Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 471
    • 472
    • 473
    • …
    • 509
  • Next »

BCX1 goes offline when reloading the controller

Issue There are many BCX1 on the site. All of the BCX1s go offline when reloading the controller. Environment BCX1-CR B3 Continuum Cause Checking the system configuration and programming. The reasons listed below may cause significant traffic on the network. A lot of Polling value of points across controllers COV increment is set to zero Check all the numeric points' setpoint attribute including Runtime, DamperPosition, etc. as these change all the time. Points under b3 controllers are referenced by more than 32 devices. Device in the BACnet Device folder doesn't match the controller in infinity side.(Not deleted device from BACnet folder after replace the controller) When the special trunk with low quality cable  connect to BLink also cause this issue. Remove the problem trunk, the issue will be  gone When the heavy traffic happens on the network or some other issues , it will cause unexpected issues. Resolution Change the programs way, create a program in the BCX1 to mirror the referenced points in b3s Uncheck the setpoint attribute of all numerics except  temperature setpoint. Change the polling program flow type from looping to fall thru and trigger every minute or trigger by other digital point. Set the COV increments to a non-zero value After device replacement, delete the device from BACnet Device folder and find new BACnet device again, then send to database Remove the problem trunk from Blink or try to change the terminal resistor will  resolve this issue  After the steps above are done, the network should be stable and the BCX1 will no longer go offline when reloading.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • Andover Continuum
1677 Views

Continuum may not start if McAfee Intrusion Detection is installed

Issue Continuum Workstation initialization resolved but will not start normally. Only a few executables start Environment Continuum Windows 7 McAfee Enterprise and Intrusion Detection Cause McAfee Intrusion Detection was installed and updated and after that Continuum would no longer start Resolution Removed McAfee Intrusion Detection, rebooted and then Continuum started normally
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • Andover Continuum
1432 Views

Software Licensing for Continuum 2.0 and StruxureWare Solution

Issue Software Licensing for Continuum 2.0 & StruxureWare Solution Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum Site integration with the StruxureWare Solution Continuum Cyberstation software & Licensing Cause Request for Software Licensing compared to the Hardware key.  Resolution There is a Ordering and Activation document available on the Buildings Exchange Download Center. A link is provided below: Ordering and Activation of Software License for Continuum v2.0 Software license is a dedicated license per workstation and locked to both the hardware and the operating system. Recommended not to install on old hardware. Software licensing is available for both new and existing installations after Continuum 2.0.  A Hardware key is required in order purchase a software license.  This is because the Continuum features and options are purchased with the physical Hardware key, not with the keyless license.   When purchasing the Keyless license, the serial number of the Hardware key is submitted along with a License Information file (c2v) that has been created on the workstation that is to be licensed.  The License Information file is created using the Hasp Key Utility.   Continuum installations pre version 2.0 (e.g. v1.94) who wish to upgrade to v2.0 and would like to benefit from Software Licensing feature must download and install the required files. Those are outlined in the document above. Note: For Continuum Interface for SmartStruxure Solution the demo StruxureWare Building Operation license has all required features. Your Continuum 2.0 key must have the Advanced Webserver feature enabled.You can use the Continuum Interface Server for any Continuum installation: Standalone or Multi-User (LAN). All existing Andover Continuum configurations are supported in the Continuum Interface Server.  
View full article
Picard Product_Support
‎2018-09-11 04:38 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
3898 Views

The suggested Belkin Bluetooth adapter is obsolete. Is there a suggested replacement for use with RoamIA?

Issue The suggested Belkin Bluetooth adapter is obsolete.  Is there a suggested replacement for use with RoamIA? Environment Roam IA BACnet MSTP communications Cause The suggested Belkin adapter is no longer available. Resolution Two alternates have been found to function well with the RoamIA; they are the AZIO BTD-V400 and SMK VP-6495.  Both of these devices are very compact and use Bluetooth v4.0 technology.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • TAC IA Series
1166 Views

How long will it take for a MNB controller to drop to 'Read-Only' mode when the AC power supply voltage drops below 20.4 Vac?

Issue How long will it take for a MNB controller to drop to 'Read-Only' mode when the AC power supply voltage drops below 20.4 Vac? Environment MNB controllers Cause Site installation using one AC transformer for multiple controllers.  Site is also suffering brownout conditions. Resolution Factory testing confirms that it takes only one AC cycle of power (i.e. one complete sine wave) of voltage below 20.4 Vac for the controller to drop into 'Read-Only' mode. It is difficult to view with a standard digital multimeter.  A scope may be required to capture the voltage dip.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • TAC IA Series
973 Views

Xenta group master is offline but other controllers in the group are online

Issue The Xenta Group Master is offline in Vista Workstation but  the rest of that masters group is online. Environment Workstation TAC Vista System Plug-In Cause The issue occurs most of the time when dealing with a system that is using a Loytec NIC 852 card. Somehow the address table entry for tag_0 can become corrupted, lost, or not updated.  Resolution Open up the TAC Vista System Plug-In through LonMaker or NL220. Click on the LNS Network menu > Create Group Bindings. Now go to the TAC Network menu and click on Commence Communication. Once the Commence Communication operation is complete, click Close. Update Vista Database. Refresh the system tree in Vista Workstation.
View full article
Picard Product_Support
‎2018-09-11 04:38 AM

Labels:
  • TAC Vista
1569 Views

Unable to communicate with controller after correctly configuring and enabling Network Security.

