Can a UNC-600 or UNC-610 be replaced with a UNC-410?
  • Can a UNC-600 or UNC-610 be replaced with a UNC-410?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:34 AM
Can a UNC-600 or UNC-610 be replaced with a UNC-410?  The installed UNC is in disrepair and it only does a LON integration of approximately 25 controllers.
Niagara R2
UNC onsite no longer working as well as being obsolete and un-repairable
As long as the station being transferred from the UNC-6x0 is not large, then the UNC-410 will perform well as a replacement unit.
The UNC-410 only has 300,000 resources and is limited to 27 LON controllers.
If more LON controllers must be integrated, then a special request to open the license to a higher node count must be submitted to the Marketing Manager and approved by him.
  • TAC IA Series
  • 12774