Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 458
    • 459
    • 460
    • …
    • 509
  • Next »

Access Events associates with one controller are not being delivered.

Issue Five of the controllers are reporting access events while the sixth is not. Environment Access Evens Subnet Controller configuration Cause The subnet scheme on the network had significant subnetting errors. Resolution Resolve IP address and default router scheme.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Andover Continuum
951 Views

Cannot Learn in New Cameras to an Existing VideoServer Object.

Issue Edit VideoServer object and Learn button is greyed out. Environment CyberStation 1.94 Video Cause The Learn key in the CyberStation Security editor under VideoServer had been changed to a 'lock'. Resolution The Learn key in the CyberStation Security editor under VideoServer had to be changed to a 'key' for user Group 128. Note: there is an unconfirmed possibility that this occurred as a result of an upgrade, as the Admin user was using Group 128 and typically a change to user security during an upgrade would default to a 'key' for Group 1 but a 'lock' for all other security groups.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Andover Continuum
1208 Views

StruxureWare for Building Operation User Interface Matrix

Issue StruxureWare for Building Operation User Interface Matrix Environment SmartStruxure Cause Need information about which User Interface Option has which features Resolution You can download the User Interface Matrix from The Exchange Download Center: User Interface Summary
View full article
Picard Product_Support
‎2018-09-11 04:18 AM

Labels:
  • EcoStruxure Building Operation
1553 Views

Replacement for TAC258R

Issue Obsolete product needs replacement. Environment TAC258R 2581010000 Xenta 102-AX STR100 Xenta 121-FC STR250 Cause The TAC258R is obsolete and needs to be replaced. Resolution   We do not offer any direct replacement. Depending on application, you might consider using the Xenta 121FC with a STR100 series room unit. However, if the application is VAV, the Xenta 102-AX and a STR250 wall module might cover your needs.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Field Devices
  • TAC Vista
992 Views

Can a UNC-600 or UNC-610 be replaced with a UNC-410?

Issue Can a UNC-600 or UNC-610 be replaced with a UNC-410?  The installed UNC is in disrepair and it only does a LON integration of approximately 25 controllers. Environment Niagara R2 Cause UNC onsite no longer working as well as being obsolete and un-repairable Resolution As long as the station being transferred from the UNC-6x0 is not large, then the UNC-410 will perform well as a replacement unit. The UNC-410 only has 300,000 resources and is limited to 27 LON controllers. If more LON controllers must be integrated, then a special request to open the license to a higher node count must be submitted to the Marketing Manager and approved by him.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • TAC IA Series
1101 Views

Additional details on I/NET Automatic Backup

Issue Used the script to make an automatic backup and after the first one, it doubled on the next one. Is this what is expected from the backup? Product Line TAC INET Environment All versions of I/Net Cause What does an automatic backup really do to a database? Resolution The Automatic backup is a script that will backup the database whenever it is executed. It creates a generic database the first time but does not append it. Each time after that a backup is created and time stamped that it was executed. If it changed in size, then it would have been due to events occurring during the time that has elapsed.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • TAC INET
1046 Views

How to set a property on multiple objects in one operation.

Issue Assign a category to a large number of alarm objects without having to edit the alarm objects one at a time. Environment Automation Server Enterprise Server WorkStation Cause Categories can be used for several different reasons in a Workstation. After the alarms are created, it can be time consuming to go one by one to set a single property on a large number of alarms. The ability to edit many at once will save time. Resolution Create a Search object and set the filter to display the objects in question then select all the objects you want the set applied to. Choose the properties check box at the top of the list so that the properties window appears on the right hand side of the screen. You should see that all properties. When objects of different classes are in the Search, the properties that are common among the selected objects are editable. Go to the category field and browse to the desired category and select the category. Choose save or OK
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • EcoStruxure Building Operation
1401 Views

The SQL Server System Configuration Checker cannot be executed due to WMI configuration on the machine "machinename" error:2147942405(0x80070005).