Issue Controller comm is lost after enabling Network Security after properly configuring the Controller and Workstation. Environment Network Security NCII CX9680 ACX5740 ACX5780 Cause Network security activation was being inhibited by the domain user security policies. Resolution In this case both the controllers and Windows network security policies had been configured properly for Continuum.  This fact was confirmed when the IT department got involved.  Once they relaxed some of the security policies on this machine Continuum network security began to work as expected, both from the controller and Cyberstation point of view. The customers IT personnel did not share with us what policies were responsible for the activation issues.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1075 Views

Unable to reload or upgrade firmware on a controller.

Issue Controller drops offline when reloaded or when an attempt to flash firmware is made. Environment Infinet MSTP Cause Massive CRC errors on the MSTP bus due to a bad controller on one leg of blink. Resolution In this case the problem was due to a bad controller on the bus.  The offending controller was located by segmenting the bus to determine which legs were introducing this problem. Once it was determined which controller was causing this issue, the controller was removed and a replacement installed.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1171 Views

What is required to upgrade a UNC 196 outstation to a Sigma x96 controller?

Issue Upgrading a UNC 196 outstation. Environment UNC 196 296 Upgrade Cause Customer wishes to upgrade his BAS outstation to a Sigma controller. Resolution To upgrade the outstation the following cards will need to be replaced. Comms/CPU Card Power Supply Card. These can be purchased together as an S-x96-UPKIT If the outstation also contains a Maximum Demand card, this is replaced by a Digital Input card (S-UNC-DI).
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Satchwell BAS & Sigma
1705 Views

Importing a Xenta 121-FC controller into StruxureWare Building Operation.

Issue Importing a Xenta 121-FC controller into StruxureWare Building Operation. Environment Xenta 121FC Cause How do you setup the Xenta 121-FC using StruxureWare Building Operation only, as all the config needs setting for 1 Return Temp. Cooling Only (AO type). Fan On/Off   Resolution The original process would require the use of LonMaker and ZBuilder to configure the Xenta 121-FC controller onto the LON network, before adding it to the StruxureWare Building Operation LON interface. Version 1.4 introduces LNS device plug-in support to configure LonWorks® devices. StruxureWare Building Operation v1.4 supports third party software: OpenLNS. OpenLNS is only required on WorkStation machines used for configuration of LON® devices (e.g. WorkStation Pro machines). Automation Server and Enterprise Server databases are updated with any changes created with the plug-in. With LNS device plug-in support, now ZBuilder can be used with SmartStruxure solution. Plus, all Xenta controllers are supported, including the X100 series – e.g. Xenta 121.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • EcoStruxure Building Operation
1396 Views

Infinity controller goes offline every five to ten minutes.

Issue BCX9680 controller goes offline every five to ten minutes then returns online. Environment Infinity Controller BCX NC CX Cause Duplicate IP address on the network. Resolution Give the controller a unique IP address.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1395 Views

Webreport 1.4 - The Web Server threw an exception

Issue The Web Server threw an exception. Please make sure the StruxurewareReportingAgent service is running and is set to run "Automatic" An error occurred on the Web Server while processing your request. If the problem persists, please contact your system administrator. Environment Webreport 1.4 upgrade Cause A WebReports installer must use an admin-level SQL Server Management Studio user account to log on to a computer running WebReports. This installer account also requires the addition of three database permissions that permit access to and control of the WebReports database during installs or upgrades. For example, an administrator can detach the database. In SQL Server Management Studio, verify that the Login Properties for the NTAuthority\IUSR and designated WebReports installer user accounts include the db_datareader, db_datawriter, and db_owner database role memberships. Resolution Use SQL management SQL studio and log in to the SQL. Use properties on the user NTAuthority\IUSR and make sure the following are included db_datareader, db_datawriter, and db_owner database role memberships.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • EcoStruxure Building Operation
1462 Views

Do the Jace-6 or Jace-7 need multiple Modbus drivers if more than one port is used?

Issue The jobsite will eventually have 4 RS-485 trunks each communicating Modbus.  Two option cards have been ordered with the Jace (part# TRD-NPB-2X-485). Does each port on the option cards need a separate Modbus driver purchased for each? Environment Niagara G3 Cause Ordering/licensing clarification Resolution Purchasing one Modbus driver (part# ENC-DRV-MOD) will cover all ports used for Modbus on the Jace-6/7.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • TAC IA Series
1228 Views

Continuously repeated errors in Standard Output Window of R2 (Niagara) station, "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)"...

