 2  (public address) is accessed remotely with Workbench. Is there a way to access the stations (remotely) running on 192.168.1.102, 103 & 104 with fox tunneling? Environment Niagara G3 / AX Cause There is no Enterprise Server on site, just the four Jaces. Resolution Jaces cannot act as Proxy Servers so fox tunneling is not supported on anything except a server.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • TAC IA Series
1485 Views

Actuator feedback is connected to a MNL controller and displays a negative '%open" position.

Issue A customer installed a critical valve with an actuator containing a potentiometer for a positional feedback connection. The potentiometer was wired into a MNL controller's input. After some calibrating, the potentiometer drives past the "0 %open" position which displays as a negative value in the AI point. Is there a way to compensate in software for this negative reading? Environment WorkPlace Tech MNL and MNB controllers Cause It can be difficult to calibrate the feedback potentiometer accurately. Resolution Add a high selector block to the output of the AI block.  Connect the AI block's output and a constant set to a value of zero. Anytime the AI block's output drops below zero, the output of the high selector will display zero.  This can then be used for other logic or for graphical display.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • TAC IA Series
1175 Views

Can the manual override switches on the I/O modules still be used if the device is broken?

Issue We want to be able to control the outputs on an I/O even if the I/O module is broken. Environment StruxureWare Building Operation I/O Modules   Cause The switches for manual override on the I/O modules needs power to be able to operate. Resolution The switches on the I/O modules that are used for manual override internally controls relays, that need to be powered to be able to operate.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • EcoStruxure Building Operation
888 Views

Editing the Continuum security group export file outside of Continuum.

Issue Is there a way to edit the Continuum Security Group export file outside of Continuum? Environment Security Groups .sdf file format Cause The need for a more efficient method of editing Continuum user Security Groups. Resolution There is no method of editing the Security Groups export file outside of Continuum.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
961 Views

SBO user accounts not working as configured.

Issue Graphics are not displaying values under certain user accounts Environment User Accounts Domains Cause Although the user account configuration appeared to be correct, something in the user accounts was broken. Resolution Once the User Accounts were deleted and recreated with exactly the same configuration the graphics began displaying the values. 
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • EcoStruxure Building Operation
1094 Views

Continuum controller grounding requirements.

Issue The electrical contractor failed to pull an ground conductor with the controller power conductors.   Environment Controller installation. Controller Power. Cause Electrical contractor neglected to include a ground conductor when running power to the controller panel. Resolution All installation for the entire Continuum and Infinity controller product lines indicate that the controller power terminal must have a true earth ground connected to the ground terminal. Continuum controllers require a true earth ground connected to the ground terminal of the controller power strip.  Controller grounding is essential and impacts the controller in several ways including sensor bus communication, input accuracy, processor function and output performance. Improper grounding can also, in some cases, cause damage to the controllers.   The problem with grounding to the electrical enclosure or to the building structure is that each grounding point can have different  a ground potentials. This will especially cause issues with bus communication since all controller signals must be established with respect to the same ground reference. If each controller has a different ground reference the wave forms will be inconsistent.  
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
1163 Views

Is it possible to access the value of a doors ADA output for programming or reporting via graphics, listviews or reports?

Issue Is there a way to display the value of a doors ADA output or to use this value in a Plain English program? Environment ADA output Door attributes Cause Need to display and track the value of a doors ADA output. Resolution There is no sanctioned way to access or use the value of a doors ADA output.  While in some cases it may be possible to create a separate output object with the same channel number to track this value, this kind of configuration is known to have issues and it is not recommended.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
1040 Views

License Setup changes without user interaction and reverts to previous configuration

Issue The configuration in "License Setup" changes autonomously meaning that you open "License Setup", make a change, close "License Setup", open "License Setup" and the configuration has reverted to what is was before the change was made. It reverts back to what it was before making the change. Environment TAC Vista 5.1.9 Cause The cause of this is unknown. TAC Vista Server is supposed to set some values in the registry while running also regarding licensing, but not like described here. Resolution Make sure TAC Vista Server is stopped while changing the license setup: Stop TAC Vista Server Change the license setup Start TAC Vista Server
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • TAC Vista
1106 Views
  • « Previous
    • 1
    • …
    • 488
    • 489
    • 490
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of