Continuously repeated errors in Standard Output Window of R2 (Niagara) station, "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)"...
  • Continuously repeated errors in Standard Output Window of R2 (Niagara) station, "Set timer for tag: (an integer) :400" and "C...
  • SESA113595
    SESA113595
‎2018-09-11 02:24 PM
Continuously repeated errors in Standard Output Window of R2 (Niagara) station,  "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)" . The integer increments by one about every second until it reaches 128, then reverses the count, counting down by one into negative numbers.
I/A Series R2 UNC with the GCM driver
Network 8000 GCM
The cause of the problem was resolved with the gcm-2.304.530b.v1.jar.
This is considered a nuisance error, and was corrected in the gcm-2.304.530b.v1.jar.
  • TAC IA Series
  • 14013