Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/A Series R2 BACnet Alarm Fails with E_BACNET_UNRESOLVED_DEVICE_ADDRESS

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 BACnet Alarm Fails with E_BACNET_UNRESOLVED_DEVICE_ADDRESS
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1474 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 BACnet Alarm Fails with E_BACNET_UNRESOLVED_DEVICE_ADDRESS

Picard Product_Support
‎2018-09-06 10:09 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:17 PM

Issue

An I/A Series R2 station fails to send BACnet alarms to a third-party system. The error log shows:
tridiumx.bacnet.BACnetException: E_BACNET_UNRESOLVED_DEVICE_ADDRESS.

Product Line

TAC IA Series

Environment

  • I/A Series R2
  • BACnet

Cause

The station does not contain a BACnet device object for the target device. Without this object, the system cannot resolve the device address required for alarm routing.

Resolution

  1. Ensure the station includes the BACnet device object for the target device. This object provides essential details such as IP address and device instance.
  2. Verify the target device is online and capable of receiving BACnet alarms.
  3. Use BACnetUtility and the learnNetwork command to create BACnet device objects for all target devices.
  4. Refer to the I/A Series R2 BACnet Integration Reference Guide (section: Configuring for BACnet Alarm Generation) for detailed steps.

Additional Notes:

  • Only Niagara objects exposed as BACnet objects (AIs, AOs, BIs, BOs, MSIs, MSOs) can generate BACnet alarms.
  • Alarms are not regenerated if the BACnet device is offline during transmission.
  • Enterprise Server cannot generate alarms for subordinate stations; each station must be configured individually.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 14068
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore