Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 332
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 471
    • 472
    • 473
    • …
    • 508
  • Next »

Unable to communicate with controller after correctly configuring and enabling Network Security.

Issue Controller comm is lost after enabling Network Security after properly configuring the Controller and Workstation. Environment Network Security NCII CX9680 ACX5740 ACX5780 Cause Network security activation was being inhibited by the domain user security policies. Resolution In this case both the controllers and Windows network security policies had been configured properly for Continuum.  This fact was confirmed when the IT department got involved.  Once they relaxed some of the security policies on this machine Continuum network security began to work as expected, both from the controller and Cyberstation point of view. The customers IT personnel did not share with us what policies were responsible for the activation issues.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1075 Views

Unable to reload or upgrade firmware on a controller.

Issue Controller drops offline when reloaded or when an attempt to flash firmware is made. Environment Infinet MSTP Cause Massive CRC errors on the MSTP bus due to a bad controller on one leg of blink. Resolution In this case the problem was due to a bad controller on the bus.  The offending controller was located by segmenting the bus to determine which legs were introducing this problem. Once it was determined which controller was causing this issue, the controller was removed and a replacement installed.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1169 Views

What is required to upgrade a UNC 196 outstation to a Sigma x96 controller?

Issue Upgrading a UNC 196 outstation. Environment UNC 196 296 Upgrade Cause Customer wishes to upgrade his BAS outstation to a Sigma controller. Resolution To upgrade the outstation the following cards will need to be replaced. Comms/CPU Card Power Supply Card. These can be purchased together as an S-x96-UPKIT If the outstation also contains a Maximum Demand card, this is replaced by a Digital Input card (S-UNC-DI).
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Satchwell BAS & Sigma
1689 Views

Importing a Xenta 121-FC controller into StruxureWare Building Operation.

Issue Importing a Xenta 121-FC controller into StruxureWare Building Operation. Environment Xenta 121FC Cause How do you setup the Xenta 121-FC using StruxureWare Building Operation only, as all the config needs setting for 1 Return Temp. Cooling Only (AO type). Fan On/Off   Resolution The original process would require the use of LonMaker and ZBuilder to configure the Xenta 121-FC controller onto the LON network, before adding it to the StruxureWare Building Operation LON interface. Version 1.4 introduces LNS device plug-in support to configure LonWorks® devices. StruxureWare Building Operation v1.4 supports third party software: OpenLNS. OpenLNS is only required on WorkStation machines used for configuration of LON® devices (e.g. WorkStation Pro machines). Automation Server and Enterprise Server databases are updated with any changes created with the plug-in. With LNS device plug-in support, now ZBuilder can be used with SmartStruxure solution. Plus, all Xenta controllers are supported, including the X100 series – e.g. Xenta 121.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • EcoStruxure Building Operation
1395 Views

Infinity controller goes offline every five to ten minutes.

Issue BCX9680 controller goes offline every five to ten minutes then returns online. Environment Infinity Controller BCX NC CX Cause Duplicate IP address on the network. Resolution Give the controller a unique IP address.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1393 Views

Webreport 1.4 - The Web Server threw an exception

Issue The Web Server threw an exception. Please make sure the StruxurewareReportingAgent service is running and is set to run "Automatic" An error occurred on the Web Server while processing your request. If the problem persists, please contact your system administrator. Environment Webreport 1.4 upgrade Cause A WebReports installer must use an admin-level SQL Server Management Studio user account to log on to a computer running WebReports. This installer account also requires the addition of three database permissions that permit access to and control of the WebReports database during installs or upgrades. For example, an administrator can detach the database. In SQL Server Management Studio, verify that the Login Properties for the NTAuthority\IUSR and designated WebReports installer user accounts include the db_datareader, db_datawriter, and db_owner database role memberships. Resolution Use SQL management SQL studio and log in to the SQL. Use properties on the user NTAuthority\IUSR and make sure the following are included db_datareader, db_datawriter, and db_owner database role memberships.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • EcoStruxure Building Operation
1461 Views

Do the Jace-6 or Jace-7 need multiple Modbus drivers if more than one port is used?

