Issue
Controller locks up on configuration of the Modbus TCP-IP XDriver.
Environment
Continuum Controller
Cause
The Device Comm Status point was created as an InfinityString instead of InfinityNumeric
Resolution
Delete the incorrect Device Comm Status point and re-create it appropriately as an InfinityNumeric.