SHD, SHO, SHR humidity sensor series specification.
  • SHD, SHO, SHR humidity sensor series specification.
  • SESA150559
    SESA150559
‎2018-09-06 11:08 AM
The documentation states in different ways that the sensors are both 0-95% and 0-100% RH range.
SHD100 006902321
SHD100-T 006902331
SHD101-T5 006902381
SHD101-T6 6902411
SHO100 006902361
SHO100-T 006902371
SHO101-T5 006902401
SHR100 006902340
SHR100-T 006902350
SHR100-T5 006902390
Different RH (Relative Humidity) values are listed in the documentation, and needs to be explained.
Ranges are divided into "measuring range" and "working range".
Measuring range: 0…100% r.H.
Working range:   10…100% r.H. ( non condensing )
Normally 100% r.H. is already water but it is possible to have 100% r.H. in air- or gas form.
Sensor works at 100% r.H. in air but not if pure water is present.
This is why “non condensing” is added. In this case working range is 10…100%.
If we don’t add “non condensing”,  specification should read: 10…95% r.H.
 Sensor will not become damaged because of condensing.
  • Field Devices
  • 11092
0% helpful (0/1)