Issue The jobsite will eventually have 4 RS-485 trunks each communicating Modbus.  Two option cards have been ordered with the Jace (part# TRD-NPB-2X-485). Does each port on the option cards need a separate Modbus driver purchased for each? Environment Niagara G3 Cause Ordering/licensing clarification Resolution Purchasing one Modbus driver (part# ENC-DRV-MOD) will cover all ports used for Modbus on the Jace-6/7.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • TAC IA Series
1226 Views

Continuously repeated errors in Standard Output Window of R2 (Niagara) station, "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)"...

Issue Continuously repeated errors in Standard Output Window of R2 (Niagara) station,  "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)" . The integer increments by one about every second until it reaches 128, then reverses the count, counting down by one into negative numbers. Environment I/A Series R2 UNC with the GCM driver Network 8000 GCM Cause The cause of the problem was resolved with the gcm-2.304.530b.v1.jar. Resolution This is considered a nuisance error, and was corrected in the gcm-2.304.530b.v1.jar.
View full article
Picard Product_Support
‎2018-09-11 02:24 PM

Labels:
  • TAC IA Series
1294 Views

How does Cyberstation interface with MS Outlook to deliver email reports and alarms.

Issue The customer is requesting a documentation on how the Alarm notification from Continuum works with MS Outlook to send out alarm email alerts to their facility engineers.   Environment MAPI MS Outlook CyberStation Email Cause The client is asking for information on how Cyberstation works with MS Outlook. Resolution Continuum uses the Enhanced MAPI messaging architecture to interface with MAPI compliant messaging applications/systems.  To understand this process in better, research Enhanced MAPI.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1520 Views

How many animations can I have on a Pinpoint graphic?

Issue What determines haw many active animations a graphic can have? Environment Cyberstation Pinpoint graphics. Cause Graphic updates will slow down if an excessive number of animations are configured. Resolution 50 Animations on a graphic is a good limit that should give a reasonable update rate on most systems. In the Pinpoint editor you can change the polling rate of each animation from the default 1000mS allowing less important points to be polled less, thus allowing the important points to be polled more. In Edit mode; go to Configuration, Object List to see the polling rates listed, each animation allows you to change its polling rate. It is generally better to have more graphics with fewer animations for faster updates. The rate at which you can poll for updates will also depend on your system layout, a system with many animations being polled from large slow MS/TP of Infinet field bus network will update much slower than a system with NetcontrollerII and IO modules with all points connected at the Ethernet level. No Pinpoint animations poll from the SQL database, all data is polled directly from the controller that holds the Animated object. When a graphic is opened the Workstation goes to the SQL Server to get the background file and the location of all polled objects, it will then directly poll the field controllers with no further need to connect to the SQL database.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1367 Views

Short yoke Forta series actuators applications

Issue Does the short yoke Forta actuators fit on the current portfolio of valves?  Environment MG600C Venta Forta Cause With the new short stroke actuator MG600C soon available, will it work with the regular valves? Resolution The MG600C is designed to be used with the VG210R / VG310R valves that will be released in the near future. 
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Field Devices
810 Views

Viconics VT7000 Series LonTalk Plug-in

Issue LNS Plug-in for Viconics Thermostats Environment LNS NL220 Lonmaker Cause It is necessary to configure the Viconics VT7000 series controllers with an LNS Plug-in Resolution Download the latest Viconics Plug-in Here. Additional Information on the Viconics product offering can be found at http://www.viconics.com/.
View full article
Picard Product_Support
‎2018-09-07 11:09 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
  • TAC Vista
1232 Views

Return to normal (RTN) alarm setting on AI point not functioning as expected

Issue When using Conversion Coefficient slope m = 1.0, the return to normal (RTN) Alarm Limit on an AI point appears to have a built-in offset. Environment I/NET Seven - Analog Inputs (AI), all revisions. Cause There is a built-in hysteresis of 3 counts on the return-to-normal settings for both the low and high limit setting of an analog input (AI) point.  When using a conversion coefficient slope (M) of 1, this provides a 1:1 scale between counts and engineering units which could provide undesired results.  So this built-in hysteresis needs to be considered when using a slope (M) of one or higher on analog input alarm points.    Resolution Consider using a conversion coefficient slope (M) of 0.1.  Alternatively if this is not possible, creating an internal AI point (using a m = 0.1) or a DA and applying a calculation to reflect the points value or alarm state as required as a workaround.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC INET
1831 Views

The error messages "LogService.archive: SQL Exception: Container 1,342,197,790,972 not found." and "Close pooled Connection" is displayed in the Standard ou...

