Replacement for TAC258R
  • Replacement for TAC258R
  • SESA150559
    SESA150559
‎2018-09-06 10:34 AM
Obsolete product needs replacement.
TAC258R 2581010000
Xenta 102-AX
STR100
Xenta 121-FC
STR250
The TAC258R is obsolete and needs to be replaced.
We do not offer any direct replacement. Depending on application, you might consider using the Xenta 121FC with a STR100 series room unit. However, if the application is VAV, the Xenta 102-AX and a STR250 wall module might cover your needs.
Labels (2)
  • Field Devices
  • 12764