Issue Unable to install the SQL Server with I/NET. Error shows: The SQL Server System Configuration Checker cannot be executed due to WMI configuration on the machine "machinename" error:2147942405(0x80070005). Environment I/NET Seven Cause Some security settings have been changed under DCOM. If local launch and local activation properties are set to 'Not Defined,' the installation will fail. Resolution Open Administrative Tools > Local Security Policies Find Local Policies > Security Options > 'DCOM: Machine Launch Restriction in Security Descriptor Definition Language(SDDL)' Set the System user 'Local Launch' and 'Local Activation' to ALLOW.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • TAC INET
1387 Views

Get "Untranslated error" when adding a point under a B3 controller.

Issue Get error message "Untranslated error" when adding a point under a B3 controller. Environment StruxureWare Building Operation version 1.3 Automation Server version 1.3 Cause A new B3 controller was added to the AS via "Learn" Resolution Manually add the B3 controller to the AS.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • EcoStruxure Building Operation
1178 Views

Documentation for Erie thermostat T312-121

Issue Unable to locate requested documentation. Environment   T312-121 Cause Product was available in price list, but no related documentation was to be found. Resolution Unfortunately this product is terminated, and was still listed in the price list. No documentation has ever been available for download. Product is now removed from future revisions of price list.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Field Devices
1055 Views

Menta module names disappear when importing a Menta file.

Issue Menta module names disappear when exporting a Xenta from Vista version 5.1.8 and importing it to Vista version 5.1.7  Environment TAC Vista 5.1.7 and 5.1.8 Cause Changes is made in the export/import function in TAC Vista 5.1.8 which will cause problems to import a export file from TAC Vista 5.1.8  in to TAC Vista 5.1.7. Resolution To be sure that the export/import function should work only export and import between Vista systems of the same version. 
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • TAC Vista
1377 Views

Replacement for Differential Air Pressure Switches SPD900

Issue Since the SPD900 is obsolete, it needs a replacement product. Environment Differential Air Pressure Switches 004701040  SPD900-600Pa  004701020  SPD900-200Pa 004701090  SPD910-2000Pa  004701080  SPD910-1000Pa  004701070  SPD910-500Pa  004701060  SPD910-300Pa  Cause Obsolete part needs replacement. Resolution The SPD900 series was replaced by SPD910 series in 2009. Please see SPD910 data sheet for more information and details.
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Field Devices
1290 Views

Enable / Disable Personnel Manager

Issue How to enable / disable Personnel Manager in Continuum Environment Continuum Cyberstation version 1.93 and later Cause The Personnel Manager is enabled by default at each Cyberstation workstation version 1.93 and later. However, users can choose to enable the Personnel Editor, a dialog similar to other Cyberstation dialogs (used in earlier versions of Cyberstation), instead of the Personnel Manager. Resolution To enable / disable the Personnel Manager: 1. In Continuum Explorer, right click your workstation folder, and click Open   2. Select the Preferences tab of the Device editor   3. Scroll down to the preference setting, Use Personnel Manager, and select True to enable or False to use the old Personnel Editor   4. Click OK
View full article
Picard Product_Support
‎2018-09-06 10:34 AM

Labels:
  • Andover Continuum
1415 Views

Changing the panel layout

Issue The initialization of a panel does not adjust the size of objects in the panel. Once a panel is created, how to re-adjust each object's size in it? Environment SmartStruxure version 1.3 Cause When creating a panel in the WorkStation, the system does not have a step asking to adjust the size of each object (graphic, trend chat, etc.) in this panel. Users need to do additional setting in the WorkStation in order to change the layout. Resolution Create a panel according to the customer's demand. Right click on the panel just created, and select edit panel. In the right side panel, adjust the panel layout. Once the change is finished, click on the Save button on the top of the tab. Reopening the panel will find the panel now is planned as desired.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • EcoStruxure Building Operation
1272 Views

