Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
939 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?

Picard Product_Support
‎2018-09-06 09:36 AM

Issue

How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?

Environment

I/A Series G3, SE7000 Series Room Controllers

Cause

Setpoint values on the LON based SE7000 Series Room Controllers are maintained as a network configuration property (nciSetPts).  Local setpoint changes will not be seen at the I/A Series G3 station unless the value is polled or read.

Resolution

I/A Series R2 had an object (PollSnvtTempSetptCmd) in the lonextras jar that could be set to poll the nci values on a configurable time basis.  The same functionality can be setup in I/A Series G3 through the use of an interval trigger.

  1. Open the kitControl palette and expand the ControlPalette - Trigger folder
  2. Add an Interval trigger object and configure as Trigger Mode with the Interval required.  The Interval will determine how often the nciSetPts is updated (polled).  The recommendation would be 60 seconds.
  3. Right Click on the Trigger and select “Link Mark”
  4. Right Click on the SE Room Controller and display the property sheet for the device
  5. Locate and Right Click on the nciSetPts parameter.  Select Link From “Name of Your Trigger”.
  6. When the link window appears, select Fire Trigger and then select Force Read.  Select OK to complete the link.
  7. All setpoints included in the nciSetPts parameter will be updated at the time interval configured to read what has been set at the local device.
Labels (2)
Labels:
  • Field Devices
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 16080
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now