Enable / Disable Personnel Manager
  • Enable / Disable Personnel Manager
  • sesa116871
    sesa116871
‎2018-09-06 10:34 AM
How to enable / disable Personnel Manager in Continuum
Continuum Cyberstation version 1.93 and later
The Personnel Manager is enabled by default at each Cyberstation workstation version 1.93 and later. However, users can choose to enable the Personnel Editor, a dialog similar to other Cyberstation dialogs (used in earlier versions of Cyberstation), instead of the Personnel Manager.
To enable / disable the Personnel Manager:
1. In Continuum Explorer, right click your workstation folder, and click Open
2. Select the Preferences tab of the Device editor
3. Scroll down to the preference setting, Use Personnel Manager, and select True to enable or False to use the old Personnel Editor
4. Click OK