Issue Continuously repeated errors in Standard Output Window of R2 (Niagara) station,  "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)" . The integer increments by one about every second until it reaches 128, then reverses the count, counting down by one into negative numbers. Environment I/A Series R2 UNC with the GCM driver Network 8000 GCM Cause The cause of the problem was resolved with the gcm-2.304.530b.v1.jar. Resolution This is considered a nuisance error, and was corrected in the gcm-2.304.530b.v1.jar.
View full article
Picard Product_Support
‎2018-09-11 02:24 PM

Labels:
  • TAC IA Series
1294 Views

How does Cyberstation interface with MS Outlook to deliver email reports and alarms.

Issue The customer is requesting a documentation on how the Alarm notification from Continuum works with MS Outlook to send out alarm email alerts to their facility engineers.   Environment MAPI MS Outlook CyberStation Email Cause The client is asking for information on how Cyberstation works with MS Outlook. Resolution Continuum uses the Enhanced MAPI messaging architecture to interface with MAPI compliant messaging applications/systems.  To understand this process in better, research Enhanced MAPI.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1522 Views

How many animations can I have on a Pinpoint graphic?

Issue What determines haw many active animations a graphic can have? Environment Cyberstation Pinpoint graphics. Cause Graphic updates will slow down if an excessive number of animations are configured. Resolution 50 Animations on a graphic is a good limit that should give a reasonable update rate on most systems. In the Pinpoint editor you can change the polling rate of each animation from the default 1000mS allowing less important points to be polled less, thus allowing the important points to be polled more. In Edit mode; go to Configuration, Object List to see the polling rates listed, each animation allows you to change its polling rate. It is generally better to have more graphics with fewer animations for faster updates. The rate at which you can poll for updates will also depend on your system layout, a system with many animations being polled from large slow MS/TP of Infinet field bus network will update much slower than a system with NetcontrollerII and IO modules with all points connected at the Ethernet level. No Pinpoint animations poll from the SQL database, all data is polled directly from the controller that holds the Animated object. When a graphic is opened the Workstation goes to the SQL Server to get the background file and the location of all polled objects, it will then directly poll the field controllers with no further need to connect to the SQL database.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Andover Continuum
1367 Views

Short yoke Forta series actuators applications

Issue Does the short yoke Forta actuators fit on the current portfolio of valves?  Environment MG600C Venta Forta Cause With the new short stroke actuator MG600C soon available, will it work with the regular valves? Resolution The MG600C is designed to be used with the VG210R / VG310R valves that will be released in the near future. 
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • Field Devices
810 Views

Viconics VT7000 Series LonTalk Plug-in

Issue LNS Plug-in for Viconics Thermostats Environment LNS NL220 Lonmaker Cause It is necessary to configure the Viconics VT7000 series controllers with an LNS Plug-in Resolution Download the latest Viconics Plug-in Here. Additional Information on the Viconics product offering can be found at http://www.viconics.com/.
View full article
Picard Product_Support
‎2018-09-07 11:09 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
  • TAC Vista
1232 Views

Return to normal (RTN) alarm setting on AI point not functioning as expected

Issue When using Conversion Coefficient slope m = 1.0, the return to normal (RTN) Alarm Limit on an AI point appears to have a built-in offset. Environment I/NET Seven - Analog Inputs (AI), all revisions. Cause There is a built-in hysteresis of 3 counts on the return-to-normal settings for both the low and high limit setting of an analog input (AI) point.  When using a conversion coefficient slope (M) of 1, this provides a 1:1 scale between counts and engineering units which could provide undesired results.  So this built-in hysteresis needs to be considered when using a slope (M) of one or higher on analog input alarm points.    Resolution Consider using a conversion coefficient slope (M) of 0.1.  Alternatively if this is not possible, creating an internal AI point (using a m = 0.1) or a DA and applying a calculation to reflect the points value or alarm state as required as a workaround.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC INET
1838 Views

The error messages "LogService.archive: SQL Exception: Container 1,342,197,790,972 not found." and "Close pooled Connection" is displayed in the Standard ou...

Issue The Enterprise Server’s archives are not updating and the following message is displayed in the Standard Output Window:      ERROR: LogService.archive: SQL Exception: Container 1,342,197,790,972 not found.      ERROR: LogService.archive: Force close of Connection!      WARNING: Closed Pooled connection [ConnectionPool]      ERROR: XSCH1: Container 1,342,197,790,972 not found.   Environment Niagara R2 Enterprise Server – all versions Cause The “SQL Exception” error and “Closed pooled connection” warning appears to indicate a corruption within the Cloudscape SQL database. Resolution In this instance, the app folder became corrupt when copied between builds during an upgrade.  The original app folder was simply recopied. The second copy of the app folder copied without errors.   The following would apply in instances were the original app folder is corrupt:  First, try and recover the Cloudscape database and repair the corruption using the console and the dbadmin command.  After stopping the station, open the console and run the command at the prompt:            dbadmin >  recover  The software will search through the Cloudscape SQL database and attempt to clear the errors and recover the database.  If this is unsuccessful, you may have to remove the APP folder from the station and start over.    To remove the Enterprise Server’s app folder: Stop the server’s database and delete its app folder.  A new app folder will be created when the server is restarted.    Note: All archived information will be lost when the app folder is deleted.          
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
1171 Views
  • « Previous
    • 1
    • …
    • 471
    • 472
    • 473
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of