Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 443
    • 444
    • 445
    • …
    • 501
  • Next »

How long does it take to update the Continuum database.

Issue During the uprev of Continuum, the database initialization utility takes a while to update the database. Environment CyberStation SQL Cause Many factors will determine how long it will take for the database update process to complete. These include but are not limited to: - Size of the database - Server performance - Network performance Resolution The main factor determining the time it will take to update the database if its size. as a guideline a 6 GIG database will take about 30 minutes to update.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
964 Views

Can the MNB-Vx be mounted upside down?

Issue Can the MNB-Vx be mounted upside down? Environment MNB Cause Unusual site installation - VAV boxes mounted upside down for better access to the damper shaft Resolution There is no mounting orientation specified for the MNB-Vx controller.  Ensure that all other mounting instructions are followed for proper operation.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • TAC IA Series
1095 Views

How can thousands of unacknowledged alarms and exceptions be deleted quickly in SIGNAL?

Issue How can thousands of unacknowledged alarms and exceptions be deleted quickly in SIGNAL? Environment SIGNAL (all versions) Cause Months of unacknowledged alarms and exceptions were allowed to accumulate. Resolution The files containing all the alarms and exceptions are located in the SIGNAL\ALARM and SIGNAL\EXCEPT folders respectively. Shutdown SIGNAL (all programs).  In the ALARM folder, delete the alarm_a.dat, alarm_u.dat, and alarm_l.num files. In the EXCEPT folder, delete the excep_a.dat, except_u.dat, and excep_l.num files. Reboot the computer.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • TAC IA Series
894 Views

Some of the dynamic values on a graphic screen in InVue are not updating.

Issue Each time an InVue graphic screen appears, not all of the dynamic values (tags or remote references) update.  No error messages appear. Environment InVue 1.1 WIBS 1.1 Wonderware Cause The InVue computer hardware was replaced.  It has a dual/multi-core CPU which was never validated with InVue. Resolution Disable the settings in the computer's BIOS such that the CPU behaves like it is a single-core.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • TAC IA Series
1281 Views

Will the Vykon Alarm Service run on a Niagara G3 Soft Jace or ENC?

Issue Will the Vykon Alarm Service run on a Niagara G3 Soft Jace or ENC? Environment Niagara G3 Cause Application specific for a jobsite Resolution No.  The Vykon Alarm Service is only supported on an Enterprise Network Server (ENS).
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • TAC IA Series
1365 Views

Replacing EM42 actuator on VTRA valve

Issue EM42 is obsolete and is no longer available when replacement is needed Environment VTRA linkage kit 8600990000 EM9 180° 8601110000 VTRA valve EM42 Cause Replacement of obsolete actuator on old style valve Resolution The replacement actuator for EM42 on a VTRA valve is  EM9 180°, 8601110000, together with linkage kit 8600990000. The linkage kit originally included with the EM9 package should NOT be used.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Field Devices
1609 Views

High Resolution Counter Input Specifications

Issue Need to know if the counter input on a xPDI8 meets the 140 hz specification that is called out in the Project Specification.   Environment xPDI8 xPBD4 Counter input Cause Need to know if the high resolution counter input on a xPDI8 or an xPBD4 Resolution While the xPDI8 counter input is rated for 140 Hz. this spec is based on a 50% duty cycle rate.  In any case, the minimum pulse width we can read on a high resolution counter input is 3.57 ms.  Anything less than 3.57 ms cannot be read reliably by the XPDI8.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1220 Views

Problem with StruxureWare Building Operation Workstation spreadsheet view copy/paste of an Extended Trend Log

Issue Copy/paste does not work for Extended Trend Logs in a Spreadsheet. When attempting to copy/paste an Extended Trend Log, the monitored Trend log is always included in the new Extended Trend Log and it is not possible to change it. Environment Enterprise Server version 1.2 Cause This is a bug which is fixed in version 1.4. Resolution Upgrade to version 1.4 when it is released.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • EcoStruxure Building Operation
1144 Views

Temperature sensor input is not changing.

Issue Temperature sensor input point is not updating. Sensor works fine on another input. Environment i2 controller Cause The threshold may be incorrectly set. For example, if it is set to 10 instead of 0.1. Resolution Check the threshold and make sure it is set to 0.1.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1528 Views

Controlli VMBP2M cross reference to Schneider Electric equivalent

Issue Request for Schneider Electric version of Controlli VMBP2M Environment Controlli VMBP2M Cause Some products of Controlli are also available through Schneider Electric.  Resolution Unfortunately, no cross reference to Controlli VMBP2M is available in the Schneider Electric portfolio.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Field Devices
944 Views

Behavior of IOU modules when communication is lost with the main CPU.

Issue Do IOU modules retain their current state when they lose communication with the host NetController? (NC1, NC2) Environment CX9900 CX9400 CX9680 IOU Modules Cause Documentation Resolution Upon losing communication with the NetController, output modules (DO-4. AO-4 etc) start a 260 *** second timer (4 minutes and 20 seconds), if communication is not restored before the time expires the module turns off the outputs as a safety measure. For Digital outputs the outputs will be turned OFF. (Invert attribute is taken into account). For Analog outputs the output value will be set to zero. *** For access control modules (AC1, AC1A, AC1Plus) the timer is 10 seconds to avoid leaving a door unlocked for an extended period of time.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
983 Views

Product support for EasyLobby Visitor Management.

Issue Contact information for product support for EasyLobby Visitor Management. Environment CyberStation EasyLobby Visitor Management. Cause Documentation Resolution EasyLobby directly supports their software plus the Continuum - EasyLobby integration software. Please forward all EasyLobby support requests directly to them. support@easylobby.com 781-455-8558
View full article
Picard Product_Support
‎2018-09-06 11:28 AM

Labels:
  • Andover Continuum
1550 Views

Handle mismatch issues.