Loytec NIC_USB100 interface does not work with a new HP laptop

Issue Some engineers are being issued with new HP Probook 6570b laptops, running Windows 7.  The Loytec NIC_USB100 network interface does not work with these machines, even when the latest Loytec drivers (version 4.1.4) are installed.  Environment Lonworks Windows 7 Cause Plug'n'Play does not recognise the NIC_USB100 when it is plugged in and fails to install the drivers. Resolution As a workaround, install a virtual machine running Windows XP on the HP Probook 6570b.  Install the Loytec software on the virtual machine.  The NIC_USB100 is then recognised and the drivers install correctly.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • TAC Vista
932 Views

Cannot get changed I/NET point or controller name to update in StruxureWare Building Operation

Issue Cannot get changed I/NET point or controller name to update in StruxureWare Building Operation Environment SmartStruxure I/NET integration Cause There is a designed feature for integrated I/NET objects within Building Operation.  Once an object is imported into SmartStruxure, it can be re-named and given description with more options than on the I/NET controller.  For this reason, when changing a point or controller name through the I/NET interface, it will not be updated in SmartStruxure.  All name changes should be done through the Building Operation Workstation interface. Resolution If you wish the StruxureWare Building Operation names to match the changed I/NET name, you have 2 options. Change the name manually in Building Operation Delete the point and re-upload the controller, or delete the controller and re-discover it NOTE: Do not change point names in SmartStruxure until after all converted graphics have been imported.  The import process requires the SmartStruxure name and I/NET name to match.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1075 Views

Cannot Access Database error when attempting to initialize CyberStation.

Issue When attempting to initialize Cyberstation on a workstation PC, Database Initialization says that it cannot access the database. Environment SQL Continuum CyberStation Continuum Database Initialization Cause An incorrect path and name was used in the Server Name field. Resolution Open the database up in SQL Server Management Studio. Right click on the top of the explorer tree and select Properties. The SQL server path and name will appear in the Property Window title bar.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • Andover Continuum
1040 Views

Can the AS be positioned in the middle of the mstp bus?

Issue Typically the master controller is at the end of the bus, but is it possible to place it in the middle? Environment AS b3 Cause Depending on the buildings wiring there could be a need to place the AS in the middle of the bus. Resolution The AS can be placed in the middle of the bus, but the terminating resistors must then be placed at both ends of the bus. This method wasn't officially tested in this manner by SQA, but it works similar to how a BCX 4040 does which can be placed in the middle of the bus in this fashion.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • EcoStruxure Building Operation
880 Views

SPP110 Pressure transmitter for wet media

Issue In which medias can a SPP110 be mounted? Environment SPP110: 004702020 004702040 004702060 004702080 004702100 004702120 004702140 Cause Depending on media, some sensors may not be suitable. Resolution SPP110 can be used with any media suitable with stainless steel.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • Field Devices
1222 Views

Unable to assign a foreign address to the I/A Series R2 Configurable Analog Input object to expose for BACnet use.

Issue Unable to assign a foreign address to the I/A Series R2 Configurable Analog Input object to expose for BACnet use. Environment I/A Series R2, Analog Input, Configurable Analog Input Cause The native I/A Series R2 Analog Input object is designed to not pass an NaN from input to output. The output will hold the last valid value when the input is NaN.  The Configurable Analog Input object, available from the programLib, can be configured to pass the NaN. Attempting to assign a foreign address to the I/A Series R2 Configurable Analog Input object to expose for BACnet use generates the following warning example. WARNING: Unable to export object: no BACnet equivalent object type for SpaceTemp [/B12B4_5/services/BACnetService] Resolution Only native I/A Series R2 objects (AI, AO, BI, BO, MSI, MSO calendar and schedule) can be exposed as Bacnet points using the foreign address inside the properties of the Niagara object.  Even though the ConfigurableAnalogInput is derived from the base AnalogInput class, the associated BACnet module is not designed to process as native object. The only workaround is to replace the ConfigurableAnalogInput object with a native AnalogInput object and adjust the application accordingly.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • TAC IA Series
1212 Views
  • « Previous
    • 1
    • …
    • 458
    • 459
    • 460
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of