Sample code for "two man" rule card access.
  • Sample code for "two man" rule card access.
  • AdamSteele
    AdamSteele
‎2018-09-06 09:36 AM
Require sample code to configure a Door for the "two man" rule, where two valid card reads are required before a door is opened.
Continuum Access Control
ACX5720
ACX5740
Require sample code to configure a Door for the "two man" rule.
For this "two man" rule you would need to take control from the Door object and do this through a Plain English program. Make sure to remove the door status input from the Door and define this as an Infinity Input if you want to use it within the Door program, otherwise the door will never show a "ValidAccess" signal for the program to work as it will be waiting for someone to walk through the Door first. See below example code of one way to accomplish this.
========== Sample Code ==========
Numeric LastCard
WaitForValid1:
  Door1 = off
    If Door1 ValidAccess is True then
      LastCard = Door1 EntryLastCard
      GoTo WaitForValid2
    Endif
WaitForValid2:
  If TS > 5s then
    goto WaitForValid1
  else
    If (Door1 ValidAccess is True) and (Door1 EntryLastCard <> LastCard) then
      Door1 = on
      goto TimeWait
    endif
  endif
TimeWait:
  if TS > 5s then goto WaitForValid1
Tags (2)
  • 16044
  • acx57xx