Do IOU modules retain their current state when they lose communication with the host NetController? (NC1, NC2)
CX9900
CX9400
CX9680
IOU Modules
Documentation
Upon losing communication with the NetController, output modules (DO-4. AO-4 etc) start a 260 *** second timer (4 minutes and 20 seconds), if communication is not restored before the time expires the module turns off the outputs as a safety measure.
For Digital outputs the outputs will be turned OFF. (Invert attribute is taken into account).
For Analog outputs the output value will be set to zero.
*** For access control modules (AC1, AC1A, AC1Plus) the timer is 10 seconds to avoid leaving a door unlocked for an extended period of time.