Issue Infinet controller could not see points on its parent controller (CX9680). When the parent controller was reloaded all references to point in the parent controller were broken.  Now none of the child infinet controllers can see points on the parent controller. Environment Infinet NetController BCX Handles LSX280 External references Cause The LSX280, which is the old SX8000 system service tool can be destructive to a Continuum based system. The LSX280 uses a very different process to calculate object handles.  Doing learns with the LSX280 can damage the object handle structure of a Continuum system in ways that may be hard to repair.    Resolution Ran the Import Export Fixup Utility.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1457 Views

SHD, SHO, SHR humidity sensor series specification.

Issue The documentation states in different ways that the sensors are both 0-95% and 0-100% RH range. Environment SHD100 006902321 SHD100-T 006902331 SHD101-T5 006902381 SHD101-T6 6902411 SHO100 006902361 SHO100-T 006902371 SHO101-T5 006902401 SHR100 006902340 SHR100-T 006902350 SHR100-T5 006902390 Cause Different RH (Relative Humidity) values are listed in the documentation, and needs to be explained.  Resolution Ranges are divided into "measuring range" and "working range".   Measuring range: 0…100% r.H. Working range:   10…100% r.H. ( non condensing )   Normally 100% r.H. is already water but it is possible to have 100% r.H. in air- or gas form. Sensor works at 100% r.H. in air but not if pure water is present. This is why “non condensing” is added. In this case working range is 10…100%. If we don’t add “non condensing”,  specification should read: 10…95% r.H.  Sensor will not become damaged because of condensing.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Field Devices
2127 Views

Installed I/A Series G3 Workbench on a new computer with Windows 7 Professional 32-bit and the host ID changes each time Workbench is started.

Issue Installed I/A Series G3 Workbench on a new computer with Windows 7 Professional 32-bit and the host ID changes each time Workbench is started.  This has been seen on new Dell laptops and computers that have been provided a replacement hard drive with Dell operating system (Microsoft OS) installation disks. Environment I/A Series G3 build 3.4.xx, Enterprise Server, Workbench Cause Host IDs continuously change as the software does not have rights to write the encrypted host ID key into the registry. Resolution Locate the Niagara service and Workbench executables (niagarad.exe and wb.exe).  These files are located under the niagara's directory (bin folder).          Example: \niagara\niagara-3.x.xx\bin Right click and select properties for each executable. Select the compatibility tab and check the "Run this program as an administrator" privilege level checkbox.  The host ID is now allowed to be written to the registry by the software.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • TAC IA Series
1186 Views

Modbus RTU Communication is sluggish.

Issue Controller error log reports the following modbus error codes.  0x0000f806 0x0000f808 0x0000f80c   Environment Modbus RTU Stop Bits Cause Incorrect comm port configuration. Resolution Changed the comm port configuration from 1 stop bit to 2 stop bits.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1597 Views

Is it possible to dump objects to text from a PE program?

Issue How to dump object from a PE program Environment CyberStation Cause Documentation Resolution Use the DUMP keyword to dump objects from a PE program running in CyberStation. Example: Dump MyNetwork\MyController\MyObject to "C:\Temp\MyObject.txt" The object will be exported in DUMP format, there is no way to do the same in CSV format.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1158 Views

What is the maximum allowable distance between two Lon devices on a lon network?

Issue What is the maximum allowable distance between two Lon devices on a lon network? Environment TAC Vista 5.1.X  Lon devices such as Xenta 2/3/400 FTT10-A either free or bus topology Cause The physical layout of a building may require nodes to be installed far apart. Resolution The maximum distance between two devices (nodes) is 320m. No node may be more than 320m worth of cable from the bus termination (if bus topology is used). More information can be found in the Lonworks Installation Handbook, chapter 5 "Physical Network Structuring".
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • TAC Vista
2227 Views

How to integrate StruxureWare Building Operation with a hotel booking system.

Issue What is the best way to integrate StruxureWare Building Operation with a hotel booking system?   Environment StruxureWare Building Operation version 1.2 Cause The way to integrate with a third party hotel booking system is in the most cases to use Web services. Web Services are programmable applications accessible from standard Internet protocols. You can use Web Services to consume information, such as temperature from a weather service over the internet. Resolution In most cases the best way to integrate StruxureWare Building Operation with a hotel booking system is to use Web Services. 
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • EcoStruxure Building Operation
1622 Views

Scan time on a Netcontroller is high

Issue Performance of the Netcontroller could be slow because of the scan rate Environment All Netcontrollers Cause Programs and functions that are polling data frequently can drive up the scan time Resolution The scan cycle has the following components to evaluate and process: System variables, download schedules, update inputs, run programs, update outputs, process alarms. Any of these can drive up the scan, but typically there is a program that is requesting polling updates on child controllers (infinet, mstp, modbus) that is driving up the scan. To troubleshoot this, disable all of the programs and enable them one by one to determine which programs are driving up the scan. Once that is determined, focus on adjusting the program accordingly. Performance of the system can be affected by a slow scan time and normally as the scan rate goes up, the performance goes down. An extremely high scan rate would be 50 where the performance is unusable, but could still be working. A scan rate of less than 1 second is ideal, but the real measure of the acceptable rate would be determined by the end user. A scan time of 5 seconds may be acceptable. The scan rate is similar to CPU utilization on a PC, so that high utilization over long periods of time will be more taxing on the controller.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1574 Views
  • « Previous
    • 1
    • …
    • 443
    • 444
    • 445
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore