Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

I/A Series R2 station fails to send BACnet alarm to a third-party system. The error indicates tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 station fails to send BACnet alarm to a third-party system. The error indicates tridiumx.bacnet.BACnetException...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1291 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 station fails to send BACnet alarm to a third-party system. The error indicates tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS.

Picard Product_Support
‎2018-09-06 10:09 AM

Issue

I/A Series R2 station fails to send BACnet alarm to a third-party system.  The error indicates tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS.

Environment

I/A Series R2, BACnet

Cause

A notification class and BACnet recipient have been configured with a BACnet device instance however an error is generated for each alarm attempt.  The error log indicates that there is an unresolved device address.

tridiumx.bacnet.BACnetException E_BACNET_UNRESOLVED_DEVICE_ADDRESS
  at tridiumx.bacnet.services.BACnetTransport.sendConfirmedRequestSimple (bytecode 21)
  at tridiumx.bacnet.notification.BACnetNotification.sendRequest (bytecode 9)
  at tridiumx.bacnet.notification.AsyncEventNotificationRequest.execute (bytecode 15)
  at tridium.services.helpers.AsynchronousRequestHelper.processMsg (bytecode 4)
  at tridium.services.helpers.MessageQueueHelper.run (bytecode 23)
  at java.lang.Thread.run (line 5)

Resolution

For the alarm to work, the station must contain the associated BACnet device object for the target device.  This provides the information required to properly route the alarm (e.g. IP address, device instance, etc.).  In addition, the target device must be online and able to receive and process BACnet alarms.  Use the BACnet service BACnetUtility and learnNetwork command to create the BACnet device objects for the target devices.

Additional details can be found in the I/A Series R2 BACnet Integration Reference Guide (Configuring for BACnet Alarm Generation) included with the R2 documentation.  These requirements and restrictions apply to Niagara BACnet alarm generation:

  • Only Niagara objects that are exposed as BACnet objects can generate BACnet alarms. This means only alarms from Niagara AIs, AOs, BIs, BOs, MSIs, and MSOs can be routed to BACnet devices (Calendar and Schedule objects are not alarmable). This draws from the BACnet requirement that every alarm message must contain the BACnet object ID of its source.
  • Only local objects in a station can generate BACnet alarms. Therefore, a Enterprise Server station cannot generate a BACnet alarm on behalf of an object in a subordinate station. If a subordinate station needs to generate a BACnet alarm, it must be configured with the BACnet service and the appropriate recipient(s).
  • A separate BACnetRecipient must be created for each remote device to which BACnet alarms must be routed (one-to-one BACnetRecipient to device).
  • Alarms are not regenerated. If a BACnet device is down when the Niagara system sends an alarm, the alarm is not saved for retransmission later. The Niagara system, of course, still maintains a record of the alarm in its buffer.
  • The Niagara system does not support setting up a third-party BACnet system to receive BACnet alarms, configure its notification classes, and so forth. All alarm configuration and setup must be done using the system’s native tools.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 14068
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of