Issue The Enterprise Server’s archives are not updating and the following message is displayed in the Standard Output Window:      ERROR: LogService.archive: SQL Exception: Container 1,342,197,790,972 not found.      ERROR: LogService.archive: Force close of Connection!      WARNING: Closed Pooled connection [ConnectionPool]      ERROR: XSCH1: Container 1,342,197,790,972 not found.   Environment Niagara R2 Enterprise Server – all versions Cause The “SQL Exception” error and “Closed pooled connection” warning appears to indicate a corruption within the Cloudscape SQL database. Resolution In this instance, the app folder became corrupt when copied between builds during an upgrade.  The original app folder was simply recopied. The second copy of the app folder copied without errors.   The following would apply in instances were the original app folder is corrupt:  First, try and recover the Cloudscape database and repair the corruption using the console and the dbadmin command.  After stopping the station, open the console and run the command at the prompt:            dbadmin >  recover  The software will search through the Cloudscape SQL database and attempt to clear the errors and recover the database.  If this is unsuccessful, you may have to remove the APP folder from the station and start over.    To remove the Enterprise Server’s app folder: Stop the server’s database and delete its app folder.  A new app folder will be created when the server is restarted.    Note: All archived information will be lost when the app folder is deleted.          
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
1170 Views

Manual Service Pin location on Schneider Electric SE7600, SE7300 and SE7200 series devices (Viconics VT7600, VT7300 and VT7200)

Issue Cannot find manual service pin location Environment Schneider Electric SE76xx, SE73xx and SE72xx Viconics VT76xx, VT73xx, VT72xx Ready7 Commissioning Neuron ID Lonworks ID Service Pin message Cause The Service PIN is used to identify the device at commissioning. There is not a visible service pin button located on the Viconics device. Resolution A Service Pin will transmit the program ID and the Neuron ID (LonWorks Unique ID) contained in the device to the commissioning or service tool. The Status LED will blink when the device accepts the Service PIN command. VT7600 device - Press simultaneously the “Yes” button and the “No” button located on the keypad interface VT7300 and 7200 device - Pressing simultaneously the “Up” button and the “Down” button located on the keypad interface.       Additional Information on Viconics VT7600 series can me found in this Viconics Lon Integration Manual. Additional Information on Viconics VT7300 and VT7200 series can me found in this Viconics Lon Integration Manual.
View full article
Picard Product_Support
‎2018-09-11 02:46 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • TAC Vista
3826 Views

Is there a replacement RJ-11 to BACnet MSTP cable for I/A Series Roam IA?

Issue Is there a replacement RJ-11 to BACnet MSTP cable for I/A Series Roam IA? Environment Roam IA, MNB-ROAM-IA Cause Need to replace cable. Resolution The part number for the replacement RJ-11 to BACnet MSTP cable for Roam IA is MNB-ROAM-CBL.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
902 Views

In what positions can Continuum controllers be mounted?

Issue In what positions can Continuum controllers be mounted? Environment Continuum Product Line Cause Not sure if the controllers can be mounted on both the vertical and horizontal plane. Resolution There may be some specific mounting instructions for some of the controllers, but for the most part they can be mounted in any direction in the vertical plane. Controllers with relays should not be mounted with the edge the outputs are on facing down. Consult the installation instructions (found here) for each controller for any specific mounting requirements.
View full article
Picard Product_Support
‎2018-09-11 08:33 AM

Labels:
  • Andover Continuum
931 Views

Gasket availability in connection kits for valve V241 / V341

Issue Can the gaskets included in the connection kits be ordered / purchased separately? Environment V241 V241 Venta Connection kit gasket Cause Gasket replacement requested if lost or worn out. Resolution Unfortunately the gasket part of the connection kit is not available separately and this can only be ordered as a complete kit.  
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • Field Devices
865 Views

I/A Series R2 station fails to send BACnet alarm to a third-party system. The error indicates tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS.

