What is the maximum allowable distance between two Lon devices on a lon network?
  • What is the maximum allowable distance between two Lon devices on a lon network?
  • sesa177673
    sesa177673
  • Sacco
    Sacco
‎2018-09-06 11:08 AM
TAC Vista 5.1.X
Lon devices such as Xenta 2/3/400
FTT10-A either free or bus topology
The physical layout of a building may require nodes to be installed far apart.
The maximum distance between two devices (nodes) is 320m. No node may be more than 320m worth of cable from the bus termination (if bus topology is used). More information can be found in the Lonworks Installation Handbook, chapter 5 "Physical Network Structuring".
  • 11100