How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?
  • How can I/A Series G3 be configured to monitor local setpoint changes on the LON based SE7000 Series Room Controllers?
  • WaynePeters
    WaynePeters
‎2018-09-06 09:36 AM
I/A Series G3, SE7000 Series Room Controllers
Setpoint values on the LON based SE7000 Series Room Controllers are maintained as a network configuration property (nciSetPts).  Local setpoint changes will not be seen at the I/A Series G3 station unless the value is polled or read.
I/A Series R2 had an object (PollSnvtTempSetptCmd) in the lonextras jar that could be set to poll the nci values on a configurable time basis.  The same functionality can be setup in I/A Series G3 through the use of an interval trigger.
  1. Open the kitControl palette and expand the ControlPalette - Trigger folder
  2. Add an Interval trigger object and configure as Trigger Mode with the Interval required.  The Interval will determine how often the nciSetPts is updated (polled).  The recommendation would be 60 seconds.
  3. Right Click on the Trigger and select “Link Mark”
  4. Right Click on the SE Room Controller and display the property sheet for the device
  5. Locate and Right Click on the nciSetPts parameter.  Select Link From “Name of Your Trigger”.
  6. When the link window appears, select Fire Trigger and then select Force Read.  Select OK to complete the link.
  7. All setpoints included in the nciSetPts parameter will be updated at the time interval configured to read what has been set at the local device.
Labels (2)
  • Field Devices
  • TAC IA Series
  • 16080