Issue I/A Series R2 station fails to send BACnet alarm to a third-party system.  The error indicates tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS. Environment I/A Series R2, BACnet Cause A notification class and BACnet recipient have been configured with a BACnet device instance however an error is generated for each alarm attempt.  The error log indicates that there is an unresolved device address. tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS   at tridiumx.bacnet.services.BACnetTransport.sendConfirmedRequestSimple (bytecode 21)   at tridiumx.bacnet.notification.BACnetNotification.sendRequest (bytecode 9)   at tridiumx.bacnet.notification.AsyncEventNotificationRequest.execute (bytecode 15)   at tridium.services.helpers.AsynchronousRequestHelper.processMsg (bytecode 4)   at tridium.services.helpers.MessageQueueHelper.run (bytecode 23)   at java.lang.Thread.run (line 5) Resolution For the alarm to work, the station must contain the associated BACnet device object for the target device.  This provides the information required to properly route the alarm (e.g. IP address, device instance, etc.).  In addition, the target device must be online and able to receive and process BACnet alarms.  Use the BACnet service BACnetUtility and learnNetwork command to create the BACnet device objects for the target devices. Additional details can be found in the I/A Series R2 BACnet Integration Reference Guide (Configuring for BACnet Alarm Generation) included with the R2 documentation.  These requirements and restrictions apply to Niagara BACnet alarm generation: Only Niagara objects that are exposed as BACnet objects can generate BACnet alarms. This means only alarms from Niagara AIs, AOs, BIs, BOs, MSIs, and MSOs can be routed to BACnet devices (Calendar and Schedule objects are not alarmable). This draws from the BACnet requirement that every alarm message must contain the BACnet object ID of its source. Only local objects in a station can generate BACnet alarms. Therefore, a Enterprise Server station cannot generate a BACnet alarm on behalf of an object in a subordinate station. If a subordinate station needs to generate a BACnet alarm, it must be configured with the BACnet service and the appropriate recipient(s). A separate BACnetRecipient must be created for each remote device to which BACnet alarms must be routed (one-to-one BACnetRecipient to device). Alarms are not regenerated. If a BACnet device is down when the Niagara system sends an alarm, the alarm is not saved for retransmission later. The Niagara system, of course, still maintains a record of the alarm in its buffer. The Niagara system does not support setting up a third-party BACnet system to receive BACnet alarms, configure its notification classes, and so forth. All alarm configuration and setup must be done using the system’s native tools.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
1322 Views

Controller serial numbers are now being shipped greater than 4,194,303 range (800xxx or 900xxx). Does this cause a problem with the devices BACnet Device Id setting and it's ab...

Issue Previously the BACnet Device Id of the controller would default to the devices serial number, this is no longer possible due to the maximum BACnet Device Id being 4,194,303. Serial numbers greater than 800xxx can give an error 'Device Node id is out of range' (1 to 4,194,303) Environment Continuum BACnet Controllers Cause Concern about what the default BACnet Id will be set to a value higher than what is supported or to a value that has already been set to a previous controller. Will this conflict with existing controllers on a site when adding new controllers when all are using the default BACnet Device Id? Resolution There is an internal calculation done that uses the Serial number as a seed to then calculate the BACnet Device Id so that it falls within the 4,194,303 max. This calculated value will be unique to every other Continuum BACnet Devices default BACnet Device Id so you should be fine when newer controllers are being added to existing sites. If you want to ensure there are no address conflicts though you may want to set the value yourself when commissioning the controllers through creating the Device object manually and setting the BACnet Device Id at that time or if the device is already configured delete it from the BACnet side and then edit it from the Infinity side and enter a new and unique device id, then perform a find BACnet devices to bring the device back on the BACnet side with its new device id.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • Andover Continuum
1784 Views
  • « Previous
    • 1
    • …
    • 471
    • 472
    • 473
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of